Can I put a 125 amp breaker in a 100 amp panel box that is outside on a pole.
Submitted: 5 years ago.Category: Electrical
Ask Your Own Electrical Question
Answered in 5 minutes by:
6/3/2012
Electrician: Jason, Service Technician replied 5 years ago
Jason
Jason, Service Technician
Category: Electrical
Satisfied Customers: 4,289
Experience: Over 20 years of experience in all types of installations, troubleshooting, and repairs.
Verified

Jason :

Hello. Welcome to Just Answer.

Jason :

Is there a 100 amp rating stamped inside the panel?

Jason :

Are you trying to replace an existing 100 amp main breaker in the outdoor panel?

Customer:

are you there?

Jason :

I'm here. Can you see this text?

Customer:

Yes, I believe I will be fine with staying with the 100 amp breaker but if I can go to the 125 amp breaker, I know I will be.

Jason :

The only problem with upgrading the breaker is that it would be a Code violation if the panel's bussbars are only rated at 100 amps. If there is a 100 amp rating stamped somewhere inside the panel, I would not put the larger breaker in.

Customer:

I guess what I am saying is I doubt I will even draw 100 amps on this line, I just wanted a little more so it would not trip the 100 if it went over a little.

Jason :

I understand. What all will you be feeding with the panel?

Customer:

Electric stove, dishwasher, fridge, washer, dryer, split system air conditioner which I was told would only draw about 27 amps, I was told to install 10-2 wire for the AC with a double pole 30 amp breaker.-- there are about 10 lights and two ceiling fans, tv, and misc small appliances

Customer:

oh and a microwave

Jason :

It sounds like a lot of load, but most of it won't be on concurrently. I suspect you

Jason :

will be fine with the 100 amp main.

Customer:

and hot water heater and well pump

Jason :

Technically, to go up to the 125, you would need to upsize the wire coming into the house. You must have branch circuit protection inside the house, correct? Is the breaker that's out on the pole in a box by itself? If so, is the branch circuit panel in the house, with only main lugs, and no main breaker?

Customer:

do you think this load if I install the 125 amp breaker would cause it to get hot enough to melt?

Jason :

No, that's not likely.

Customer:

no main breaker inside

Customer:

power will be supplied by breaker on outside of box on pole

Jason :

OK, in that case, the wire from the outside main breaker to the interior main lugs needs to be rated for 125 amps, in order to legally upsize the breaker. The box on the pole would also need to meet or exceed the rating of the breaker it contains.

Customer:

Will it work ?

Jason :

I would plan on using the existing 100 amp breaker. If it trips, which I doubt it will, you will need to upgrade more than just the breaker itself. In order to comply with Code, the breaker enclosure, and possibly the wire from the pole breaker to the house panel will need to be upsized.

Customer:

so you think I will be fine staying with the 100amp breaker. But if I did change to a 125 amp breaker, do you think it would cause a fire or cause something to melt. I know I am putting you a in bad place and ultimately I make the decision . my choice my responsibility. I release you from any liability.

Customer:

David S Sullivan

Jason :

I think the breaker would most likely trip on overload, but it's really difficult to know for sure.

Customer:

Thank you. I understand.

Jason :

You are most welcome. Is there anything else I can do for you?

Customer:

thanks.

Jason
Jason, Service Technician
Category: Electrical
Satisfied Customers: 4,289
Experience: Over 20 years of experience in all types of installations, troubleshooting, and repairs.
Verified
Jason and 87 other Electrical Specialists are ready to help you
Ask your own question now
Ask Jason Your Own Question
Jason
Jason
Jason, Service Technician
Category: Electrical
Satisfied Customers: 4,289
4,289 Satisfied Customers
Experience: Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Jason is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

4,289 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Wiring the bath.. .should I put the ceiling fan and vanity
Wiring the bath.. .should I put the ceiling fan and vanity light behind the gfci load or should I leave any of those on the line side?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Harbor breeze has a ceiling fan and light kit with a wattage
Harbor breeze has a ceiling fan and light kit with a wattage limiter that I would like to remove. It limits the bulbs to 3 40-W incandescent equivalent bulbs which is way too low to light the room ade… read more
George Smith
George Smith
Vocational, Technical or Trade School
311 satisfied customers
I have 2 Hunter ceiling fans with lights. The light sockets
I have 2 Hunter ceiling fans with lights. The light sockets are POS.... I have replaced both with Hunter replacement parts and have the same issue. … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
We just attempted to install a new ceiling fan, which came
hi. We just attempted to install a new ceiling fan, which came with a remote. We don't plan on using the remote though. We removed the old ceiling fan and now this new one won't work on the the 3 swit… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Installing a ceiling fan with a remote, only one switch,
Installing a ceiling fan with a remote, only one switch, wiring in the ceiling has black, red, white and ground, how do I wire this? When I disconnect the red and hook up the black, the fan works but … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
My Mother has a old ceiling fan in her family home that she
My Mother has a old ceiling fan in her family home that she wants to keep , how do i remove it? is it easy to do? I will attach a photo.… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I am trying to replace a cbb6-1 capacitor in a ceiling fan
i am trying to replace a cbb6-1 capacitor in a ceiling fan the company, Craftmade sent me TWO capacitors, both marked cbb6-1. the orginal fan has one larger capacior … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I am installing a ceiling fan. The new fan has push in
I am installing a ceiling fan. The new fan has push in connectors (one white and one red). I have one black, one red and one white plus a bare ground wire coming out of the ceiling. What do I do with … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Ceiling fan light goes off by itself, fan stays on. Light
Ceiling fan light goes off by itself, fan stays on. Light comes back on once i flick the switch a few times. (i hear a click from the fan when it's ready to go back on) There is also an outlet in the … read more
mstr_elec
mstr_elec
25 satisfied customers
I NEED A REPLACEMENT LIGHT GLOBE FOR TILGHMAN CEILING FAN,
I NEED A REPLACEMENT LIGHT GLOBE FOR TILGHMAN CEILING FAN, ITEM(###) ###-#### MODEL WCK52NWZ5N. NO PARTS AT LOWES OR HOME DEPOT. … read more
David Bowden
David Bowden
Owner
463 satisfied customers
I have a Harbor Breeze 2 blades ceiling fan. The light bulb
Hi I have a Harbor Breeze 2 blades ceiling fan. The light bulb glass thing broke and I am trying to find a replacement. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
The ceiling fan is wired direct no switches no dimmer as far
The ceiling fan is wired direct no switches no dimmer as far as I know we put in the bulbs and the light kit is like a strob light flashes on and off … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I'm attempting to install a ceiling fan with a wall
I'm attempting to install a ceiling fan with a wall controller. My existing box has a single pole toggle switch that is fed to the ceiling where the fan will be hung. It is new construction and there … read more
George Smith
George Smith
Vocational, Technical or Trade School
311 satisfied customers
I have a ceiling fan with a wall switch for the light and
I have a ceiling fan with a wall switch for the light and separate 4 speed switch for the fan. The speeds and numbers don't correspond to each other. The fan never goes as fast as the two exact matche… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
We had a Chandelier that was changed to a ceiling fan, and
We had a Chandelier that was changed to a ceiling fan, and two older sconces that were updated to newer ones. The problem is that one of the sconces is coming on when the breaker is turned on, and won… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
The ceiling fan in our bedroom sparked and died. The light
The ceiling fan in our bedroom sparked and died. The light still worked. I thought that a wire had rubbed through from vibrations over the years. I replaced the whole ceiling fan and turned it on. The… read more
George Smith
George Smith
Vocational, Technical or Trade School
311 satisfied customers
Casablanca remote control ceiling fan light blinks on and
Casablanca remote control ceiling fan light blinks on and off … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Wiring a ceiling fan.....one, wiring a ceiling fan...from
wiring a ceiling fan...from the ceiling: one re wire, two white wires twisted together. Fan has one black, one white, one other thinner black wire. How to connect? … read more
George Smith
George Smith
Vocational, Technical or Trade School
311 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x