I installed a GE digital smart timer at a customer. It disregards…

Customer Question
I installed a GE digital...
I installed a GE digital smart timer at a customer. It disregards XXXXX XXXXX and turns on and off with a mind of its own. I also saw it exhibit this behavior while wired into the house with the breaker off. The unit has a battery so you can program and read the display with no line AC. I connected the same timer to a 3 prong plug and a light socket at home and it worked fine. I brought this same configuration to the customer's house and plugged it in while I worked on something else. It worked fine for about 3 hours but then started turning on and off every minute or so like it had done previously. I saw the same behavior from another unit.
Submitted: 8 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 1 hour by:
6/30/2010
Electrician: Mike G., Master Electrician replied 8 years ago
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,426
Experience: Proven Professional 49 years Experience
Verified
Hi, I'm Mike and I'll be glad to assist you. Two things come to mind with regard to your problem,

1) Possibly the feed hot and the switched hot wires are reversed.
2) or, your neutral is making and breaking.

Check and advise
Ask Your Own Electrical Question
Customer reply replied 8 years ago
1) Hot and switched are not reversed. I have been told by Jasco (tech support for GE) that this is the only known cause of the problem that I describe. I reversed hot and switched to see if it would behave in a similar manner. It did not. It simply did not work. It returned to normal operation when I connected hot and switched correctly.

2) Maybe neutral is making and breaking. If so then it is not enough to visibly affect the light when a normal switch is used. Also I saw this problem on 2 different circuits.
One cirucit was the original light cirucit. This circuit seems to affected all the time
The other circuit was a garage plug circuit into which I pluged my test set up. This circuit seems affected intermittently.


My theory is that there is noise on either ground or neutral that is scramblig the smart timer processor. Since I saw the problem with the CB off, I am inclinded to think the problem is not on the hot but I cannot discard that possibility.

I also asked the homeowner if there were any signal over the powerline devices in the house and he said there were none.
Electrician: Mike G., Master Electrician replied 8 years ago
The only thing I could suggest due to the situation, is that you replace the timer with an Intermatic Timer not requiring a neutral. That would eliminate one possible cause and end the problem.
Ask Your Own Electrical Question
Customer reply replied 8 years ago
Mike,

The Intermattic 2 wire timer suggestion is something I can try among several other things.
If the problem is noise on the hot then this won't solve my problem.
I assumed that I wasn't the 1st person to run encounter this problem.
I may put a scope on line, neutural and ground. If I see funny stuff in the panel then I can call the power company.

As work arounds, I can use the timer you suggested or another that works on the old fashioned turning wheel principle.

I have seen other references to this problem on the internet. If you find why this has happened to someone else (and it's not wrong connections) then I will be happy to accept the answer.
Electrician: Mike G., Master Electrician replied 8 years ago
The only other suggestion I can offer is that you check to see if the wiring is switching the neutral. If it has reversed polarity, this could be the cause of the malfunction.
Ask Your Own Electrical Question
Customer reply replied 8 years ago
Line and neutral are OK. I've checked on several outlets including the one where I saw the peculiar behavior with my test setup. This is going to be a tough one. I used to work in tech support. It happens sometimes. However, I'm pretty sure the answer is out there somewhere. I just can't find it with Google.
Electrician: Mike G., Master Electrician replied 8 years ago
I've done a fair amount of work with Leviton Intelesense Controls. So I know what your concern is with noise on the line and signal at zero. I don't think that either are pertinent to your problem. I'd try the intermatic timer if it were my job.
Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Mike G. Your Own Question
Mike G.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,426
8,426 Satisfied Customers
Experience: Proven Professional 49 years Experience

Mike G. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,426 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,414 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I purchased a dryer in January, and GE replaced it under
I purchased a dryer in January, and GE replaced it under warranty because the circuit board kept getting fried. When the new dryer was delivered, it would not turn on. Multi-meter showed 245v at the p… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
Hi. I bought a GE 15318 Push Button In-wall Countdown Timer
Hi. I bought a GE 15318 Push Button In-wall Countdown Timer switch and installed it. Did not work. I have the hot connected to hot, red to load, green to a good ground (and then even grounded to a cop… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,426 satisfied customers
hi there. I just got a new/used dryer with a 4 prong plug.
hi there. I just got a new/used dryer with a 4 prong plug. my house has a 3 prong outlet. can i change the plug. ive bought a replacement 3 prong plug but am having second thoughts… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
HAVE GE 15070, 24 HOUR TIMER INSTALLED ON OUTSIDE LIGHTING
HAVE GE 15070, 24 HOUR TIMER INSTALLED ON OUTSIDE LIGHTING CIRCUIT. NEUTRAL IS "BACKFED" FROM CIRCUIT OTHER THAN HOT WIRE, ALL WORKED FINE FOR 2 YRS. TODAY INSTALLED 110V GROUNDFAULT OUTLET IN CIRCUIT… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,426 satisfied customers
I configured GE digital timer with 6 LED 10W potlights to turn
I configured GE digital timer with 6 LED 10W potlights to turn on the lights at 6 PM and turn it off at 10 PM. It works well, but the timer turns the lights off after 5 - 10 minutes. The first time, i… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,426 satisfied customers
ge smart digital timer install and when I push the cover to
ge smart digital timer install and when I push the cover to manually over ride the timer and turn the light on the timer turns the relay on and off continually making the light flash. The relay is loc… read more
Alex
Alex
Owner
Bachelor\u0027s Degree
1,783 satisfied customers
Hi. I have a two GE Smart digital timers. One is model 15312
Hi. I have a two GE Smart digital timers. One is model 15312 and one is model 15086. Opened the 15312 box last night and was trying to connect to the switch (inside the house) which controls the outsi… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,426 satisfied customers
I just bought a GE Smart Digital Timer model 15071. I would
I just bought a GE Smart Digital Timer model 15071. I would like to use this timer in a 3-way setup (a switch by my front door and a switch in my garage both turn out outside lights on and off). Can t… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,426 satisfied customers
For many years I have had an Intermatic Time-All, Model TB111.
For many years I have had an Intermatic Time-All, Model TB111. Now it has become hot so I know it's time to replace it. My question is that I want a new one to function exactly the same as the old one… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
I have an old house with 2 wire outlets white and black, I
I have an old house with 2 wire outlets white and black, I want to install a GE Smart Digital Timer, but it has 4 wires, Red White Black and Green. Green I can ground to the box, White to White, Black… read more
Kevin
Kevin
Owner
High School or GED
258 satisfied customers
Hello. I have a 12v fan that I plug into the cigarette socket
Hello. I have a 12v fan that I plug into the cigarette socket in my truck to work. The cord is pretty heavy duty, similar to an electrical cord. Is it possible to slice in a regular two prong house el… read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
Just bought a Smart Digital timer for my front porch light.
Just bought a Smart Digital timer for my front porch light. Removed the old switch and all the wires are black (or appear to be from being so old). The switch only had 2 screws - 1 wire connected to t… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,426 satisfied customers
I have a GE Digital Timer 15086 with four wires on the time
I have a GE Digital Timer 15086 with four wires on the time: white, black, red, green. The wall electrical switch box has one two-wire cable (black and white), with a bare ground. I wired it as follow… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,426 satisfied customers
Trying to hook up a four wire timer where I originally had
Trying to hook up a four wire timer where I originally had an on off switch. Can't seem to locate a neutral wire in the junction box (though there is an unconnected black wire in addition to the groun… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,426 satisfied customers
GE DT300 digital timer 15091. Bought 4 of them last Christmas,
GE DT300 digital timer 15091. Bought 4 of them last Christmas, now they do not have anything on the screen. Do they need to charge? Are there batteries inside?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,426 satisfied customers
I have two GE Smart Digital Timers installed for my outside
I have two GE Smart Digital Timers installed for my outside lights. Both have stopped working after only two years. Even the display is completely blank. Pushing on the cover to override will not turn… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,426 satisfied customers
I installed two GE smart timers last fall in our winter home.
I installed two GE smart timers last fall in our winter home. They worked fine theu the winter and in july when we visited a few days but now both of them will not work at all. If I press the reset bu… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,426 satisfied customers
I need to install a GE Smart Digital Timer for an outside light.
I need to install a GE Smart Digital Timer for an outside light. The light has two switches (which I believe means its three phase?). Connecting black to black, red to red and white to white doesn't s… read more
Craig
Craig
Electrical Director
Electrical Automation Technician
2,133 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x