Electrical

Electrical Questions? Ask an Electrician Online.

Ask an Expert,
Get an Answer ASAP!

My question is about derating conductors. Let's say I have…

Customer Question
My question is about derating...
My question is about derating conductors. Let's say I have 24 #10 THHN wires in a conduit. More than 20 wires thru 30 wires you are at 45%. That results at 18amps. Sence they don't make an 18amp breaker, can I put these wires on a 20 amp breaker or do I have to land them on a 15 amp breaker.
Submitted: 3 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 7 hours by:
6/19/2015
Electrician: AssuredElectrical, Master Electrician replied 3 years ago
AssuredElectrical
AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 4,241
Experience: Contractor-42+ Years in the ElectricalTrade
Verified
Welcome. My name is ***** ***** would be glad to assist.You can put the #10 on a 20 amp breaker in this case, IF the load meets the below requirements only. 240.4 Protection of Conductors Conductors, other than flexible cords, flexible cables,and fixture wires, shall be protected against overcurrent in accordance with theirampacities specified in 310.15, unless otherwise permitted or required in 240.4(A) through (G).(B) Overcurrent Devices Rated 800 Amperes or Less. The next higher standard overcurrent devicerating (above the ampacity of the conductors being protected) shall be permitted to be used, provided all of the following conditions are met: (1) The conductors being protected are not part of a branch circuit supplying more than onereceptacle for cord- and-plug-connected portable loads.(2) The ampacity of the conductors doesnot correspond with the standard ampere rating of a fuse or a circuit breaker without overloadtrip adjustments above its rat- ing (but that shall be permitted to have other trip or rat- ingadjustments).(3) The next higher standard rating selected does not ex- ceed 800 amperes. Let me know anything further needed,Thanks
Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask AssuredElectrical Your Own Question
AssuredElectrical
AssuredElectrical
AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 4,241
4,241 Satisfied Customers
Experience: Contractor-42+ Years in the ElectricalTrade

AssuredElectrical is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,290 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,414 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

4,241 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I am in arizona installing a 200 amp panel in a new location
i am in arizona installing a 200 amp panel in a new location against the wall on the outside of the house. i would like to pipe from the new panel location, into the attic and splice to the old wires … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
Is there a problem with having multiple 2 pole circuits in
Is there a problem with having multiple 2 pole circuits in the same pipe example 4 2 pole circuits in a 1 rigid conduit … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I'm installing a Marey Eco270 on demand water heater
I'm installing a Marey Eco270 on demand water heater which requires (3) 50amp 20v double pole breakers using 8/3 wire. It will be located in my mechanical room about 25' from the main panel. Is instal… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I have the revised 2002 edition. My question: page 67: ampacities
I have the revised 2002 edition. My question: page 67: ampacities of not more than 3 conductors in a raceway. The 14,12,and 10 readings have an asterick stating much lower max amps than it says in the… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
4,241 satisfied customers
I need THWN-2 AWG 12 wire. Per the Code, this wire has 90
I need THWN-2 AWG 12 wire. Per the Code, this wire has 90 degree celcius capacity in wet locations with a 30 amp ampacity. I am running 8 current carrying conductors in a conduit, which means the ampa… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
4,241 satisfied customers
There are 5- 20 amp circuits in a 11/4 EMT conduit. 90 c copper
There are 5- 20 amp circuits in a 11/4 EMT conduit. 90 c copper 12 gauge wire. They are all at full load of 20 amps. Are these circuits overloaded? Conduit is attached to a concrete wall exposed to ai… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
4,241 satisfied customers
IF I HAVE 25 #10AWG IN A 2" CONDUIT(RACEWAY), WITH DERATING
IF I HAVE 25 #10AWG IN A 2" CONDUIT(RACEWAY), WITH DERATING FACTURE, HOW MANY #10AWG CONDUCTORS I'M I ALLOWED?… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
4,241 satisfied customers
Is it ok to put a 20 amp breaker on a 10 awg wire to run a
Is it ok to put a 20 amp breaker on a 10 awg wire to run a well pump rated for a 20 amp breaker. the wires for the pump are braided 12 gauge or equivalent for a 20 amp circuit. Also, can a circuit wit… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
Conduit fill question: Outdoor rigid conduit; one inch; contains
Conduit fill question: Outdoor rigid conduit; one inch; contains four #10 stranded; can I pull three additional #10 stranded to bring existing circuit up to code and add an additional circuit?… read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
I have 1.5 emt conduit with 28 # XXXXX is this a code violation
I have 1.5 emt conduit with 28 # XXXXX is this a code violation of CEC 310.15(B) (2) (a) and what does the CEC stand for, I'm use to comforimg to the NEC Code or quick reference Ugly's Book which say … read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
4,241 satisfied customers
I have 6 current carrying conductors in a 3/4 raceway. My
I have 6 current carrying conductors in a 3/4" raceway. My load is 22 amps and I have 75 deg terminations. My overcurrent protection is 30 amps the question is can a #10 thhn be used per code for this… read more
Rich
Rich
Master Electrician
Vocational, Technical or Trade Scho
1,117 satisfied customers
Mogie, here is my issue. I have a 1 1/4 EMT condiut inside
Mogie, here is my issue. I have a 1 1/4 EMT condiut inside a building running about 90feet long with the allowable number of wires per this conduit size. I have an inspector telling me I have to run 1… read more
No. 1 Sparky
No. 1 Sparky
Vocational, Technical or Trade Scho
18 satisfied customers
I have a row of 12 machines that are 480v 30 amp. I have a
I have a row of 12 machines that are 480v 30 amp. I have a panel that I'm feed them with, question is How many machines am I allowed to feed out of a single conduit? in other words can I come out of t… read more
Rich
Rich
Master Electrician
Vocational, Technical or Trade Scho
1,117 satisfied customers
i have a 2inch conduit with 21 hots 21 neutrals 1 ground all
i have a 2inch conduit with 21 hots 21 neutrals 1 ground all number 10 thhn wire, is this legal per nec as far as derating is concerned? all ckts are on 20 a breakers in a three phase panel 120/208… read more
Sir Sparks
Sir Sparks
Owner
State & UK Certified Master electri
2,519 satisfied customers
My question regards derating branch conductors in a conduit
My question regards derating branch conductors in a conduit if I have 21 phase conductors and 7 neutrals ( half a 42 circuit panel board ) and put them in an 1-1/4 conduit the derating is at 45%......… read more
Sir Sparks
Sir Sparks
Owner
State & UK Certified Master electri
2,519 satisfied customers
When calculating derating factors for lighting loads what do
When calculating derating factors for lighting loads what do you use for the starting point. The ampacity of the wire eg: 15 Amps or the actual load of the circuit eg: 9 lights at 87 VA each? The sena… read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
When you read this question, I really need more than a generic
When you read this question, I really need more than a generic answer.....I would like to know where you found it and the method you used...I have had my butt handed to me for doing some electrical wo… read more
InspectorL
InspectorL
Associate Degree
32 satisfied customers
Is it legal to pull 20 - 20 amp circuits in a 2 EMT a total
Is it legal to pull 20 - 20 amp circuits in a 2" EMT a total of 40 # XXXXX THHN terminated on 20 amp circuit breakers… read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x