the travelers on a 3way switch controls 2 flourescents lights…

Customer Question
the travelers on a 3way...
the travelers on a 3way switch controls 2 flourescents lights has 14/3 wg is this sufficient enough commercial building m an electrician is telling me I need no.12 awg
Submitted: 8 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 3 minutes by:
6/11/2010
Electrician: Mike G., Master Electrician replied 8 years ago
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,417
Experience: Proven Professional 49 years Experience
Verified
Hi, I'm Mike and I'll be glad to assist you. Is the 14/3 NM or MC? Is it above a suspended ceiling? Is the circuit being used by any other load or is it dedicated to the two light fixtures?
Ask Your Own Electrical Question
Customer reply replied 8 years ago
14/3 nm drop in lights suspended ceiling the handy single light switch box has no.12 awg for power supply not sure if it feeds any thing elsethe 14/3 is just the travlers between the switches
Electrician: Mike G., Master Electrician replied 8 years ago
OK. The electrician was right. If the feed id #12 chances are it is on a 20A breaker. All the conductors must be #12. Also you can't use NM in a commercial suspended ceiling.
Ask Your Own Electrical Question
Electrician: Mike G., Master Electrician replied 8 years ago
I'm waiting for an acceptance of the answer. It may not have been what you wanted to hear, but it was the answer to the question. Please accept it.
Ask Your Own Electrical Question
Was this answer helpful?

How JustAnswer works

step-image
Describe your issueThe assistant will guide you
step-image
Chat 1:1 with an electricianLicensed Experts are available 24/7
step-image
100% satisfaction guaranteeGet all the answers you need
Ask Mike G. Your Own Question
Mike G.
Mike G.
Mike G., Master Electrician
Category: Electrical
Satisfied Customers: 8,417
8,417 Satisfied Customers
Experience: Proven Professional 49 years Experience

Mike G. is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

3,958 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

8,417 satisfied customers

Proven Professional 49 years Experience

Kevin

Kevin

Licensed Electrical Contractor

4,414 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,117 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I have LED reset light (12 watt) on the ceiling and when I
I have LED reset light (12 watt) on the ceiling and when I remove the cover (due to the light were not on) I see the wires go into the LED power supply (the label says Input:AC 110V, output:9-18 watt)… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I'm working on finishing my basement and I'm ready to wire
I'm working on finishing my basement and I'm ready to wire it, can you show me from subpanel how to run my circuits from subpanel to lights to switch, like in one open room we want about six recess li… read more
Steven Parent
Steven Parent
Journeymen Electrician
Electrical Journeyman Certificate
69 satisfied customers
ive got a cooper smart aim06 dimmer master switch with power
ive got a cooper smart aim06 dimmer master switch with power coming from a light. I know the black and white are runners. My question is regarding the difficulty I'm having hooking up the 4-way. It is… read more
AssuredElectrical
AssuredElectrical
Master Electrician
High School or GED
3,264 satisfied customers
I have 12-2 powering the switch,the exhaust fan and light have
I have 12-2 powering the switch,the exhaust fan and light have 14-2 in it can I use 14-2 to go from fan to switch.… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I have a 20 amp GFCI in a bathroom. Its fed by a 15 amp breaker
I have a 20 amp GFCI in a bathroom. It's fed by a 15 amp breaker using, I think, 12 awg wire. I'm going to take power from the GFCI to a 3-way switch that will be used to control a light/fan/night lig… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
Hello Mike, Patrick here. I am wanting to wire a double gang
Hello Mike, Patrick here. I am wanting to wire a double gang box with two dimmers. One to control a light fixture, the other to control two outlets for under cabinet lighting. The power source is at t… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I am trying to move a lightswitch which is part of a 3way setup.
I am trying to move a lightswitch which is part of a 3way setup. I mimicked the wires at the original location and ran 14/3 to the new location. I am finding that the light only works when both switch… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
8,417 satisfied customers
Can i wire multiple lights between 2 3way switches using only
Can i wire multiple lights between 2 3way switches using only 12-3 12/2pwr > 3way switch12/3>light>light>light>3way switch… read more
Steve
Steve
Chief Engineer
9 satisfied customers
Hello I am grounding a gasoline generator to a brass grounding
Hello I am grounding a gasoline generator to a brass grounding rod, and the manual says a 12 gauge copper strand wire is acceptable for the connection of generator to rod. I need to go 15 ft. and was … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
4,414 satisfied customers
I am do some of the initial wiring in my house and having an
I am do some of the initial wiring in my house and having an electrician co next everything after i am done. My question is how do I wire two ceiling fans(on the same circuit) to two three way switche… read more
Rick
Rick
Owner
High School or GED
467 satisfied customers
I am trying to wire a 3way switch outside the bathroom to inside
I am trying to wire a 3way switch outside the bathroom to inside the bathroom. The inside of the bathroom has a 3gang box with a duplex switch, a GFI and a single switch with a receptacle. I want the … read more
mrromex
mrromex
field supervisor
5 years of college courses
281 satisfied customers
In Pa., what are the code requirements for wiring 8 flourescent
In Pa., what are the code requirements for wiring 8' flourescent lights in a commercial building? I am just jumping off of an existing line to a new run of lights.… read more
Phil
Phil
Consultant to Engrs, Govt & Contractors
Degree, Mech Engr Technology
3,671 satisfied customers
I have a 3way switch that when turned on turns on 4 lights.
I have a 3way switch that when turned on turns on 4 lights. How to put a 3way switch between those lights.… read more
Alex
Alex
Owner
Bachelor\u0027s Degree
1,783 satisfied customers
I am wiring a recessed lighting fixture with the existing wiring
I am wiring a recessed lighting fixture with the existing wiring from the previous fixture. The documents that came with the fixture only have english warnings, but the directions are not in english, … read more
Electrical Doctor
Electrical Doctor
Master Electrician
Associate Degree
8 satisfied customers
Im having trouble wiring a 3-way. Existing light (#1) controlled
I'm having trouble wiring a 3-way. Existing light (#1) controlled by a SP switch in a box (box #1 - has 3 other 3ways). I added a light (#2) and want to make it a 3-way going to (box #2). So I ran 3-1… read more
Paul
Paul
Owner
Vocational, Technical or Trade Scho
51 satisfied customers
I have a single switch downstairs operating 4light fixtures,
I have a single switch downstairs operating 4light fixtures, and I want to change it to a 3way and add a 3way switch upstairs. The upstairs 3way has 3-wire cable and ground from it to the last fixture… read more
Sir Sparks
Sir Sparks
Owner
State & UK Certified Master electri
2,519 satisfied customers
I am installing a 3 way switch in a commercial building. a
I am installing a 3 way switch in a commercial building. a switch at either end of the building (200' long) with 11 fluorescent lights in between(2 bulbs each lights), Can I use 14 gauge wire or shoul… read more
electrifier
electrifier
Master Electrician
Bachelor's Degree
1,458 satisfied customers
Iwant to install 2-3way switchs that will control 7 can lights.
Iwant to install 2-3way switchs that will control 7 can lights. There will also be 1 other light that is in parallel with the 7 can lights. I have 14-2 wire coming from the main power supply already. … read more
Jason
Jason
Service Technician
Associate Degree
3,958 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x