Turned off breakers in kitchen to replace a wall dimmer...

Customer Question
When breakers turned back on...
Turned off breakers in kitchen to replace a wall dimmer... When breakers turned back on, dishwasher wont work- no lights on control panel
Submitted: 2 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 21 minutes by:
6/23/2015
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago
Kevin
Kevin, Licensed Electrical Contractor
Category: Electrical
Satisfied Customers: 3,791
Experience: 31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License
Verified
Hello.....my name is ***** ***** I will be happy to assist you with your electrical question. My goal is to exceed your expectations on Just Answer!
1) You mention breakers as in multiple breakers.....the dimmer switch should be on a separate breaker than the dishwasher, is that correct?
Please confirm, in addition to the dishwasher not working, is the lighting circuit working?
2) Take a look a the breaker layout in the electrical panel, are the breakers that are affected stacked on top of each other or located in different slot positions in the electrical panel?
3) Is the dishwasher protected by a GFCI receptacle or a GFCI breaker? Any GFCI's that may have tripped?
4) Do you have a 2 wire lead AC voltage tester (contact type) or an AC voltmeter available?
5) Were any of the breakers tripped?
Ask Your Own Electrical Question
Customer reply replied 2 years ago
Dimmer on a different circuit. In locating that circuit, i flipped the dishwasher circuit off. The breaker that controls dishwasher also controls garbage disposal. GD is working. No access to voltmeter. Gfi's in kitchen working. No breakers tripped thx
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago
Thanks for the replies.
1) I need to know if the lighting breaker and the dishwasher breaker are stacked on top of each other or using a double pole circuit breaker? Am trying to confirm if the circuit may have been wired as a shared neutral circuit?
2) Inside the wall dimmer switch box, is there a group of white neutral wires that are spliced and wire nutted together? Possibly a loose connection at a splice?
3) Since 2 different circuits are impacted, I suspect a shared neutral circuit?
4) Perhaps you can borrow a voltmeter from a neighbor or a friend? A meter can easily determine if the hot conductors are not working or if a neutral wire problem. If unable to borrow a meter, a good meter is available at any local Lowe's or Home Depot for around $23.00
Ask Your Own Electrical Question
Customer reply replied 2 years ago
Thank you.. The dimmer is working fine. The breaker that controls dimmer on opposite side of breaker box. The dw is stacked with g disposal- which works. All GFIi's in kitchen area working. Dishwasher 3 years old worked fine until I tripped the breaker- only in an attempt to find the dimmer Once the dimmer located and fixed the other breakers switched back on. Didnt notice the controll panel lights were off on the dw until last evening. As mentioned the gd works fine. Yhx
Electrician: Kevin, Licensed Electrical Contractor replied 2 years ago
OK, thanks again for the replies.
1) A voltmeter will be required to confirm for voltage at the DW. Let me know when you have a meter and we can take it from there.......Thanks........Kevin!
Ask Your Own Electrical Question
Ask Mike Your Own Question
Mike
Mike
Mike, Master Electrician
Category: Electrical
Satisfied Customers: 1,425
1,425 Satisfied Customers
Experience: Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Mike is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,940 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,603 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,791 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I have 2 dedicated circuits in my circuit breaker box that
I have 2 dedicated circuits in my circuit breaker box that are 240V, they each have 2 hot wires going to them. The circuit is terminated to an individual plug (L6-20R) for each circuit. The device I'm… read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
I have 415 amps worth of branch circuit breakers. what size
I have 415 amps worth of branch circuit breakers. what size service do i need for my house? is 200 sufficient … read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
I'm trying to move a circuit breaker box in a place I'd like
I'm trying to move a circuit breaker box in a place I'd like to put a bathroom. Knowing it isn't code to have one in a bathroom, is a junction box ok? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
How do I determine the correct size circuit breaker panel
How do I determine the correct size circuit breaker panel for an stand alone workshop. I don't suspect I would draw more than 20 amps at any given time, but do I need a box assumes everything is turne… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
What is the function that makes a circuit breaker different
what is the function that makes a circuit breaker different from a switch so that it is able to break fault current … read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
Was wondering which circuit breaker I should look into
Hello, was wondering which circuit breaker I should look into replacing. As it stands my Dryer flips the circuit breaker for the upstairs bedrooms. Should I look into replacing the circuit breaker for… read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
My circuit breaker was buzzing, so I pushed the test button.
Hello. My circuit breaker was buzzing, so I pushed the test button. This switched all the sockets off in my house but left all the lights on. When I flipped the breaker switch back, al the sockets cam… read more
Sam I
Sam I
Electrician
B.S.
364 satisfied customers
My circuit breaker is tripped and will not reset. I've
My circuit breaker is tripped and will not reset. I've checked wiring to outlets looks okay. At the electrical panel there is no power to breaker itself. I check other breakers and the have power. Any… read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
950 satisfied customers
I just need to know what circuit breaker to buy for my
I just need to know what circuit breaker to buy for my mitsubishi mini split that is a 50A 2 pole that provides earth leakage protection … read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
Honda EU7000is has 30 amp line with circuit breaker with
Honda EU7000is has 30 amp line with circuit breaker with each line up to 22.6 amps. Questions is 32 amp draw too large and will trip circuit breaker and can circuit breaker be upgraded to 40 amp to al… read more
Sam I
Sam I
Electrician
B.S.
364 satisfied customers
I have a question about ITE circuit breakers, First call,
I have an ITE electrical panel #FEQ 28MBB. I need compatible circuit breakers… read more
Sam I
Sam I
Electrician
B.S.
364 satisfied customers
I have a zinsco circuit breaker panel. The main line circuit
I have a zinsco circuit breaker panel. The main line circuit breaker is a 125 amp Zinsco 2pole breaker.My question is can I safely replace 125 amp breaker with a 100 amp 2 pole breaker? Main lineRegar… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have a well pump wired into a 240v/20a circuit breaker. C/
I have a well pump wired into a 240v/20a circuit breaker. C/B has white wire, black wire, ground wire. Pressure switch on well pump has same...black, white. ground. Output from pressure switch to pump… read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
I've checked ALL circuit breaker with a voltage meter. They
I've checked ALL circuit breaker with a voltage meter. They are good, but I still don't have power in both bathrooms. Not in the outlets or ceiling lights. Can you help. … read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
The circuit breaker tripped controlling all the electricity
The circuit breaker tripped controlling all the electricity in my son's bedroom. This circuit also controls the recessed lighting in the dining room. The only way I can reset the circuit breaker is if… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
One of my circuit breakers tripped a few months ago. It
Hello. One of my circuit breakers tripped a few months ago. It would not turn back on. Tonight, the night before I have scheduled an electrician to come, I checked the breaker and I was able to flip i… read more
Kevin
Kevin
Licensed Electrical Contractor
3,791 satisfied customers
I currently live in apartment with a circuit breaker that
I currently live in apartment with a circuit breaker that has 100 amps total. I would like to know to upgrade to 200 amps if it only requires switching the breaker box only or you have to bring anothe… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
What is the standard circuit breaker for an wall oven and
Greetings, What is the standard circuit breaker for an wall oven and for a dual fuel range? Aren't they typically 40A? The installation instruction I am looking at for a Kenmore Elite wall oven (3.4kW… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x