if one of my leg is burnt or open then why is both of my 2…

Customer Question
if one of my leg...
if one of my leg is burnt or open then why is both of my 2 hot wires leg still have 120 volt in it? by using the voltage tester i turned off the main 200 breaker and test the ground with one hot wire individually and it produce 120v and the other produce 120v as well. but when i use the voltage tester and test both of the hot wires it doesn't show nothing when the main breaker is off. but when i turn it on i use the tester again and test both of the hot wires it comes out to be 120 volt instead of 240 volt because my house is 200 amp so what would be the problem to this and how would i solve it without calling an electrician because i want to fix it myself?
Submitted: 8 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 5 minutes by:
6/27/2010
Electrician: electrifier, Master Electrician replied 8 years ago
electrifier
electrifier, Master Electrician
Category: Electrical
Satisfied Customers: 1,633
Experience: Electrical contractor and electrical inspector for over 24 years with phone and networking expertise
Verified
Tell me what you are calling a voltage tester. Is it a meter that tells you voltage or a tester that lights up when there is power there?
Ask Your Own Electrical Question
Customer reply replied 8 years ago
is a meter that tells you the voltage
Electrician: electrifier, Master Electrician replied 8 years ago
Where are you testing your main lines? Are you testing line to line or are you testing line to neutral?
Are you testing with the main breaker on or off?
Are you testing the terminals on the main breaker where the wires from the meter connect?
Ask Your Own Electrical Question
Customer reply replied 8 years ago
im testing my main line through the electrical panel outside my backyard. im testing the line to neutral which is the ground right? i test it when the main breaker is off. what i test was i use the voltage test meter by touching the neutral to one of the main hot wires and it only shows 120v and the other hot wire shows 120v as well. but what i was saying was when i touch both hot wire with the test meter it should show 240v right? but instead it doesn't show nothing while the main breaker is on. but people is telling me that one of the leg is burnt and i figure is not true becuase that leg is still showing 120v with the test meter while the main 200 amp breaker is off. but when i turn it on i touch both of the leg with the meter tester and it doesn't read nothing when it should read 240v. so why wouldn't my 2 hot wires read 240v? could it be a short circuit somewhere or could it be a overload? and part of my house electrical wouldn't work unless i turn on the air conditioner but the ac central outside is not functioning
Electrician: electrifier, Master Electrician replied 8 years ago
Test line to neutral with the main breaker OFF. This is to prevent feedback from the panel.
It does sound like a problem with the power coming to your house but we need a bit more information.
Is this service overhead or underground?
Does your house have it's own transformer or are there other houses on the same transformer?
Ask Your Own Electrical Question
Customer reply replied 8 years ago
underground and yes there are other houses on the same transformer
Electrician: electrifier, Master Electrician replied 8 years ago
I need you to test voltage with the main breaker turned off at the lugs that feed the main breaker. Test line to line and each line to neutral and let me know what you get.
Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Mike Your Own Question
Mike
Mike
Mike, Master Electrician
Category: Electrical
Satisfied Customers: 1,426
1,426 Satisfied Customers
Experience: Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Mike is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,290 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,414 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,633 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I ust installed a 240-volt breaker for a dryer at a house
Hi there, I ust installed a 240-volt breaker for a dryer at a house and for some reason the drum of the dryer turns but the heating element doesn't work. The receptacle and dryer nstructions said to w… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
In a sub panel with buried wire im getting 240 volts across
in a sub panel with buried wire im getting 240 volts across both legs but when i test each leg to ground im getting 0 on one and the full 240 on the other… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
Certain circuits in my house will go out. Other parts of the
Certain circuits in my house will go out. Other parts of the house will work. None of the inside breakers are tripped. This has been happening on and off for a while with slightly different outcomes. … read more
Expert
Expert
Certified Journeyperson Electrician
86 satisfied customers
I want to install a ceiling fan/light fixture in an existing
I want to install a ceiling fan/light fixture in an existing ceiling light fixture. When I removed the old light fixture there were only two black electrical line inside the junction box. One black li… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I have a water heater that has an electrical issue (i think).
I have a water heater that has an electrical issue (i think). Each probe reads 120 volts individually, but when testing both probes together my multireader readers zero. I checked the breaker and test… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I amooking at a 240 volt single phase electrical breaker box.
I amooking at a 240 volt single phase electrical breaker box. One leg registers 131 volts, the other 108… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
We are having reduced voltage in several areas of our kitchen
We are having reduced voltage in several areas of our kitchen that started today. When checking the two incoming lines, one registers 110 v. and one registers 120 v. Any ideas?… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
several breakers in my box are not working I replaced one
several breakers in my box are not working I replaced one of them with a new breaker and still no power… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
The power company here in the Philippines will be supplying
The power company here in the Philippines will be supplying two insulated wires at 220V for our house service. Can I use one wire as a ground or neutral for bonding and grounding and a single pole bre… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
I have a 240V application using a 40A relay contactor (120V
I have a 240V application using a 40A relay contactor (120V coil). About 9kw of load was put on the contractor (about 38A) and powered with 50A/240V breaker. There is a thermostat that activates the c… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
Hi there, I have a westerbeke Westerbeke 6BTD 6.0 8 kw (it
Hi there, I have a westerbeke Westerbeke 6BTD 6.0 8 kw (it actually has 6 and 8 BTD) stamped on the name plate..as far as I can see the 8BTD is the one I have as it's running 120 vac at 60 hertz.. I b… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
My dryer stopped working. I checked the three prong dryer
My dryer stopped working. I checked the three prong dryer plug with a basic pen tester. One prong was hot and the other two where ground. So, I replaced two 30 amp circuit breakers off the main box th… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I disconnected the ground wire from my panel to the water line
I disconnected the ground wire from my panel to the water line to replace a valve and lost all my light bulbs and the stove and microwave. Also arching occurs when the ground wire is touched to the wa… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
How can I tell if a 240 volt circuit is properly wired vs.
How can I tell if a 240 volt circuit is properly wired vs. the appliance being connected to it (i.e. a Dryer) has a problem?… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I have a 240 volt electrical stovetop being repolaced with
I have a 240 volt electrical stovetop being repolaced with a gas stovetop. This new top needs a 120 plug to power the igniters. How do I lower the voltage coming in to that electrical box?… read more
Jerry
Jerry
Plumber
High School or GED
1,456 satisfied customers
Two circuits in my house flickered and then went out. After
Two circuits in my house flickered and then went out. After some inspection, I determined the breakers to be bad. The panel is a challenger. At the same time, my range, oven, and dryer have power, but… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,290 satisfied customers
I am having a problem with my dryer. It seemed to work fine
I am having a problem with my dryer. It seemed to work fine at first, but now the heater element is no longer heating up the air. To compound the problem the back panel of the dryer and metallic plate… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
Hi, A family member is having troble with a used electric clothes
Hi, A family member is having troble with a used electric clothes dryer they got. It was tested befor they bought it and it ran fine. They live in a trailer and have been throught 4 other dryers in ab… read more
Mike
Mike
Master Electrician
Working on MBA
1,426 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x