Does flexiable conduit for a service entrance meet code

Does flexiable conduit for a service entrance meet code
Ask Your Own Electrical Question
Answered in 1 minute by:
11/3/2011
AssuredElectrical
AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 4,241
Experience: Contractor-42+ Years in the ElectricalTrade
Verified

AssuredElectrical :

Hi, Welcome to Just Answer. My name is XXXXX XXXXX would be glad to assist.

AssuredElectrical :

Is this the riser to connect weather head from power company?

Customer:

This is a rural setting. The meter is at the pole. So the overhead runs from the pole to the home where it is attached at the second story. Then service then runs done the side of the home in flexiable conduit to where the service enters the home and into the panel.

AssuredElectrical :

Flexible metal conduit is limited to 6 foot length in any application.

AssuredElectrical :

240.43 NEC

AssuredElectrical :

230.43 Wiring Methods for 600 Volts,
Nominal, or Less
Service-entrance conductors shall be installed in accordance
with the applicable requirements of this Code covering the
type of wiring method used and shall be limited to the following
methods:
(1) Open wiring on insulators
(2) Type IGS cable
(3) Rigid metal conduit
(4) Intermediate metal conduit
(5) Electrical metallic tubing
(6) Electrical nonmetallic tubing (ENT)
(7) Service-entrance cables
(8) Wireways
(9) Busways
(10) Auxiliary gutters
(11) Rigid polyvinyl chloride conduit (PVC)
(12) Cablebus
(13) Type MC cable
(14) Mineral-insulated, metal-sheathed cable
(15) Flexible metal conduit not over 1.8 m (6 ft) long or
liquidtight flexible metal conduit not over 1.8 m (6 ft)
long between raceways, or between raceway and service
equipment, with equipment bonding jumper
routed with the flexible metal conduit or the liquid

AssuredElectrical :

tight flexible metal conduit according to the provisions
of 250.102(A), (B), (C), and (E)
(16) Liquidtight flexible nonmetallic conduit

AssuredElectrical :

Section 230.43(15) and (16) permit no more than 6 ft of
flexible metal conduit or liquidtight flexible metal conduit to
be used as a service wiring method. Because of the high levels
of fault energy available on the line side of the service
disconnecting means, a bonding jumper must be installed
where these raceway types are used for service conductors.
The bonding jumper is allowed to be installed inside or outside
the raceway, but it must follow the path of the raceway
and cannot exceed 6 ft in length. In order to minimize the
impedance of the ground fault current return path, the bonding
jumper must not be wrapped or spiraled around the flexible
conduit.

Customer:

I have not measured this but from the photo I have it is over 12 foot I see your reply is there away I can print it. This is just what I am looking for. GREAT JOB!

AssuredElectrical :

Try the copy and paste into a notepad or word program..

AssuredElectrical :

I use notepad, but other programs work also

Customer:

I just did. I own an Insurance Agency and I am on the board of directors of an insurnace company. This was GREAT and I will use this serives again. Tom Powers

AssuredElectrical :

You are very welcome. Been a pleasure. If your are satisfied with my answers , please do
click the Accept for my time.You can come back to this page anytime.

AssuredElectrical
AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 4,241
Experience: Contractor-42+ Years in the ElectricalTrade
Verified
AssuredElectrical and 87 other Electrical Specialists are ready to help you
Ask your own question now
Customer reply replied 6 years ago
Please tell me what type of conduit this is in the attached photos.
Customer reply replied 6 years ago
I was unable to attach the photos graphic
Customer reply replied 6 years ago
graphic
OUCH. That is NOT a conduit of any type. That is the actual service cable run up the side of the house.
I do not know what year that was installed to tell you whether it was proper at the time or not.
Todays installations does not allow such.
Ask Your Own Electrical Question
Customer reply replied 6 years ago
I know the photos are not very good but the cables are running inside this conduit. When I first looked at this I said the same thing. The person that owns the home is an electrical engineer and he tells my agent that this is schedule 40.
Customer reply replied 6 years ago
I know the photos are not very good but the cables are running inside this conduit. When I first looked at this I said the same thing. The person that owns the home is an electrical engineer and he tells my agent that this is schedule 40. I think I need to call the owner and ask him what it is. I have been in the insurance business 37 years and have not seen this before. I was rised in a family of electrical workers my father was the oldest living member of the electrical workers union when he passed away.
I can say that it is CABLE and not conduit for sure.
AssuredElectrical
AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 4,241
Experience: Contractor-42+ Years in the ElectricalTrade
Verified
AssuredElectrical and 87 other Electrical Specialists are ready to help you
Ask your own question now
Customer reply replied 6 years ago
I think the only thing I can do at this point is to get a reply from the owner. If I find out that this is some type of conduit I will let you know is you wish. I know it is hard for you to see but at the very top you can see where the black cable runs into these white where ever it is.
The black cables you see are the wires in the cable. There are 2 black and 1 bare. I assure you that that is service cable run on the outside of the house. There is No conduit. Conduit is ROUND, the cable is FLAT.
Ask Your Own Electrical Question
Ask AssuredElectrical Your Own Question
AssuredElectrical
AssuredElectrical
AssuredElectrical, Master Electrician
Category: Electrical
Satisfied Customers: 4,241
4,241 Satisfied Customers
Experience: Contractor-42+ Years in the ElectricalTrade

AssuredElectrical is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,425 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,940 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,603 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,715 satisfied customers

30 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

4,241 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Can I add a 90 elbow to the main conduit so that I can raise
can I add a 90 elbow to the main conduit so that I can raise that conduit the conduit is running vertical and i need some height under the conduit … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
Need to wire a 240 volt single phase 3 wire motor. Just
the motor has 2 connections for the hot wire and also has a common… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have 3 black wires and 3 wires and 1 coming out of
I have 3 black wires and 3 white wires and 1 white coming out of electrical outlet, how t … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
I have a sauna that is wired with 240 two wire for load (red
I have a sauna that is wired with 240 two wire for load (red and black) and a ground -- the neutral line (white) is not used -- currently it is not on a GFI and I would like to put it on a GFI - I wou… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
TROUBLE WIRING A LEVITON 6683. I HAVE ONE HOT WIRE BLACK/
I AM HAVING TROUBLE WIRING A LEVITON 6683. I HAVE ONE HOT WIRE BLACK/ WHITE /GROUND. I AM TRYING TO WIRE 2 /6683 SWITCHES OFF THIS WIRE TO GO TO DIFFERENT LIGHTS … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Wondering if I can run wires that are not mounted on studs
Wondering if I can run wires that are not mounted on studs in wall in the state of VA? … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
Had broken wire from outside breaker. changed wire to
had broken wire from outside breaker. changed wire to copper. 60 amp breaker trips when power is turned back on. disconnect wire on 60 amp wire and still have voltage in disconnected wire … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
How do I wire a motion sensor with black and supply wires,
Hi! How do I wire a motion sensor with black and white supply wires, red (or pink) light wires and red, blue and brown sensor wires? Thanks. … read more
Sam I
Sam I
Electrician
B.S.
364 satisfied customers
I have a dedicated 10 amp romex line in conduit, going to a
I have a dedicated 10 amp romex line in conduit, going to a direct wired garbage disposer under my kitchen sink. I want to connect this line up to a single gang outlet box to make exchanging the dispo… read more
Sam I
Sam I
Electrician
B.S.
364 satisfied customers
I am running 3 circuits inside of pvc conduit. 220v 30a
I am running 3 circuits inside of pvc conduit.220v 30a water heater 220v 15a ac 120v 20a receptaclecan I use 1 shared 10awg ground wire for all circuits?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Are the wires from the main box to a jump box sapose to be
are the wires from the main box to a jump box sapose to be in riggid conduet … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Wiring garage have 14-3 and 14-2 wire going to outlet and
Wiring garage have 14-3 and 14-2 wire going to outlet and there is no ground how would you hook these up to sub panel… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Need help determining wire size, wire type, and conduit size
Need help determining wire size, wire type, and conduit size for 200amp panel with a 200 amp subpanel. Here is a list of my questions: http://mnjustin.com/diagram.jpg… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
How much to install 100' of electrical line in a conduit if
how much to install 100' of electrical line in a conduit if the trench is already dug. Include the cost of wiring and adding a 50 Amp Circuit Breaker … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
What size wire is needed to run underground in conduit to a
What size wire is needed to run underground in conduit to a garage about 60 feet from the main connection at the power pole? This would be connected to a subpanel in the garage. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
Do you need to remove existing conduit and or conductors if
Do you need to remove existing conduit and or conductors if they are being abandoned and not being used? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,603 satisfied customers
Can I use the conduit that leads into the panel box by
Can I use the conduit that leads into the panel box by adding a second pair of wires to be connected to another circuit breaker? Easier to do than setting up another separate conduit attachment? I kno… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
I have a black, and wire in mtl. conduit. It appears that
I have a black, white and green wire in mtl. conduit. It appears that the green wire is the hot wire. Do I hook this to the side of the plug with the brass screws. Which wire is likely to be the groun… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,715 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x