Electrical

Electrical Questions? Ask an Electrician Online.

Ask an Expert,
Get an Answer ASAP!

Electrical

I need to know how to test a main breaker to tell if it is

Customer Question
bad or not. The...
I need to know how to test a main breaker to tell if it is bad or not. The problem I have is that I am losing half the power in my house while half of it stays on and there are no circuit breakers tripped. The power board checked their side and found nothing wrong. I have a murray 200amp mian breaker panel.
Submitted: 7 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 2 minutes by:
3/10/2010
Electrician: Jason, Service Technician replied 7 years ago
Jason
Jason, Service Technician
Category: Electrical
Satisfied Customers: 4,289
Experience: Over 20 years of experience in all types of installations, troubleshooting, and repairs.
Verified
HiCustomer Do you have a multimeter that will read AC voltage? If not, are you able to get one? Basic models are available at any home improvement store for around $25. The digital models are the easiest to use.

Ask Your Own Electrical Question
Customer reply replied 7 years ago
Hi jason, yes I have a multi-meter.
Electrician: Jason, Service Technician replied 7 years ago
Good. Set it to AC volts, and if you have the option of setting the range, set it higher than 240 volts. With the panel cover removed, very carefully touch one meter probe to one of the main lugs at the main breaker, and the other probe to the other lug. You should see a reading around 240 volts.

Next, take a reading on any double pole breaker in your panel by touching one meter probe to each lug on the double pole breaker. If your main breaker is bad (which is fairly common), you will likely see a 0 reading, or a very low reading.

You can also read between the 2 bussbars if you have them exposed anywhere in the panel. If necessary, you can remove 2 adjacent breakers to expose both bars.

Ask Your Own Electrical Question
Electrician: Jason, Service Technician replied 7 years ago
Another test you can try is turning the main breaker off and back on to see if power is restored. If that restores power, but it goes out again a short time later, that's another indication that the main could be bad. It's not a "smoking gun", but it's good evidence.

Ask Your Own Electrical Question
Customer reply replied 7 years ago

so, if I test the main breaker first and see a reading of 240 volts and then test a double pole and read o or have a very low reading then my main is bad?

 

That will cause the power loss in half my house with no circuit breakers tripped? Also when the heat/air unit kicks on the lights dim pretty low as it has just started doing this. Is this another sign that the main is going bad?

Electrician: Jason, Service Technician replied 7 years ago
Assuming your utility company checked everything on their side (this includes the transformer/connections, the wire from the transformer to your house, and all connections in the meter base), then yes, that is strong evidence that your main is bad. However, loose connections and damaged bussbars will mimic a bad main breaker.

Ask Your Own Electrical Question
Customer reply replied 7 years ago
One more question. The power board did check and said they found nothing. So, Is the response you gave a sure way to test the main(check the main and then a double pole) to tell if it is bad or not? Thanks
Electrician: Jason, Service Technician replied 7 years ago
Yes, I would be comfortable using that test as conclusive evidence. But I would also inspect the bussbars and the jaws on the double pole breaker to make sure they were mating properly, and that there was no corrosion between the two. I would also make sure all connections are tight. But based on what you have told me, all signs point toward a bad main breaker.

Jason
Jason, Service Technician
Category: Electrical
Satisfied Customers: 4,289
Experience: Over 20 years of experience in all types of installations, troubleshooting, and repairs.
Verified
Jason and 87 other Electrical Specialists are ready to help you
Ask your own question now
Ask Jason Your Own Question
Jason
Jason
Jason, Service Technician
Category: Electrical
Satisfied Customers: 4,289
4,289 Satisfied Customers
Experience: Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Jason is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

4,289 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I checked all circuit breakers to see if any tripped. I
Hi, I checked all circuit breakers to see if any tripped. I reset all of them and checked voltage. They are all receiving power. So I changed the 2 outlets that went out on the side of one room. Still… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have a problem with a circuit breaker tripping fairly
I have a problem with a circuit breaker tripping fairly regularly. I believe I have too many plugs on one circuit. How can I check to see if I have too many on one breaker. I have done a lot of wiring… read more
George Smith
George Smith
Vocational, Technical or Trade School
317 satisfied customers
My microwave flips a circuit breaker when I turn it on. It's
my microwave flips a circuit breaker when I turn it on. It's in the same location, same outlet, same everything. The outlet works with other things, like vacuum, elec light. The microwave works perfec… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Circuit breaker blew switch. Switch is not resetting. Just
Circuit breaker blew switch. Switch is not resetting. Just kinda dangles there, with no tension to either side. How can I fix this?… read more
Sam I
Sam I
Electrician
B.S.
473 satisfied customers
The circuit breaker hasn't popped but in living room non of
The circuit breaker hasn't popped but in living room non of the 4 outlets are working. Checked the 4 plugs for any signs of loose wires or spark marks. ? What's next? … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I want to remove a double circuit breaker from electrical
i want to remove a double circuit breaker from electrical panel … read more
Sam I
Sam I
Electrician
B.S.
473 satisfied customers
Can a General Electric type THQL-GCI hot tub circuit breaker
can a General Electric type THQL-GCI hot tub circuit breaker be tested with an ohm meter. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have 2 dedicated circuits in my circuit breaker box that
I have 2 dedicated circuits in my circuit breaker box that are 240V, they each have 2 hot wires going to them. The circuit is terminated to an individual plug (L6-20R) for each circuit. The device I'm… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have 415 amps worth of branch circuit breakers. what size
I have 415 amps worth of branch circuit breakers. what size service do i need for my house? is 200 sufficient … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I'm trying to move a circuit breaker box in a place I'd like
I'm trying to move a circuit breaker box in a place I'd like to put a bathroom. Knowing it isn't code to have one in a bathroom, is a junction box ok? … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
How do I determine the correct size circuit breaker panel
How do I determine the correct size circuit breaker panel for an stand alone workshop. I don't suspect I would draw more than 20 amps at any given time, but do I need a box assumes everything is turne… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
What is the function that makes a circuit breaker different
what is the function that makes a circuit breaker different from a switch so that it is able to break fault current … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Was wondering which circuit breaker I should look into
Hello, was wondering which circuit breaker I should look into replacing. As it stands my Dryer flips the circuit breaker for the upstairs bedrooms. Should I look into replacing the circuit breaker for… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
My circuit breaker was buzzing, so I pushed the test button.
Hello. My circuit breaker was buzzing, so I pushed the test button. This switched all the sockets off in my house but left all the lights on. When I flipped the breaker switch back, al the sockets cam… read more
Sam I
Sam I
Electrician
B.S.
473 satisfied customers
My circuit breaker is tripped and will not reset. I've
My circuit breaker is tripped and will not reset. I've checked wiring to outlets looks okay. At the electrical panel there is no power to breaker itself. I check other breakers and the have power. Any… read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
1,045 satisfied customers
Honda EU7000is has 30 amp line with circuit breaker with
Honda EU7000is has 30 amp line with circuit breaker with each line up to 22.6 amps. Questions is 32 amp draw too large and will trip circuit breaker and can circuit breaker be upgraded to 40 amp to al… read more
Sam I
Sam I
Electrician
B.S.
473 satisfied customers
I've checked ALL circuit breaker with a voltage meter. They
I've checked ALL circuit breaker with a voltage meter. They are good, but I still don't have power in both bathrooms. Not in the outlets or ceiling lights. Can you help. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
The circuit breaker tripped controlling all the electricity
The circuit breaker tripped controlling all the electricity in my son's bedroom. This circuit also controls the recessed lighting in the dining room. The only way I can reset the circuit breaker is if… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x