Building an RV park in the Texas area. With a total of 96 sites. They will all be 50 amp sites. Do I still us a demand factor of .41 I will be setting pole ever 150 .the lot is 1000 ft deep. The site will be 4 roll wide with road ways between them. Will be installing sub meters at the RV pads. The sub meter pedestals will have breakers in them. Be I still need a breaker panel off the main. Trying to keep my runs to the sub meter less an 300 ft. All wiring after the main will be run under ground in conduit. What is the most cost effective way to run power from the main to the sub meters.
Thanks for all the help.
Show More
Show Less
Ask Your Own Electrical Question
Answered in 2 hours by:
9/15/2013
Phil
Phil, Mechanical Engineer
Category: Electrical
Satisfied Customers: 8,824
Experience: Retired electrical contractor, 51 years experience.
Verified

Welcome to Just Answer!

Electrical engineering will be required to get the building permit. These issues can get complex when attempting to minimize wire runs and costs and still comply with the code.

I can answer a few questions generally however.

You might want to bring the power onto the property at two separate locations. I would divide the property into 4 separate quadrants, and bring the power into a spot centered in each pair of quadrants, Put an electrical room at each location, each electrical room with 2 each, breaker panels capable of holding 24 each 60 amp 230v single phase breakers.

Each of the 60 amp breakers to serve one spot, with an electric meter at each spot along with a 50 amp GCFI breaker/ disconnect made for RV parks. Run the 3 conductor wire with ground in direct burial underground rated cable, at least 36 inches deep. on a 2" thick bed of sand, then covered with 2 inches of sand, some people lay a 1 inch thick, x 10 inch wide redwood plank over the top bed of sand, then back fill the trench.

Wire size of the cable to be determined by your electrical engineer (or licensed electrical contractors) final design and length of each run)

The under ground cable runs should be in pattern and available for later excavation, and well marked as under ground cable routes.

.41 demand factor for sizing the main feeder side from the utility to your electrical rooms is about as tight as you would want to go, take your electrical engineers advice on those issues as he designs the electrical rooms and panels. The code in these cases is a *minimum standard...not... always best practice in all situations.

Let me know what you think, we can go from there as long as you rate this answer positively...in that case I leave the question open for a few follow up questions.

Phil




Phil
Phil, Mechanical Engineer
Category: Electrical
Satisfied Customers: 8,824
Experience: Retired electrical contractor, 51 years experience.
Verified
Phil and 87 other Electrical Specialists are ready to help you
Ask your own question now
Customer reply replied 4 years ago
I am in Harris County. In a town called Highlands 77562. Houston does not inspect this area. Only the civil. All may plain have been stamped. But no electrical plain are needed. Just have to get new tie in permit from Center Point. Can I send you a drawing of my lay out. Can only bring power down one side of the propertie. All my prints for ease ments have bent stamped. The land is 185' wide by 1200 deep
Hello again, this job still needs some electrical engineering, even without a permit. You can make costly mistakes trying to do it yourself with only a few answers addressing some of the issues, Cost savings on equipment sourcing alone will pay for the engineering if you tell the engineer you will try to use surplus electrical panels and you get the right engineer. I can be helpful from here, but cannot provide the detailed engineering you need..thats an extensive project.

Just Answer, is rolling out a new set of options the 19th of September that will allow us to do this sort of extended work..

If you can send me some good photo's of the drawings you have, I can take a look at them and give you an estimate of the time that will be involved.

We can go from there.

Phil
Ask Your Own Electrical Question
Customer reply replied 4 years ago
I am in Harris County. In a town called Highlands 77562. Houston does not inspect this area. Only the civil. All may plain have been stamped. But no electrical plain are needed. Just have to get new tie in permit from Center Point. Can I send you a drawing of my lay out. Can only bring power down one side of the propertie. All my prints for ease ments have bent stamped. The land is 185' wide by 1200 deep
Customer reply replied 4 years ago
Do you have an Email address I will send you a file.

Hello again,

Send the file to '[email protected]' attention:Customerbr/>

Center Point will issue not you a tie in permit until they inspect the job and insure that it meets the national electrical code....they may very well require a Registered Professional Electrical Engineer in the State of Texas to stamp the drawings... he will not stamp the drawings unless he or his engineering office draws them....or... if someone else draws them and they are accurate in *every detail... a set of plans like that generally runs 5 to 10, 36 inch by 48 inch prints... and involves specifications for each and every component of the system, including detail drawings of every connection type and other aspects of the project. They will charge you between $50,000 and $100,000 for that work depending on what the net load analysis turns out to be... probably in the 450-600 kwh range depending what services you end up supplying to each site..

A sketch from someone on a basic layout and not details, and no registration in Texas will generally not come close to being adequate, and puts everyone involved, including yourself as owner, at great risk. Thats why such things are simply not done with electrical systems. Other things such as carpentry, drainage, water systems etc are less risky and you can often get a job build in those regards XXXXX XXXXX But thats seldom if ever true with electrical when you dealing with a large electrical utility.




Before you proceed further you should contact Center Point and get from them in detail what they need from you before they will connect to an electrical grid system for such a large RV park. If they say 'Stamped drawings' this extensive set of drawings is what I am referring to.

The electric utility can be held liable for negligence if they connect to an improperly wired power distribution grid... just defending such a lawsuit can cost several hundred thousand dollars, and jury awards can run into the tens of millions of dollars.

What I can do for you from here beyond the advice already given if you choose to rate my work so far positively, is to provide a schematic sketch that will take me 8 or 10 hours including research, of what will generally be required to help you assess the cost, get engineering quotes and possibly deal with an electrical contractor on some aspects of the job. That will not be sufficient in helping you get deal with Center Point.

You will still need a set of electrical plans to satisfy Center Point, those plans must meet the National Electrical Code...regardless if you need a local building permit or not.


Let me know if that option interests you, we can go from there.

Phil

Ask Your Own Electrical Question
Customer reply replied 4 years ago
Thanks Phil. I meeting Center Point this week. As for as drawing it seam strang but I have 2 parks that friends have build and there were no electrical drawing. I will talk to them and give you an up date.

Thanks, XXXXX XXXXX be looking forward to what the utility company has to say.

The electrical engineering estimate I gave was high I was using the wrong chart, it will likely be in the $10,000 to $15,000 range, you will have to put the job out to bid in order to get the exact price if you end up going that way.

Phil

Ask Your Own Electrical Question
Ask Phil Your Own Question
Phil
Phil
Phil, Mechanical Engineer
Category: Electrical
Satisfied Customers: 8,824
8,824 Satisfied Customers
Experience: Retired electrical contractor, 51 years experience.

Phil is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,940 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,603 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,715 satisfied customers

30 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Can I add a 90 elbow to the main conduit so that I can raise
can I add a 90 elbow to the main conduit so that I can raise that conduit the conduit is running vertical and i need some height under the conduit … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
Need to wire a 240 volt single phase 3 wire motor. Just
the motor has 2 connections for the hot wire and also has a common… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have 3 black wires and 3 wires and 1 coming out of
I have 3 black wires and 3 white wires and 1 white coming out of electrical outlet, how t … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have a sauna that is wired with 240 two wire for load (red
I have a sauna that is wired with 240 two wire for load (red and black) and a ground -- the neutral line (white) is not used -- currently it is not on a GFI and I would like to put it on a GFI - I wou… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
TROUBLE WIRING A LEVITON 6683. I HAVE ONE HOT WIRE BLACK/
I AM HAVING TROUBLE WIRING A LEVITON 6683. I HAVE ONE HOT WIRE BLACK/ WHITE /GROUND. I AM TRYING TO WIRE 2 /6683 SWITCHES OFF THIS WIRE TO GO TO DIFFERENT LIGHTS … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Wondering if I can run wires that are not mounted on studs
Wondering if I can run wires that are not mounted on studs in wall in the state of VA? … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
Had broken wire from outside breaker. changed wire to
had broken wire from outside breaker. changed wire to copper. 60 amp breaker trips when power is turned back on. disconnect wire on 60 amp wire and still have voltage in disconnected wire … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
How do I wire a motion sensor with black and supply wires,
Hi! How do I wire a motion sensor with black and white supply wires, red (or pink) light wires and red, blue and brown sensor wires? Thanks. … read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
I have a dedicated 10 amp romex line in conduit, going to a
I have a dedicated 10 amp romex line in conduit, going to a direct wired garbage disposer under my kitchen sink. I want to connect this line up to a single gang outlet box to make exchanging the dispo… read more
Sam I
Sam I
Electrician
B.S.
366 satisfied customers
I am running 3 circuits inside of pvc conduit. 220v 30a
I am running 3 circuits inside of pvc conduit.220v 30a water heater 220v 15a ac 120v 20a receptaclecan I use 1 shared 10awg ground wire for all circuits?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Are the wires from the main box to a jump box sapose to be
are the wires from the main box to a jump box sapose to be in riggid conduet … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Wiring garage have 14-3 and 14-2 wire going to outlet and
Wiring garage have 14-3 and 14-2 wire going to outlet and there is no ground how would you hook these up to sub panel… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Need help determining wire size, wire type, and conduit size
Need help determining wire size, wire type, and conduit size for 200amp panel with a 200 amp subpanel. Here is a list of my questions: http://mnjustin.com/diagram.jpg… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
How much to install 100' of electrical line in a conduit if
how much to install 100' of electrical line in a conduit if the trench is already dug. Include the cost of wiring and adding a 50 Amp Circuit Breaker … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
What size wire is needed to run underground in conduit to a
What size wire is needed to run underground in conduit to a garage about 60 feet from the main connection at the power pole? This would be connected to a subpanel in the garage. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
Do you need to remove existing conduit and or conductors if
Do you need to remove existing conduit and or conductors if they are being abandoned and not being used? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Can I use the conduit that leads into the panel box by
Can I use the conduit that leads into the panel box by adding a second pair of wires to be connected to another circuit breaker? Easier to do than setting up another separate conduit attachment? I kno… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
I have a black, and wire in mtl. conduit. It appears that
I have a black, white and green wire in mtl. conduit. It appears that the green wire is the hot wire. Do I hook this to the side of the plug with the brass screws. Which wire is likely to be the groun… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x