My power went out on one side of the living room. I went outside

Customer Question
to flip the breaker and...
My power went out on one side of the living room. I went outside to flip the breaker and it would not stay on. I found a burned wire in an outlet and took the receptacle off and taped off the wires black to black and white to white. The breaker would still not stay on. So I replaced the breaker. This also did not work. So I have now taped off one more outlet and a light switch that are on the same outlet to no avail. Am I on the wrong path? Any advice?
Submitted: 9 years ago.Category: Electrical
Show More
Show Less
Ask Your Own Electrical Question
Answered in 6 minutes by:
12/8/2008
Electrician: Jason, Service Technician replied 9 years ago
Jason
Jason, Service Technician
Category: Electrical
Satisfied Customers: 4,289
Experience: Over 20 years of experience in all types of installations, troubleshooting, and repairs.
Verified

HiCustomer You are not on the wrong path. The troubleshooting steps you have taken so far are good steps to take. You will need to continue opening wall boxes on the affected circuit, and inspecting the wires inside. This sounds like a direct short, where the ground wire or a neutral wire is touching the hot wire or the hot screw on the side of an outlet. Before you go to the trouble of opening more wall boxes, make sure you have unplugged everything from all of the outlets on the affected circuit. There could be a faulty item plugged in that is causing this problem.

 

These types of problems can be frustrating to find, especially if there are a lot of outlets and lights on the affected circuit. You may have to open a lot of wall boxes. Also, it wouldn't be a bad idea to open your electrical panel, if you are comfortable doing so. Once you get it open, I recommend trying to tighten every wire in the panel. This includes the wires on the breakers (with the breakers turned OFF, for safety), as well as the wires on the ground/neutral bars.

 

After performing these troubleshooting steps, please post back here if you don't get the problem resolved. I will continue to work with you on it until we get it fixed, or exhaust all means of remote troubleshooting. Thank you.

Ask Your Own Electrical Question
Ask Jason Your Own Question
Jason
Jason
Jason, Service Technician
Category: Electrical
Satisfied Customers: 4,289
4,289 Satisfied Customers
Experience: Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Jason is online now

A new question is answered every 9 seconds

How JustAnswer works:

  • Ask an ExpertExperts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional AnswerVia email, text message, or notification as you wait on our site. Ask follow up questions if you need to.
  • 100% Satisfaction GuaranteeRate the answer you receive.

JustAnswer in the News:

Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.

What Customers are Saying:

You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future.

JimmyBagley, IA

Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help.

Mary C.Freshfield, Liverpool, UK

This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!!

AlexLos Angeles, CA

Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult.

GPHesperia, CA

I couldn't be more satisfied! This is the site I will always come to when I need a second opinion.

JustinKernersville, NC

Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around.

EstherWoodstock, NY

Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know.

RobinElkton, Maryland

< Previous | Next >

Meet the Experts:

Mike

Mike

Master Electrician

1,426 satisfied customers

Licensed Master Electrician - OnQ Certified Data Voice Audio Video Installer

Jason

Jason

Service Technician

4,289 satisfied customers

Over 20 years of experience in all types of installations, troubleshooting, and repairs.

Mike G.

Mike G.

Master Electrician

7,826 satisfied customers

Proven Professional 48 years Experience

Kevin

Kevin

Licensed Electrical Contractor

3,870 satisfied customers

31 years Licensed Electrical Contractor in Illinois, Adjunct College Electrical Instructor, Former Electrical Inspector, Diploma: Digital Electronics, FCC Technician License

AssuredElectrical

AssuredElectrical

Master Electrician

3,264 satisfied customers

Contractor-42+ Years in the ElectricalTrade

electrifier

electrifier

Master Electrician

1,458 satisfied customers

Electrical contractor and electrical inspector for over 24 years with phone and networking expertise

Rich

Rich

Master Electrician

1,115 satisfied customers

Over 35 years residential, commercial, industrial wiring, install, troubleshoot, service, maintain

< Previous | Next >

Related Electrical Questions
I am trying to add a power outlet to wall. The light switch
I am trying to add a power outlet to wall. The light switch above it has 2 wires(black and white) and ground. I was told to run black wire from outlet to switch and leave black wire attached the switc… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have a few questions about changing the outlet that is
Good Morning, KevinI have a few questions about changing the outlet that is controlled by a wall switch. I would like the switch to control a different outlet - are you available for few questions. Mc… read more
Sam I
Sam I
Electrician
B.S.
473 satisfied customers
I replaced an old GFI outlet with Leviton GFNT1_KW outlet. 4
I replaced an old GFI outlet with Leviton GFNT1_KW outlet. 4 wires and a ground, two black two white. Green status light is on but no power. … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I have a half switched outlet that need to be changed. I
i have a half switched outlet that need to be changed. I understand that i should break the tab between the two brass screws to separate the red and the black wires but do i need to break the tab on t… read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
Gfci outlet was fried which caused the upstairs outlets in
Ok... so gfci outlet was fried which caused the upstairs outlets in the bathrooms not to work... pulled the old gfci switch, put a new one in, had the white wires on the neutral side and black on the … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Im trying to replace an electrical outlet with a USB outlet
Im trying to replace an electrical outlet with a USB outlet but I'm not sure if it can be done or how it should be done. Here are pictures.… read more
Sam I
Sam I
Electrician
B.S.
473 satisfied customers
Wiring diagram for outlet on a switch the to a light on same
wiring diagram for outlet on a switch the to a light on same switch … read more
David Bowden
David Bowden
Owner
468 satisfied customers
Which wires go where? In replacing a switch and outlet in
Which wires go where? In replacing a switch and outlet in the bathroom I mistakenly didn't label the wires before I ran down to answer the door now I don't know where the three main lead wires into th… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a legrand adorne outlet I took out the old outlet
Hi I have a legrand adorne outlet I took out the old outlet which had a red and black both on hot and a white on white. I put the red and black on hot - first I put the two hot wires in opposite sides… read more
Sam I
Sam I
Electrician
B.S.
473 satisfied customers
I need to wire a switch and 2 outlets in same box) without
I need to wire a switch and 2 outlets in same box) without the switch controlling the outlets. The switch is for a ceiling light. Thanks. … read more
Eddie
Eddie
Home Improvement Contractor and Repairs
High School or GED
1,045 satisfied customers
Question on wiring GFCI outlet... Late 80's...and no. Outlet
outlet is under the sink...bottom outlet goes to switch on the wall… read more
Sam I
Sam I
Electrician
B.S.
473 satisfied customers
I have a Leviton T5225 combination switch/outlet and I want
I have a Leviton T5225 combination switch/outlet and I want to wire it so the switch controls the outlet. There is a break-off tab connecting the two black screws. There is another dual outlet in the … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a question related to electrical outlet combo switch,
i have a question related to electrical outlet combo switch … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
How do Locate a reset switch for a GFCI outlet. One day
how do Locate a reset switch for a GFCI outlet JA: I'll do all I can to help. How long have you been dealing with this? Customer: one day JA: Do you plan on doing the work yourself? Customer: yes JA: … read more
Kevin
Kevin
Licensed Electrical Contractor
Diploma
3,870 satisfied customers
I took down a half wall with an outlet. the outlet was
i took down a half wall with an outlet. the outlet was connected to a 3 way switch and now the light will not come on. what should i do … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have several outlets that seem to be in the same "switch"
hello there... I have several outlets that seem to be in the same "switch" in my panel. as it happens it is the bathroom, part of the kitchen, my bedroom, my children's bedroom and a hallway next to b… read more
Sam I
Sam I
Electrician
B.S.
473 satisfied customers
I have a combination switch/outlet that I would like to wire
I have a combination switch/outlet that I would like to wire into a box so that the switch operates the outlet. what would the wiring diagram look like? Thx … read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
I have a switched outlet (a switch that comes before the
I have a switched outlet (a switch that comes before the outlet and turns the power to the outlet on and off). I want to remove the switch and replace it with a blank, thus capping the wires in the bo… read more
Mike G.
Mike G.
Master Electrician
Vocational, Technical or Trade Scho
7,826 satisfied customers
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.

Show MoreShow Less

Ask Your Question

x