i have a10ga. 2 wire w/grnd to hookup for the lights outlets…

i have a10ga. 2 wire...
i have a10ga. 2 wire w/grnd to hookup for the lights outlets garage door opener etc. the old fuse box , 2 30 amp fuses. am trying to install a main lug loadcenter 70 amp cutler-hammer BR24L70SP f808& useing 2 br15amp gfcb115cs
i cantfigure out where the bl. wh. & gnd. should be going. got any PICTURES it looks odd the way the load wires are set in the breakers im confused. help! lauren
Show More
Show Less
Ask Your Own Electrical Question
Answered in 9 minutes by:
6/27/2010
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,417
Experience: Proven Professional 49 years Experience
Verified
Hi, I'm Mike and I'll be glad to assist you. Pictures aren't necessary, just follow my directions.

1) The 2 lugs attached to the breaker buss are where you attach the black wires.
2) On the side there is a bar with multiple screws. That's the neutral bar and where the white is terminated.
3) This installation is a sub panel, so you will have to purchase and install a ground bar for the feed ground and where all the circuit grounds will attach.

Now wasn't that simple.
Ask Your Own Electrical Question
Customer reply replied 8 years ago
i have done that already. where are the circuits supposed to go if there is cap. for 4 there are 2 set screws on the front. so the one w/ whitr dot is for /white other side for the black ? that seems kindof ugly did i miss something.
I'm sorry but I don't know what you're trying to say.

1) does cap. mean capacity?
2) 4 of what?
3) 2 set screws on front - of what?

Pleas don't abbreviate, spell it out so I may better be able to understand what you're asking. The instructions for wiring a sub panel are as good as you'll get anywhere. What is the rest ?
Ask Your Own Electrical Question
Customer reply replied 8 years ago

the breaker has 2 setscrews one called load terminal the other is called load neutral the pigtail goes to white neutral bar.

 

there is 2 breaker spaces and 4 max. circuits for the lug loadcenter i figured it out for 2 circuits but how there will be space for 4 circuits in the 2 breakers just put 4 wires in the setscrews ?

If there isn't room for the breakers, then you'll need a larger sub panel. They wire the same and the only difference is that they may be rated for a higher amperage but you can use it for a lesser. Does that help.
Ask Your Own Electrical Question
Customer reply replied 8 years ago

no room ? right on the box it says a maximum of FOUR circuits i GUESS you dont have any idea either

thanks i ll fake it

lauren

How many circuits did you need?
Exactly what are intending to put on this panel?

Edited by Mike G. on 6/27/2010 at 2:20 AM EST
Ask Your Own Electrical Question
Customer reply replied 8 years ago

ok, sorry about getting snotty on last reply. was pist at subpanel.

i was going to have 3 circuits . 1 for a compressor , 1 for lights & garage door opener , 1 for outlets. in the subpanel, left side where the breakers connect i connected the black wire to the lug and jumped to other lug where other breaker connects. the white wire to lug at upper right side of subpanel . the ground wire to the ground bar that i installed. i also connected the pigtail from the breaker to the whites bar. then i tried to tempoary connect the lights circuit by connecting the white wire to the setscrew space in the front of the breaker (on right) the black wire to the setscrew on left and it is tripping the breaker when energised. i cant think of what i missed.

OK, I see what your doing now.

You have 10/2 with a ground going to sub panel
  • Land the White on the neutral bar
  • Land the black on the buss lug and jumper it to the other lug.
  • Land the ground on ground bar.
You now have 4 positions for your breakers 120V.

Install your breakers. The GFCI breakers should have the factory pig tails land on the neutral bar. The blacks and whites from your loads should both land on the breakers.
The grounds should land on the ground bar.

That should do it.
Ask Your Own Electrical Question
Customer reply replied 8 years ago

thanks i had to undo the outlet circuit i got it into the light circuit and when i removed it and connected the light alone the lights worked. now for the next breaker.

thanks

If your all set, Please hit the accept button and leave feedback.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,417
Experience: Proven Professional 49 years Experience
Verified
Mike G. and 87 other Electrical Specialists are ready to help you
Ask your own question now
To make sure that there isn't a problem - Don't forget to pull the white off the 30A termination in the main equipment and land it on the neutral bar.
Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Mike G. Your Own Question
Mike G.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,417
8,417 Satisfied Customers
Experience: Proven Professional 49 years Experience

Mike G. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,417 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,414 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I'm trying to calculate the load for 2166 sqft new
I'm trying to calculate the load for 2166 sqft new construction house: 3 ton geothermal w/15kw heat strips, Hybrid electric heatpump water heater, everything else pretty much standard, stove, microwav… read more
George Smith
George Smith
Vocational, Technical or Trade School
450 satisfied customers
I appreciated the info on wiring the sub-panel. I have same
I appreciated the info on wiring the sub-panel. I have same issue, but I am bringing a12-2 w ground. Do I use a hot jumper between the two lug screws at top of breaker soaces? … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I wish to add a power meter to a garage to moniter the
I wish to add a power meter to a garage to moniter the electric use. Need a little help with the wiring of the meter socket.… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
I've a exterior 30 amp RV outlet professionally installed by
I've a exterior 30 amp RV outlet professionally installed by Baltimore Gas & Electric (BGE) Its a 110/115/120 Volts, whatever standard house current is, #10 wire. I've frequently used the outlet with … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I am renovating my kitchen and have some electrical
I am renovating my kitchen and have some electrical questions about adding a sub panel. See the link for the two photos. As of now my entire garage is without power and I really need it in order to do… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,417 satisfied customers
Situation: Replacing a standard outlet with GFCI in two gang
Situation: Replacing a standard outlet with GFCI in two gang box with separate switch to garbage disposal. Previous wiring: cable into box is 12/2 w/gnd; cable out is 14/3 w/gnd (goes to outlet for di… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,417 satisfied customers
I am renovating my basement and wanted to make sure that my
I am renovating my basement and wanted to make sure that my electrical is up to par. I had an electrician come an he said that the changes needed to be made b/c the electrical panel is too full. Too f… read more
Randy119
Randy119
President
High School or GED
7 satisfied customers
hooked rv up to home that has old style fuse system. we want
hooked rv up to home that has old style fuse system. we want to make a designated line for the rv...help… read more
AskTheElectrician
AskTheElectrician
Licensed Electrical Contractor
Associate Degree
17 satisfied customers
Hooked up photoelectric light in yard. decided to use same
Hooked up photoelectric light in yard. decided to use same power source (20 amp),12 ga., wh, bl & grnd to continue on to outlet inside shed. Wiring before adding outlet worked fine. Added outlet and a… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,417 satisfied customers
200 Amp service adding 124 Amp service box to run a 220 breaker for
200 Amp service adding 124 Amp service box to run a 220 breaker for central air. question what gauge wire should be used to connect boxes how many breakers can I add and be safe. [email protected]… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,417 satisfied customers
Im adding a 125 amp (Square D) breaker to my houses 200 amp
I'm adding a 125 amp (Square D) breaker to my houses 200 amp (Square D) Serive Pannel. I have 4-6 open slots in the lower right corner, bottom two of which I will use for the 125 amp breaker. I will t… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,417 satisfied customers
hello, i need to run power to attached garage for lighting,
hello, i need to run power to attached garage for lighting, outlets, 220v compressor-40amps, and 110v welder but my 200amp main has no room. i am lost on what to do.… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,417 satisfied customers
bought a cutler hammer 1 30amp camper two 20amp normal outlets.
bought a cutler hammer 1 30amp camper two 20amp normal outlets. I can only get the 30amp to work. can I get a wiring diagram from you?… read more
Rich
Rich
Master Electrician
Vocational, Technical or Trade Scho
1,117 satisfied customers
Hi, I just bought a vacation home. The home is 90% complete.
Hi, I just bought a vacation home. The home is 90% complete. The builder was foreclosed on. My question is about the electric panel. It has a few circuit breakers installed so they could work. But I d… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
I replaced a split receptacle and switch. The switch controls
I replaced a split receptacle and switch. The switch controls the split receptacle and a light/ceiling fan. I have 2 wire and a ground (Bl, wh, gnd) as my source. I have 3 wire and ground to the recep… read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
I am looking for a 200 amp box(new addition) that will be able
I am looking for a 200 amp box(new addition) that will be able to feed another 200 amp box(in existing house).… read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
I have an odd electrical system. The property was built in
I have an odd electrical system. The property was built in stages starting with a trailer in the 60's, a garage in the late 60's, and a house replacing the trailer in 1973. I have a 100 amp breaker pa… read more
Sir Sparks
Sir Sparks
Owner
State & UK Certified Master electri
2,519 satisfied customers
I just bought a Frigidaire electric range and my existing electrical
I just bought a Frigidaire electric range and my existing electrical hookup is a 2 wire (blk, wht). The back of the new Frigidaire range shows a 3 or 4 wire hookup (red, blk, wht). Can I use my existi… read more
The Home Smithy
The Home Smithy
Home Improvement Repair Consultant
1,890 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x