HI there,
I want to give my husband a garbage disposal for Christmas, I don't have power outlet under the sink. I have a dishwasher, that is connected to a direct wire underneath, that goes down to the basement. Can I Install an outlet to this direct wire so I can plug both the disposal and the dishwasher into it? and then use an air switch to control the disposal. Or if its easy enough, it might be cheaper to install a regular switch to operate the disposal. then I would have to split the outlet so half would be "hot" or on always for the dishwasher and the other half is powered by the switch correct? please help :)
Show More
Show Less
Ask Your Own Electrical Question
Answered in 1 minute by:
11/1/2013
P.J.
P.J., General Contractor
Category: Electrical
Satisfied Customers: 750
Experience: Various skills in all areas of construction allows me to help others solve their problems.
Verified

P.J. :

Hi, my name is XXXXX XXXXX I'll be working with you today.

P.J. :

Either method you describe would work fine.

P.J. :

The air switch is certainly the simplest.

Customer:

ok... so I can just attach an outlet to this direct wire thing?

P.J. :

Yes. You would only need to insure there aren't too many loads on the circuit already such that the additional load would cause it to be overloaded.

Customer:

how would I know that? wouldn't it only be the dishwasher?

P.J. :

It may be. The easiest way is to trace the wire if you can see it in your basement as you describe.

Customer:

well it goes under the floor, so I assume it goes to the breaker box in the basement

P.J. :

The other is the trial and error method by checking surrounding outlets, etc., to see if they turn off and on with that dishwasher breaker.

Customer:

it has its own switch on the breaker box

Customer:

so how do I wire an outlet to the wire?

P.J. :

Then it is probably by itself.

P.J. :

You will need to add a box either in or on the wall where the wire exits now.

Customer:

ok.... so is there some kind of video or something so I know how to wire the outlet to the wire?

P.J. :

Yes. Home Depot has a video available on Youtube.

P.J. :

There are several videos available on there for just your situation.

Customer:

ok... I guess I cant contact you with further questions, I might have... I have been trying to find this situation on youtube and havnt come across exactly this...

P.J. :

A video title for you to watch is called how to install a switched (or half hot) receptacle.

P.J. :

You can always contact me back here.

Customer:

now I am worried that I just spend $ and I still don't know how to wire this outlet in

Customer:

but I would have to pay again coccect?

P.J. :

You would not.

P.J. :

There is a time limit I believe but I think it is a week or so.

Customer:

ok lol... I guess I should have asked closer to Christmas when I would actually be installing it

P.J. :

Oh. Well at least search the videos and I think you will find what you need and won't need any further assistance. You can handle it.

Customer:

so would I still need the switch to be half hot, if I go with the air switch? instead of the regular switch?"

P.J. :

softcellelectrical is the person that uploads many useful videos on Youtube.

P.J. :

You would not want an half hot outlet with the air switch

P.J. :

It would be a regular duplex outlet that is hot all the time.

Customer:

ok I though so

Customer:

so the wire that connects to my dishwasher, should be the same kind of wires that are in the videos that they attach the outlets to right?

P.J. :

Yes.

Customer:

I have seen some videos where they attach the end of am extention cord, or a "pigtail" they called it... could I also do that?

P.J. :

Cord and plugs are allowed in most locations and by most manufacturers.

P.J. :

Most can't exceed 4 feet long.

Customer:

hmmm.... ok, well thank you!

Customer:

one more thing

P.J. :

Ok

Customer:

if I did want to install a regular switch... would I use this same wire?

Customer:

how does that wor?

Customer:

work*

P.J. :

You would need to add a new wire from the new box containing the outlet to a new switch box.

Customer:

so I would wire the box as we discussed above and the take a new wire and also attach that to the box, and then attach the other end of that wire to the switch, and when I plug the dispoal into the outlet and take off that metal pc between the two screws to make half hot, then the witch will control the disposal?

P.J. :

Yes. The details of how to connect those switch wires will be in the video but you are correct.

Customer:

but either way attaching the outlet box is the same and the first step right?

P.J. :

That is correct.

Customer:

ok...I hope it all works out!

P.J. :

I'm confident it will. You sound like you have a good understanding already.

Customer:

thank again

P.J.
P.J., General Contractor
Category: Electrical
Satisfied Customers: 750
Experience: Various skills in all areas of construction allows me to help others solve their problems.
Verified
P.J. and 87 other Electrical Specialists are ready to help you
Ask your own question now
Ask P.J. Your Own Question
P.J.
P.J.
P.J., General Contractor
Category: Electrical
Satisfied Customers: 750
750 Satisfied Customers
Experience: Various skills in all areas of construction allows me to help others solve their problems.

P.J. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I am trying to add a power outlet to wall. The light switch
I am trying to add a power outlet to wall. The light switch above it has 2 wires(black and white) and ground. I was told to run black wire from outlet to switch and leave black wire attached the switc… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have a few questions about changing the outlet that is
Good Morning, KevinI have a few questions about changing the outlet that is controlled by a wall switch. I would like the switch to control a different outlet - are you available for few questions. Mc… read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
I replaced an old GFI outlet with Leviton GFNT1_KW outlet. 4
I replaced an old GFI outlet with Leviton GFNT1_KW outlet. 4 wires and a ground, two black two white. Green status light is on but no power. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have a half switched outlet that need to be changed. I
i have a half switched outlet that need to be changed. I understand that i should break the tab between the two brass screws to separate the red and the black wires but do i need to break the tab on t… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Gfci outlet was fried which caused the upstairs outlets in
Ok... so gfci outlet was fried which caused the upstairs outlets in the bathrooms not to work... pulled the old gfci switch, put a new one in, had the white wires on the neutral side and black on the … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Im trying to replace an electrical outlet with a USB outlet
Im trying to replace an electrical outlet with a USB outlet but I'm not sure if it can be done or how it should be done. Here are pictures.… read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
Wiring diagram for outlet on a switch the to a light on same
wiring diagram for outlet on a switch the to a light on same switch … read more
David Bowden
David Bowden
Owner
478 satisfied customers
Which wires go where? In replacing a switch and outlet in
Which wires go where? In replacing a switch and outlet in the bathroom I mistakenly didn't label the wires before I ran down to answer the door now I don't know where the three main lead wires into th… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a legrand adorne outlet I took out the old outlet
Hi I have a legrand adorne outlet I took out the old outlet which had a red and black both on hot and a white on white. I put the red and black on hot - first I put the two hot wires in opposite sides… read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
I need to wire a switch and 2 outlets in same box) without
I need to wire a switch and 2 outlets in same box) without the switch controlling the outlets. The switch is for a ceiling light. Thanks. … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
1,052 satisfied customers
Question on wiring GFCI outlet... Late 80's...and no. Outlet
outlet is under the sink...bottom outlet goes to switch on the wall… read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
I have a Leviton T5225 combination switch/outlet and I want
I have a Leviton T5225 combination switch/outlet and I want to wire it so the switch controls the outlet. There is a break-off tab connecting the two black screws. There is another dual outlet in the … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a question related to electrical outlet combo switch,
i have a question related to electrical outlet combo switch … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
How do Locate a reset switch for a GFCI outlet. One day
how do Locate a reset switch for a GFCI outlet JA: I'll do all I can to help. How long have you been dealing with this? Customer: one day JA: Do you plan on doing the work yourself? Customer: yes JA: … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I took down a half wall with an outlet. the outlet was
i took down a half wall with an outlet. the outlet was connected to a 3 way switch and now the light will not come on. what should i do … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have several outlets that seem to be in the same "switch"
hello there... I have several outlets that seem to be in the same "switch" in my panel. as it happens it is the bathroom, part of the kitchen, my bedroom, my children's bedroom and a hallway next to b… read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
I have a combination switch/outlet that I would like to wire
I have a combination switch/outlet that I would like to wire into a box so that the switch operates the outlet. what would the wiring diagram look like? Thx … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a switched outlet (a switch that comes before the
I have a switched outlet (a switch that comes before the outlet and turns the power to the outlet on and off). I want to remove the switch and replace it with a blank, thus capping the wires in the bo… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x