Mike, I'm new lighting and outlet circuits in my home and eliminating an old fuse box. I'm experienced with residential electrical work but not with AFCI issues. I put in 2 Siemens AFCI breakers for two bedrooms and they trip with any load. So as I isolated one outlet to make a direct home run line from the breaker and panel to that outlet, with all those down the line separated. And the AFCI breaker still trips with a guitar amp or lamp, and it seems with any load (amp was handy). This was to isolate workmanship issues. Any thoughts? I think there are very likely issues with other wiring into the panel still as the work has progressed room by room
Submitted: 4 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 9 minutes by:
9/12/2013
Electrician: Mike G., Master Electrician replied 4 years ago
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 7,952
Experience: Proven Professional 49 years Experience
Verified
Hi, I'm Mike and I'll be glad to assist you. AFCI breaker are a good idea but are not required on a service upgrade. By code, only if a circuit is installed or modified by extending it are they required.

The first thing to do is map out the circuits to know exactly what is on each circuit. Panel directories are worthless. Can't put enough info in a small label to identify the outlets. See below for maping directions. When completed, you see exactly how the circuit was ran. Then it would be a matter of opening it in places to see if the AFCI holds, if you decide to use them. If not then you need to be on the look out for flicking. That is the indication of a bad connection, which the AFCI is made to protect.
graphic
Ask Your Own Electrical Question
Customer reply replied 4 years ago
I'm disabling all the fuse box circuits and rewiring. I don't understand why the AFCI trips when there is a new cable direct to a single outlet with all the others disconnected from it on that circuit. Could it be related to something else in the house wiring and panel? I've diagrammed everything on a floor plan.
Electrician: Mike G., Master Electrician replied 4 years ago
If the circuit is a direct run to the outlet, I would check to see if the ground is touching a neitral connection. That would trip an AFCI under load.
Ask Your Own Electrical Question
Electrician: Mike G., Master Electrician replied 4 years ago
One more thing to check. Are the wires terminated under the screws or in the push backs.
Ask Your Own Electrical Question
Customer reply replied 4 years ago
That's why I'm baffled. Already pulled the outlet and checked everything. I"ll check again in the morning. It's a Siemens AFCI and indicating arc to ground.
Electrician: Mike G., Master Electrician replied 4 years ago
To verify the breaker is good, swap it with another to see if another will hold the circuit. After that the only thing it could be is a staple in a wire or a bad strip.
Ask Your Own Electrical Question
Customer reply replied 4 years ago
I've done a lot of wiring and don't use push backs. Carefully make a loop and screw connection. Twisted the connections before puting on the wire nuts. Pigtails to the outlet. There isn't any problem with the connections to this outlet and the wire run is direct from the panel box. I isolated it to see if there is something I don't know about or product issue with the AFCI? I can even run a another short cable to the AFCI tomorrow with an outlet to see if it still trips, but I really don't think there is any damage to the cable.
Electrician: Mike G., Master Electrician replied 4 years ago

Swap the breaker. I'm doing a aluminum remediation of 100 apartments and using Siemens AFCI. Each apartment needs 5 AFCI breaker. Out of the 150 I have already installed, there was one failed breaker. There is not tester for checking them, so the only thing to do is swap it.

Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 7,952
Experience: Proven Professional 49 years Experience
Verified
Mike G. and 87 other Electrical Specialists are ready to help you
Ask your own question now
Customer reply replied 4 years ago
OK, i purchased a month trial plan. I'll swap the breaker tomorrow. One forum suggested having a spare AFCI, a GFCI, and a regular breaker. Use the GFCI to check if there is a ground fault. It would seem odd to have a failed breaker really. Thanks, I'm likely to have some more questions!
Electrician: Mike G., Master Electrician replied 4 years ago

Come back after you swap the breaker and let me know how it worked out. You can return for follow ups, no charge.

Ask Your Own Electrical Question
Customer reply replied 4 years ago
Thanks Mike!
Electrician: Mike G., Master Electrician replied 4 years ago
You're welcome.
Ask Your Own Electrical Question
Customer reply replied 4 years ago
I was unfamiliar w this breaker. Once I installed it with neutral in and out everything worked fine. I have a question about surface wiring in an attached garage w plaster ceilings.
Electrician: Mike G., Master Electrician replied 4 years ago
What"s the question?
Ask Your Own Electrical Question
Electrician: Mike G., Master Electrician replied 4 years ago
I see that you opened another question and it is being assisted by another expert. I'll close this follow up.
Ask Your Own Electrical Question
Customer reply replied 4 years ago
I would like to keep with one electrician. How do I do that? I bought a plan.
Ask Mike G. Your Own Question
Mike G.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 7,952
7,952 Satisfied Customers
Experience: Proven Professional 49 years Experience

Mike G. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,952 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I have a dual outlet wall receptacle with two sets of wires
I have a dual outlet wall receptacle with two sets of wires attached to it. I want to split this receptacle so that one outlet is controlled by a switch and add another unswitched dual outlet "downstream." Is this possible and if so, how should it be wired? Thanks. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I am replacing an electric outlet that has 3 sets of wires,
I am replacing an electric outlet that has 3 sets of wires, 3 white, 3 black, and 3 ground. The tabs between the screws are intact and it is not a switched outlet. 2 white wires are stabbed in the bac… read more
Mike G.
Mike G.
Master Electrician
7,952 satisfied customers
4 prong outlet for a electric car which wires go where. New
4 prong outlet for a electric car which wires go where … read more
Mike G.
Mike G.
Master Electrician
7,952 satisfied customers
I am trying to replace an outlet. Red wire backstabbed high.
I am trying to replace an outlet. Red wire backstabbed high. Black wire back stabbed low. Black wire looped to screw low. My new outlet only has screws, no back stabs … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Gfci outlet was fried which caused the upstairs outlets in
Ok... so gfci outlet was fried which caused the upstairs outlets in the bathrooms not to work... pulled the old gfci switch, put a new one in, had the white wires on the neutral side and black on the … read more
Mike G.
Mike G.
Master Electrician
7,952 satisfied customers
Im trying to replace an electrical outlet with a USB outlet
Im trying to replace an electrical outlet with a USB outlet but I'm not sure if it can be done or how it should be done. Here are pictures.… read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
Wiring diagram for outlet on a switch the to a light on same
wiring diagram for outlet on a switch the to a light on same switch … read more
David Bowden
David Bowden
Owner
478 satisfied customers
Which wires go where? In replacing a switch and outlet in
Which wires go where? In replacing a switch and outlet in the bathroom I mistakenly didn't label the wires before I ran down to answer the door now I don't know where the three main lead wires into th… read more
Mike G.
Mike G.
Master Electrician
7,952 satisfied customers
I need to wire a switch and 2 outlets in same box) without
I need to wire a switch and 2 outlets in same box) without the switch controlling the outlets. The switch is for a ceiling light. Thanks. … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
1,052 satisfied customers
A range 4 prong outlet to a 3 wire cord. Today. Does the
yes, does the neutral wire go to t he white or ground? … read more
Mike G.
Mike G.
Master Electrician
7,952 satisfied customers
Question on wiring GFCI outlet... Late 80's...and no. Outlet
outlet is under the sink...bottom outlet goes to switch on the wall… read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
I have a wall outlet that has 220v 3phase in a 3 wire setup.
I have a wall outlet that has 220v 3phase in a 3 wire setup. I need to change it to a 3wire single phase setup … read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
12/3 wire goes to power a kitchen gfci outlet which protects
12/3 wire goes to power a kitchen gfci outlet which protects more outlets down line. The black wire is used there. The red wire goes to power the refrigerator. They are on 2 separate circuits. If I re… read more
Mike G.
Mike G.
Master Electrician
7,952 satisfied customers
Removing old outlet with three wires and a black plus
Removing old outlet with three white wires and a black plus ground. Also has a black and red wire pig tail and black and white oigtail in the box. Outlet connected to light switch … read more
Mike G.
Mike G.
Master Electrician
7,952 satisfied customers
Wiring a gfci outlet in kitchen (had old normal outlet) and
Wiring a gfci outlet in kitchen (had old normal outlet) and have disposal and over sink light in same box. Power comes into outlet. There are also 3 other lines leaving to other outlets in kitchen. Wa… read more
Mike G.
Mike G.
Master Electrician
7,952 satisfied customers
I have an outlet that is affecting wiring in other parts of
I have an outlet that is affecting wiring in other parts of the house. When I opened outlet I found two black wires and a white wire, in a wire nut and two bare white wires and a black wire. One whit … read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
Wiring garage have 14-3 and 14-2 wire going to outlet and
Wiring garage have 14-3 and 14-2 wire going to outlet and there is no ground how would you hook these up to sub panel… read more
Mike G.
Mike G.
Master Electrician
7,952 satisfied customers
My outlet had 2 black wires and a ground, no wire, it
Hi, my outlet had 2 black wires and a ground, no white wire, it connects to the internet when I have one black wire connected to BK and one connected to WH but does not operate the lights at all. … read more
Mike G.
Mike G.
Master Electrician
7,952 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.