Lennox Model G12Q3-110-2 blower won't shut off even with pilot out/turned off.

Submitted: 20 days and 4 hours ago.
Category: HVAC
Value: $16
Status: CLOSED
+
Read More

Optional Information

Make : RICH @www.hvac-for-beginners.com

Posted by KenCan 20 days and 4 hours ago.

Answer

Hello,

Can you shut the power down and remove the low voltage at the furnace, R, W, Y, G, and C. Turn power back on after you do this and see if you still have blower.

 

Thanks,

Ken

 

Please Do not Push ACCEPT until you are satisfied with answer.

20 days and 4 hours ago.

Reply

Where will I find the low voltage R,W,Y,G,C connections to disconnect them as you suggest?

Posted by KenCan 20 days and 4 hours ago.

Info Request

These wire into the blower section area of the furnace. Your thermostat wires will route to this furnace and use the same color wires that you have at your thermostat. You will need to take off both doors to get to your blower section.

 

Thanks,

Ken

20 days and 4 hours ago.

Reply

I'll check

Posted by KenCan 20 days and 4 hours ago.

Info Request

Okay.

20 days and 2 hours ago.

Reply

KenCan,

Found a 4-wire lead (from the thermostat?) holding finer gauge blue, green, red and white leads. The blue was pigtailed (via wire nut) to a pair of larger gauge yellow wires.

I'm not sure whether these were the wires you were describing.

However, I should tell you that I before I contacted you I turned off the power to the unit by way of an externally mounted single pole/single throw "light" switch mounted on the furnace cabinet exterior.

On my second trip to the basement to check for the wires you described, I flipped that switch back on, and the blower motor did not activate. If you recall, I'd already set the fan to "auto" at the thermostat, and turned the thermostat "cool/heat" switch to "off" at the start of all this.

By the time I returned to the basement the second time, a unit mounted to the right and above the on-off-pilot switch that had been very hot to the touch now was cool. The unit has two wires connected at the top, one brown, the other black. When I disconnected them one at a time while the blower was running non-stop, it didn't seem to affect the blower motor at all, as it continued to run.

At any rate, after flipping the externally mounted switch back on, since the blower remained off this time and having let nearly an hour pass before trying to fire up the furnace, I relit the pilot. After 60 seconds, I turned the pilot to "on," set the thermostat to "heat" and the fan to "auto." Now, everything seems to be working just fine.

Is it possible that there really was no problem in the first place and the component I described above just needed to cool down in order for the blower to shut off?

One more thing, we were gone overnight for four days, and the pilot could have blown out due to extremely high winds soon after we left. Could that have contributed to any of this?

Thanks for your patience.

Answer

It sounds like your limit was picking up addiational heat and opened the limit which is a saftey and turned your blower on to cool down the unit. Chances are this will happen again if you are stacking up heat near your limit from your burner piolt. Burner piolt will need to be adjusted if this happens again.

 

Thanks,

Ken

Picture
Expert: KenCan
Pos. Feedback: 94.7 %
Accepts: 
Answered: 11/3/2009

HVAC Technician

20+ years experience, Nate certified, EPA certified, TX state license

+
Read More

Related HVAC Questions

  • I have a 11 year old furnace, should I replace it when I rep...
  • we have a simple comfort thermostat model 2200. when turnin...
  • I am getting charged $300 dollars here in pomona, CA to inst...
  • Hello, Need to ask a question- Had a Heil system install...
  • i have a beckett burner and i just replaced the oil pump abo...
  • I have a gooman model HPTD18-60 thermostat. one of the termi...
  • I had a Trane TWE037E13FB air handler with 10kW heating coil...
  • i have a trane heatpump that the outside condenser won't com...



Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.
Question List | Become an Expert | Terms of Service | Security & Privacy | About Us
© 2003-2009 JustAnswer Corp.