I have an outside electric circuit on a pool pump. Water got

Customer Question
I have an outside electric...
I have an outside electric circuit on a pool pump. Water got into the conduit and now the GFI trips under load even though the water has been drained from the circuit. The circuit does not trip under no load. Any suggestions on what to check?
Submitted: 4 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 2 minutes by:
8/28/2013
Electrician: Mike G., Master Electrician replied 4 years ago
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 7,946
Experience: Proven Professional 49 years Experience
Verified
Hi, I'm Mike and I'll be glad to assist you. Disconnect the motor and try the GFCI again. You may have to dry out the motor as well.
Ask Your Own Electrical Question
Customer reply replied 4 years ago

The GFI trips under any load (although I haven't tried a very low load like a 10 watt lamp). I tried the heat gun and a rotary tool and it tripped under each load. It does not trip without a load.

Electrician: Mike G., Master Electrician replied 4 years ago
Where are you appling the load? At the breaker or on the circuit at the pump.
Ask Your Own Electrical Question
Customer reply replied 4 years ago


I am plugging the load into a new receptacle installed at the end of the circuit (at the pump location in a shed). I read 118 volts across the receptacle and also from the hot lead to ground. I read no voltage from the receptacle neutral to ground. The circuit worked fine before water got into the conduit but I changed the receptacle in order to raise it off the pump shed floor. The source of water was not in the pump shed, it was rain infiltration in the pull box near the house. The only other access I have to the wires is an intermediate pull box about half way from the house to the pump shed. I read the same voltages there.

Electrician: Mike G., Master Electrician replied 4 years ago
Let me suggest that you temp a receptacle at the panel on the GFCI. Now put a load that tripped it when you had it in the shed. If it hold, the breaker is good and there is a fault in the circuit. If it trips then the breaker has failed and needs to be replaced.
Ask Your Own Electrical Question
Customer reply replied 4 years ago

I'll try it. If there is a fault in the circuit, will it eventually dry out or will I need to pull new wire?

Electrician: Mike G., Master Electrician replied 4 years ago
What did you use for wire in the conduit?
Ask Your Own Electrical Question
Customer reply replied 4 years ago

Hard to remember, it was 20 years ago. Up to the first pull box where the water infiltrated it appears to be regular 3 conductor #12 wire (it has a white outer sheath). From that connection I pulled individual #12 wires because of the long run (it was easier to pull individual wires). None of it is gray covered outdoor cable.

Electrician: Mike G., Master Electrician replied 4 years ago
If ou used a NM cable, that is more than likely what faulted. If can only be indoors. Any wiring outside is considered a wet location and the circuit should be either a THHW or THW in conduit or a UF cable.
Ask Your Own Electrical Question
Customer reply replied 4 years ago


I'm 99% certain it's THHW or THW. The fact that it worked fine for 20 years until the rain infiltration is somewhat revealing. If it's THHW or THW should I give it more drying time before biting the bullet and pulling all new wire?

Electrician: Mike G., Master Electrician replied 4 years ago
Do the test that I suggested and let me know how it went. You said the cable had a white sheath, and that makes me think it was NM cable. If it was only means you were lucky for 20 years. If it is NM, replace it.
Ask Your Own Electrical Question
Customer reply replied 4 years ago

I will try the test. What I don't understand is why it only trips under load. If there is a fault in the circuit, wouldn't it trip without a load?


How do I get ahold of you after I try the test? It might be tomorrow.


 

Electrician: Mike G., Master Electrician replied 4 years ago
Just return to the last post, as you have been. The question remains open.
Ask Your Own Electrical Question
Customer reply replied 4 years ago


Ok - I'll let you know. Thanks for your help.

Electrician: Mike G., Master Electrician replied 4 years ago
You're welcome.
Ask Your Own Electrical Question
Customer reply replied 4 years ago
Mike - the problem is solved. Actually it's not solved yet but I know where the circuit fault is. Prompted by your suggested test, instead of hooking up a load at the GFI circuit breaker, I tried the load at the intermediate junction/ pull box that I mentioned earlier about 3/4 of the way between the house and the pump shed. The GFI held so the fault was between this box and the shed. I ran a new temporary feed from this box to the shed and the circuit is running.

Although the original problem was water infiltration into a junction/pull box at the house, the new fault was not caused by the water. I assume that when I raised the receptacle I nicked two or three wires when I hand cut the 3/4 inch conduit to add the new riser. I was carefully, but not careful enough. So now I'll pull new wire through this 25 foot run for the permanent fix.

I still don't understand why it held until a load was applied. Do you have an explanation for that? By the way, I am satisfied with your help.
Electrician: Mike G., Master Electrician replied 4 years ago
I can't say for sure why it held, except that it was Murfey's Law. Glad it's resolved.
Ask Your Own Electrical Question
Customer reply replied 4 years ago
Satisfied
Electrician: Mike G., Master Electrician replied 4 years ago
Please hit one of the rating selections to close the question. Thanks.
Ask Your Own Electrical Question
Ask Mike G. Your Own Question
Mike G.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 7,946
7,946 Satisfied Customers
Experience: Proven Professional 49 years Experience

Mike G. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,942 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,946 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Need GOULD Circuit Breaker Panel size 14WX42H. 1983. Just
just panel should not need electrician I am electric engineer myself … read more
George Smith
George Smith
Vocational, Technical or Trade School
322 satisfied customers
I checked all circuit breakers to see if any tripped. I
Hi, I checked all circuit breakers to see if any tripped. I reset all of them and checked voltage. They are all receiving power. So I changed the 2 outlets that went out on the side of one room. Still… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have a problem with a circuit breaker tripping fairly
I have a problem with a circuit breaker tripping fairly regularly. I believe I have too many plugs on one circuit. How can I check to see if I have too many on one breaker. I have done a lot of wiring… read more
George Smith
George Smith
Vocational, Technical or Trade School
322 satisfied customers
My microwave flips a circuit breaker when I turn it on. It's
my microwave flips a circuit breaker when I turn it on. It's in the same location, same outlet, same everything. The outlet works with other things, like vacuum, elec light. The microwave works perfec… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Circuit breaker blew switch. Switch is not resetting. Just
Circuit breaker blew switch. Switch is not resetting. Just kinda dangles there, with no tension to either side. How can I fix this?… read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
The circuit breaker hasn't popped but in living room non of
The circuit breaker hasn't popped but in living room non of the 4 outlets are working. Checked the 4 plugs for any signs of loose wires or spark marks. ? What's next? … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I'm wiring a 230v compressor motor, and need to verify that
I'm wiring a 230v compressor motor, and need to verify that I have wires properly combined. I will provide motor information below. Thank youMake: Steveco Farm Duty Model: MS182C17FB2A Labeled Wires P… read more
George Smith
George Smith
Vocational, Technical or Trade School
322 satisfied customers
I want to remove a double circuit breaker from electrical
i want to remove a double circuit breaker from electrical panel … read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
Can a General Electric type THQL-GCI hot tub circuit breaker
can a General Electric type THQL-GCI hot tub circuit breaker be tested with an ohm meter. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
What is the function that makes a circuit breaker different
what is the function that makes a circuit breaker different from a switch so that it is able to break fault current … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Was wondering which circuit breaker I should look into
Hello, was wondering which circuit breaker I should look into replacing. As it stands my Dryer flips the circuit breaker for the upstairs bedrooms. Should I look into replacing the circuit breaker for… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
My circuit breaker is tripped and will not reset. I've
My circuit breaker is tripped and will not reset. I've checked wiring to outlets looks okay. At the electrical panel there is no power to breaker itself. I check other breakers and the have power. Any… read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
1,050 satisfied customers
Honda EU7000is has 30 amp line with circuit breaker with
Honda EU7000is has 30 amp line with circuit breaker with each line up to 22.6 amps. Questions is 32 amp draw too large and will trip circuit breaker and can circuit breaker be upgraded to 40 amp to al… read more
Sam I
Sam I
Electrician
B.S.
474 satisfied customers
I have a well pump wired into a 240v/20a circuit breaker. C/
I have a well pump wired into a 240v/20a circuit breaker. C/B has white wire, black wire, ground wire. Pressure switch on well pump has same...black, white. ground. Output from pressure switch to pump… read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
Need help determining wire size, wire type, and conduit size
Need help determining wire size, wire type, and conduit size for 200amp panel with a 200 amp subpanel. Here is a list of my questions: http://mnjustin.com/diagram.jpg… read more
Mike G.
Mike G.
Master Electrician
7,946 satisfied customers
The circuit breaker tripped controlling all the electricity
The circuit breaker tripped controlling all the electricity in my son's bedroom. This circuit also controls the recessed lighting in the dining room. The only way I can reset the circuit breaker is if… read more
Mike G.
Mike G.
Master Electrician
7,946 satisfied customers
What size wire is needed to run underground in conduit to a
What size wire is needed to run underground in conduit to a garage about 60 feet from the main connection at the power pole? This would be connected to a subpanel in the garage. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
What is the nec for wiring a control panel circuit breaker.
What is the nec for wiring a control panel circuit breaker. Can you feed the line into the bottom and have the load come out the top of the breaker… read more
George Smith
George Smith
Vocational, Technical or Trade School
322 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x