The propane dector is on, the green light is blinking and the alarm sounds. fuse checks good.
If a VOM is a voltage / ohm meter I do have and can use. At a time in the past I was an electrical apprentice and understand electrical (basic) problems.
Yes -- The breaker for the water heater has been checked and reset.
I cannot followup until Tuesday 08/25/89. Will the possible control value being bad or a bad coil will that keep the light indicating that the LP gas is turned on from buring???
Yes-- I do have 110 volts to the motorhome.
I will reply again tomorrow after I gain access to the gas controls inside a storage compartment and removing a panel.
The back side of the water heater for the electrical connections will require the removal of washer dryer panel.
LP gas Problem: After gaining access there is 12 volts to the solenoid. I cannot hear any clicking when removing power. The switch will also disconnect power to the solenoid. IS IT A BAD SOLENOID????
WATER HEATER PROBLEM: Atwood Model #: GC10A-4E , Ser # 94021 447608 , Mfc Date : 03-23-06.
The fuse is good, the electronic ingition sparks on gas but will not work on electric power. The 110 volt breaker is not off. I do not know where to check for 110 volts on the front of the unit (outside). I hope that the unit will work on gas after repairing the LP Gas.
Thanks for your advice. I will have to check the element & termostat by entering behind the washer - dryer. (kots of fun).
The control board has two (2) sets of wires. 1 plug has 6 wires, the other plug has 3 wires.
I will not remove the washer - dryer unit for access to rear of water heater until I hear from you again.
LP Gas : No clicking of the solenoid can be heard, detector & on/off switch will remove the 12 volt readings.
Thanks.
I am on standby until you get to work.
Upon removing the solenoid I tapped it a couple of times, tried adding voltage and the thing started clicking. I testing for gas thru the soleoid- good. I then reattached the pressure regulator and tested- good. I reconnected all gas lines and tested the refrig on the gas setting - it operates. I tested the furnace and it worked. I tested the water heater on gas and it worked. I pulled wires from quick connections and reattached and the electrical water heater works.
I now have the water heater heating on gas to see if the therostat will cut unit off.
This MH unit had set for 9 months and some of the things must have corroded and the solenoid may hav been stuck since the DC power had been put out of service.
However, 2 problems remain. The switch for electrical power to water heater is the type that lights up when turned on - the light will not burn even though the heater is working.
There is also a light that should burn when the LP gas switch is turned on - it does not burn.
Could these 2 bulbs be burned out but both of the switches turn off & on ?????