Hi. I have a 15 amp circuit (14 gauge romex) to my garage. It is fine except when I try to use my air compressor. The circuit breaker will always blow on the first start attempt. Once I go downstairs and reset the break, the compressor runs fine. Is there some kind of a breaker I can get for this 15 amp circuit that will not blow on a high-current starting load? Thank you for your time! This circuit is used only for the compressor or power tools, but not at the same time. Would a slow-blow/high-current 15A breaker work in this scenario? Where could I get a breaker of this type?
Show More
Show Less
Ask Your Own Electrical Question
Answered in 6 minutes by:
6/27/2010
Mike
Mike, Master Electrician
Category: Electrical
Satisfied Customers: 2,743
Experience: Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
Verified
Because this is a general use circuit, and not just supplying the one receptacle, no. But it sounds like the startup current is just enough to trip the breaker so you may actually get by with just changing out the breaker for a new one, especially if the breaker is older. These things aren't produced to exact specs, so one breaker may hold while another won't. But truth be told, the correct way to solve this problem is to install a dedicated 20A circuit with #12 wire specifically for your compressor. I'm not sure what the specs are on your compressor, but if it's tripping a 15A circuit, it likely needs a 20A circuit to operate efficiently. This can also increase the life of your compressor (larger wire = equals more voltage = longer life).
Mike
Mike, Master Electrician
Category: Electrical
Satisfied Customers: 2,743
Experience: Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
Verified
Mike and 87 other Electrical Specialists are ready to help you
Ask your own question now
Customer reply replied 8 years ago
Mike, adding a new circuit is not practical. The compressor is rated at 5 amps contiuous. Once it is going, the compressor runs fine, it is just the start-up current causing the circuit to trip. I have dealt with this in cars by using a 'slow-blow' fuse, but never had to deal with it in a house. Isn't there anything else that could be done? Does someone make a high-current or slow-blow breaker for such situations?
Yes, they are made, but they don't properly protect a multi-outlet branch circuit. You can't install a time delay fuse on a multi-outlet branch circuit. If this were the only receptacle on the circuit, and it was dedicated for the compressor, the solution would be simple; install a time delay fuse. Unfortunately, the code is not written on practical. If you want to do this right, you need a new circuit.

Edited by Mike on 6/27/2010 at 10:24 PM EST
Ask Your Own Electrical Question
Customer reply replied 8 years ago
This circuit is for a single outlet in the garage. It is used for any power tools I need in the garage. When the compressor is plugged in, nothing else is on the circuit with it. Under these circumstances would a slow-blow/high-current breaker be satisfactory?
Well, it doesn't quite work like that. This isn't a breaker. You would install a motor starter and wire the compressor to the starter. The starter itself would contain the overload protection, which would allow for startup currents. This isn't really practical if you ever use the receptacle for anything other than the compressor. You may get by with just changing out the breaker though. A standard breaker is designed to allow a surge of current. It shouldn't really be tripping even if the compressor is drawing 40A at startup. A 15A breaker doesn't trip as soon as current exceeds 15A. So either there is an issue with the compressor and it's drawing an excessive amount of current for an excessive amount of time (which could be caused by a long run #14 gauge wiring - voltage drop) or many other things. There's no shortcut. Sorry this isn't what you want to hear. Change the breaker and see if a new breaker holds. If not, your only real option is to run a new circuit.
Mike
Mike, Master Electrician
Category: Electrical
Satisfied Customers: 2,743
Experience: Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer
Verified
Mike and 87 other Electrical Specialists are ready to help you
Ask your own question now
Customer reply replied 8 years ago
Mike,

Okay, thank you again for your time and expertise. Have a great day!

Sincerely,
Mike DiSante
No problem, Mike. Thank you!
Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Mike Your Own Question
Mike
Mike
Mike, Master Electrician
Category: Electrical
Satisfied Customers: 2,743
2,743 Satisfied Customers
Experience: Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Mike is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

2,743 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,290 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,414 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I have a charbroil electric bistro grill that keeps blowing
i have a charbroil electric bistro grill that keeps blowing the gri plug on my patio … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I have a fridge in the garage plugged into a normal 15amp
I have a fridge in the garage plugged into a normal 15amp outlet that is on a GFCI protected circuit. The breaker is a 15amp and the GFCI keeps tripping every few hours. I'm currently plugging the sam… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
Adding a NEMA 6-15 outlet to an existing NEMA 14-30 outlet
Adding a NEMA 6-15 outlet to an existing NEMA 14-30 outlet and 30 amp circuit. I bought a Bosch washing machine which tries to force you to buy the washer/dryer combination by having the washing machi… read more
ProGrade
ProGrade
Electrical Contractor
564 satisfied customers
I am interested in finding out what the process is for
Hello, I am interested in finding out what the process is for stress testing a circuit. We bought a fixer upper upstate new York, a raised ranch built in 1978. The three bedroom outlets are on one bre… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I find that, in my home, a 15A breaker feeds a 20A GFCI,
I find that, in my home, a 15A breaker feeds a 20A GFCI, which then feeds bathroom countertop outlets. All wiring is 14 gauge, and all outlets except the GFCI are rated 15A. Wouldn't it be better for … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
Hi, I am changing the outlets and light switches in two
Hi, I am changing the outlets and light switches in two bedrooms in my house and ran into a problem, I think. The electricity to the both bedrooms is controlled one 20 amp breaker. I know normally peo… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
can I change out a 15 amp breaker for a 20 amp.? the reason
can I change out a 15 amp breaker for a 20 amp.? the reason is that the builder have the microwave and the dinning room light on the same line. Just those two. However every time we turn on the dinnin… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I just had our breaker panel replaced (a 200 amp Federal Panel
I just had our breaker panel replaced (a 200 amp Federal Panel was replaced with a 200 amp 40 slot , Square D panel), and i had an aux panel installed with a 220 volt temporary generator connection re… read more
Steve
Steve
Chief Engineer
9 satisfied customers
good morning, our home is knob and tube wiring upgraded to
good morning, our home is knob and tube wiring upgraded to a newer 100 amp service. we are not electricians and know this is likely problematic (old wires adapted to new system). we have just had two … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I am finishing my basement. I had already built my office
I am finishing my basement. I had already built my office in the basement. I ran two 20 amp circuits to the office. One was for the outlets. I used a 20a circuit for the outlets since I am running a c… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I am adding a GFCI outlet next to a new egress window well
I am adding a GFCI outlet next to a new egress window well with cover. I understand that the outlet box needs to be at least 12" above grade and weather tight. First question is which would be better … read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
Hello,I have an old cabin that needs a few electrical fixes.
Hello, I have an old cabin that needs a few electrical fixes. ne of the circuits has a 15 amp breaker that has some 14-2 wire for switches and plugs. Can I use a 12 gauge wire to tie into that circuit… read more
Rick
Rick
Owner
High School or GED
467 satisfied customers
Hello, I wonder if someone can help me here. I have built
Hello, I wonder if someone can help me here. I have built up into the attic above my garage. It is now all little room for boarding cats. I checked with the city and there's no issue, provided I don't… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
What gauge wire ( #14 or #12 ) should I use for a circuit with
What gauge wire ( #14 or #12 ) should I use for a circuit with 3 residential ceiling fans and one outside light fixture for a small 2 bedroom home ? Should the circuit breaker be 15 amps or 20 amps ? … read more
Alex
Alex
Owner
Bachelor\u0027s Degree
1,783 satisfied customers
If a circuit breaker box is labeled kitchen outlets with a
If a circuit breaker box is labeled kitchen outlets with a 20 on the switch. Can I trust that the kitchen outlets are safe for that load? Is it ok to run a 20A extension to a portable air conditioner … read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
The Awning company i bought from wired my awning from a circut
The Awning company i bought from wired my awning from a circut in the kitchen that is 20 amps 12 Ga. They put an outlet on the outside of the house with a 15 amp outlet and ran out of the interior box… read more
Mike
Mike
Master Electrician
Working on MBA
2,743 satisfied customers
Im replacing wall receptacles from ivory to white in a home
I'm replacing wall receptacles from ivory to white in a home wired circa 1970. When I removed one of the old receptacles, it is 15A 125V (Leviton) that accepts 12 or 14 gauge wire for the push in hole… read more
Alex
Alex
Owner
Bachelor\u0027s Degree
1,783 satisfied customers
Hi. My house has a 20 amp circuit that is labeled Basement
Hi. My house has a 20 amp circuit that is labeled "Basement GFI, Garage GFI, WP, and GDO" I know the GDO is the garage door openers, but I'm not sure what WP is. I wanted to run some extra outlets to … read more
Sir Sparks
Sir Sparks
Owner
State & UK Certified Master electri
2,519 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x