I am slightly renovating 2 bathrooms. I am adding 2 exhaust fans - each pulls approx. 2 amps - and 4 overhead/vanity lights.

I have a 30amp breaker with # XXXXX wire not being used in my box. It is terminated in a junction box in my attic.

I would like to come off the junction box (#10) in the attic with 2 - #12's to 2 junction boxs near each of the 2 bathrooms - approx 15 feet. I would then run 14/2 to each of the fans and lights.

Is this a good plan or bad plan?
Submitted: 8 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 4 minutes by:
6/29/2010
Electrician: Mike G., Master Electrician replied 8 years ago
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,427
Experience: Proven Professional 49 years Experience
Verified
Hi, I'm Mike and I'll be glad to assist you.

1) Is the 30A breaker 120V or 240V?
2) Is the #10 - 2 or 3 wire w/ grd?
3) Are you going to also wire in a GFCI receptacle in each bath?
Ask Your Own Electrical Question
Customer reply replied 8 years ago
The 30 amp breaker is a double and was supplying a 240v water heater. It has a black and white #10 wire attached.

The breaker appears like it can be "Un-doubled" or what ever the correct term is - so that it can be used as 2 30 amp breakers.

I plan on "Un-doubling" the breaker, removing the white wire and placing it with the other commons on the common bar. I will do nothing with the other side of the breaker.

The wire is romex with 2 conductors and a ground.

Each bath currently has GFCI's. just adding fans and lights.
Electrician: Mike G., Master Electrician replied 8 years ago
OK, let's proceed,

4) The circuit will need to have over current protection not exceeding 15 Amps. Using the 14/2 is the determining factor. Remove the 2 pole 30Amp breaker and install a 15A single pole for the circuit.

5) Move the white #10 to the neutral bar.

6) forget the use of 12/2. It doesn't need to any larger than 14/2.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,427
Experience: Proven Professional 49 years Experience
Verified
Mike G. and 87 other Electrical Specialists are ready to help you
Ask your own question now
Customer reply replied 8 years ago
It's not a good idea to hook up a #10 to a 15 amp breaker is it? Everything I've been taught says no.2

I would like to make each of the baths home runs back to the box with 15amp breakers, but getting new wires into the box is almost impossible.

Electrician: Mike G., Master Electrician replied 8 years ago
You only have one 120V circuit in 10/2 cable. The fact that you're going to use it for that precludes its use for two circuits. You can fuse the 10 wire for 15 Amps. You just can't have 14/2 on a 30A circuit.
Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Mike G. Your Own Question
Mike G.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,427
8,427 Satisfied Customers
Experience: Proven Professional 49 years Experience

Mike G. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,427 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,414 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
Ing my bathroom renovation. Got most of it done, but now its
Hello, I am DIY 'ing my bathroom renovation. Got most of it done, but now its time for electrical. Would need some help with a wiring diagram from an expert. I wanted add (if possible) a 3-bulb vanity… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,427 satisfied customers
In my bathroom, I have a double gang box with 12-2 running
In my bathroom, I have a double gang box with 12-2 running in from attic junction box. I have 1 switch going to a vanity light. I am going to get a 3 switch to run fan, light, nightlight combo. Will i… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
We have 2 story home plan is to install bathroom exhaust fans
We have 2 story home plan is to install bathroom exhaust fans supposedly this requires a extra 20 amp circuit to attic gfci protected,we have hear approx 350 for extra ckt.Generally speaking what may … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
Adding a ceiling fan to a bedroom with no light fixture. Trying
Adding a ceiling fan to a bedroom with no light fixture. Trying to plan the wiring. My options are to either to tap in to the bedroom receptacle circuit (20 amp). This would involve me running wire to… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
Hi, I am doing a bathroom remodel (total gut to studs) and
Hi, I am doing a bathroom remodel (total gut to studs) and am adding a ventilation fan as it did not exist before. I do not have an electrical source I can junction into in the attic (at least none I … read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
Im trying to connect a Nutone exhaust fan,light and nitelight
I'm trying to connect a Nutone exhaust fan,light and nitelight in my bathroom. There is 14/2 (2 wires 1black,1 white) going into a junction box in the attic. Coming out from the junction box to the sw… read more
Alex
Alex
Owner
Bachelor\u0027s Degree
1,783 satisfied customers
Trying to install bathroom exhaust fan. The light switches
Trying to install bathroom exhaust fan. The light switches on and off properly by the switch, but fan stays on. Junction box in ceiling has 2 blacks, 1 white and a red. I connected the whites all toge… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,427 satisfied customers
In my bathroom, from a switch, I would like to wire an overhead
In my bathroom, from a switch, I would like to wire an overhead light fixture and on the far wall (near the bathroom mirror) an unswitched GFI outlet. How can I accomplish that?… read more
Alex
Alex
Owner
Bachelor\u0027s Degree
1,783 satisfied customers
Adding bathrm exhaust fan w/light--no ceiling wiring/light
Adding bathrm exhaust fan w/light--no ceiling wiring/light now. Plan/Question: Now, 5X8 room 3-light (60wattx3) strip over vanity, junction box centered w/all blk&whites pigtailed, overcrowded octagon… read more
Sir Sparks
Sir Sparks
Owner
State & UK Certified Master electri
2,519 satisfied customers
Good Morning......I have a bathroom that needs a ventilation
Good Morning......I have a bathroom that needs a ventilation fan. I would like to wire it to be powered on when one of the lights goes on. The existing light has a wire coming from the switch and goin… read more
Alex
Alex
Owner
Bachelor\u0027s Degree
1,783 satisfied customers
My bathroom does not have a GFCI receptacle next to the sink.
My bathroom does not have a GFCI receptacle next to the sink. There is a regular receptacle in its place. I bought a 20 Amp GFCI receptacle. After removing the cover, I noticed that the lead wire is r… read more
Rich
Rich
Master Electrician
Vocational, Technical or Trade Scho
1,117 satisfied customers
Can I put a 20 Amp tandem breaker in a panel box and have a
Can I put a 20 Amp tandem breaker in a panel box and have a 12-2 wire go to a grinder and a tank alarm in a double gang (two outlets) one for each and have a GFI at the end of the line..Then use the o… read more
Mike
Mike
Master Electrician
Working on MBA
1,426 satisfied customers
Hello. I just finished installing exhaust fans with lights
Hello. I just finished installing exhaust fans with lights in two bathrooms. Each installation was the same as follows. I had an existing light over the sink (wall light) with single switch (a single … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,427 satisfied customers
I have a 15A circuit which contains a single receptacle and
I have a 15A circuit which contains a single receptacle and two light switches for vanity and overhead light/exhaust fan in a bathroom, an overhead hallway light which has a 3-way switch at each end, … read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
Here is my situation. I am adding a new bathroom to my Sons
Here is my situation. I am adding a new bathroom to my Son's house, in the basement. It looks like this. 20A homerun from panel(all 12G wire), to junction box, to GFCI outlet(double). From there, to, … read more
Rich
Rich
Master Electrician
Vocational, Technical or Trade Scho
1,117 satisfied customers
I am installing a Fantech ventilation fan in my attic which
I am installing a Fantech ventilation fan in my attic which will ventilate two 2nd floor bathrooms. I would like to run a new circuit from my electrical box in the basement to power the fan and bathro… read more
Paul
Paul
Owner
Vocational, Technical or Trade Scho
51 satisfied customers
I have the ability to wire a bathroom addition however i want.
I have the ability to wire a bathroom addition however i want. Should I start with the main overhead light switch in the bathroom, then go to the light and then continue on? Will the light switch have… read more
Glenn
Glenn
Maintenance, Technician
Associate Degree
1,612 satisfied customers
Wiring a bathroom circuit and getting a little confused now.
Wiring a bathroom circuit and getting a little confused now. Pulled the wire to the 2 GFCI outlets first and need to wire in a Vanity light, a shower light and a fan/light combo over the toilet. Was n… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.