Question

Furnace diagnostics indicate "pressure switch open with inducer on." What could be the problem? I recently had my natural gas turned on after being off for a few months. Furnace (Nordyne model KG6RC-080C-16B) used to work fine before, but has not worked since reactivating gas. I don't see a flame in the aperture, nor do I smell the gas. Is there a way to tell that the gas is actually getting to the furnace, or is this not likely related?

Submitted: 53 days and 18 hours ago.
Category: HVAC
Value: $24
Status: CLOSED
+
Read More
Posted by Mark Henley 53 days and 17 hours ago.

Answer

Hi,

 

No, not related at least not yet. The code means that the vent motor is running but there is no pressure differential being sensed by the pressure switch. The pressure switch is a device like the one in the photo,

 

graphic
View Full Image

 

 

If you remove the 1/4" hoses on this and clean out the barbed fittings that the hose (s) attach to you may get it to work, this device is there to ensure that you exhaust vent is clear before firing the furnace.

 

Let me know,

 

Thanks

 

Mark

53 days and 17 hours ago.

Reply

What would you recommend for cleaning the barbed fittings?

Posted by Mark Henley 53 days and 17 hours ago.

Answer

Hi,

 

You can use anything that has a toothpick shape and won't break off, but you don't want to go past the depth of the barbed fitting when cleaning the pressure switch fittings as there is a diaphragm in there.

 

Let me know,

 

Thanks

 

Mark



Edited by Mark Henley on 10/1/2009 at 12:59 AM

53 days and 17 hours ago.

Reply

Okay. I cleaned both ports out thoroughly and restarted twice. I'm still getting the same diagnostics reading--pressure switch open with inducer on. Any ideas?

Posted by Mark Henley 53 days and 17 hours ago.

Answer

Hi,

 

Yes , the pressure switch is there to ensure that the unit will not fire without sufficient airflow across the heat exchanger basically it verifies that the vent motor is running and that the exchanger or flue is not blocked, the next step would be to make sure that the flue is not blocked. Can you do that ?

 

Thanks

 

Mark

53 days and 16 hours ago.

Reply

There are 2 White PVC pipes that empty on the side of the house. One is straight. The other is curved downward at the terminal portion & has a mesh filter in it. I looked at both. They both appear free of obstruction, though I can only see up into the pipe that is curved downward.

Posted by Mark Henley 53 days and 16 hours ago.

Answer

Hi,

 

More than likely you are going to need the new pressure switch.

 

Thanks

 

Mark

53 days and 16 hours ago.

Reply

Where would you recommend to purchase a new pressure switch?

Accepted Answer

Hi,

 

A lot of people use this site .

 

http://www.myhvacparts.com/Nordyne%20Parts.html

 

Thanks

 

Mark

Picture
Expert: Mark Henley
Pos. Feedback: 99.2 %
Accepts: 
Answered: 10/1/2009

Journeyman Technician

UA Journeyman Pipefitter , HVAC, Refrigeration, DDC controls. 26 years.Commercial & residential

53 days and 16 hours ago.

Reply

Thank you very much, Mark. I will order the pressure switch & give it a shot.

 

Tim

Posted by Mark Henley 53 days and 16 hours ago.

Info Request

Hi Tim.

 

The question stays open so reply back when you get it,

 

Thanks

 

Mark

53 days and 14 hours ago.

Reply

Hi Mark,

Did you need any more information from me regarding the pressure switch? Let me know. Thanks

Posted by Mark Henley 52 days and 18 hours ago.

Info Request

Hi,

 

No just let me know how it goes,

 

Thanks

 

Mark

42 days and 1 hours ago.

Reply

Hey Mark,

 

I ordered the new pressure switch, installed it, and am still getting the same response from the furnace diagnostics--"pressure switch open with inducer on." What is likely to be the problem?

 

Thanks,

 

Tim

Posted by Mark Henley 41 days and 23 hours ago.

Info Request

Hi,

 

It must not be making the vacuum, can you get the combustion air pipe off of your furnace or at least a portion of it , for a test ?

 

Thanks

 

Mark

41 days and 23 hours ago.

Reply

I'll sure try. Which is the combustion air pipe?

Posted by Mark Henley 41 days and 23 hours ago.

Info Request

Hi,

 

It will be the one that just dumps into the combustion chamber, where the exhaust one connects to the inducer assembly.

 

Let me know,

 

Thanks

 

Mark

+
Read More

Related HVAC Questions

  • This is for an HVAC expert with Carrier. I have a model TSTA...
  • Dear HVAC wisdom God: I have a forced air heater-A/C comb...
  • How to add proper amount of R-22 charge to my heat pump usin...
  • I need to rewire my Weil McLain boiler for cold start "on".
  • thermostat ct8775c
  • I have a york Diamond 80, came with house built in 1996. Whe...
  • My condenser unit outside will not turn on. Could there be
  • my cental heat and AC UNIT HAS RUN FINE FOR THE LAST COUPLE



Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.
Question List | Become an Expert | Terms of Service | Security & Privacy | About Us
© 2003-2009 JustAnswer Corp.