My air conditioner is not blowing air out through the vents. The line that runs from the AC unit outside to the inside unit gets ice/frost on it. Any idea of what might be wrong?

Submitted: 130 days and 2 hours ago.
Category: HVAC
Value: $9
Status: AWAITING CUSTOMER ACTION
+
Read More

Accepted Answer

<p>Yes your coil is frozen solid and will not allow any air flow thru it. You will have to shut outdoor unit off and leave the inside blower motor on and wait about an hour to hour and half to thaw out. Then you must check the air filter if its dirty it needs to be changed since this may be the cause of this problem. I have a canned list of what else to look for</p><p> </p><p> </p><ul><li>Overcharge of refrigerant or oil. </li><li>Compressor is oversized. </li><li>Uneven or inadequate evaporator loading, probably caused by poor air distribution. </li><li>Excessive accumulation of oil in the evaporator. Check the defrost controls for proper operation and add more defrost cycles. A minimum of four should be used. </li><li>Expansion valve bulb and / or equalizer tube located improperly on the system. </li><li>External equalizer line plugged or capped. </li><li>Expansion valve defective or held open by a foreign material causing liquid flood back. </li><li>Moisture in the system causing the expansion valve to freeze in the open position. </li><li>Evaporator fan blades are on backwards. </li><li>Oversized condenser. </li><li>Excessive subcooling. </li><li>Poor distribution of refrigerant thru the evaporator nozzle and circuits. Usually the bottom rows of the evaporator will freeze up when this occurs. There should be no more than 5 degrees F difference in the superheat between any two circuits as they enter the header. </li><li>Expansion valve defective or has the incorrect power element charge. </li><li>Interrupted pump down which will leave refrigerant in the low side. This creates the possibility of flooding on start up. </li><li>Oversized expansion valve. </li><li>Liquid migration on the off cycle. Install pump down controls and a crankcase heater. </li><li>The expansion valve, solenoid valve or the compressor discharge valve leaks. This will leave refrigerant in the low side which creates the possibility of flooding on start up. </li><li>Excessive evaporator coil icing. </li><li>Superheat setting on expansion valve too low. </li></ul>

Picture
Expert: Rick Mather
Pos. Feedback: 96.2 %
Accepts: 
Answered: 7/14/2009

HVAC Technician

35 years experience, HVAC

130 days ago.

Reply

Thanks. Running the fan inside with the outdoor ac unit off seems to have done the trick. I found a bunch of water near the HVAC unt inside which I assume is normal? I am going to let the fan run for a while longer to be sure everything thawed properly. I also replaced the air filter.

After performing all of this, is the problem usually fixed or would you recommend I have the unit serviced for anythig else.

Thanks again.

Posted by Rick Mather 130 days ago.

Answer

If may do the same thing if so have the charge check with superheat charging chart

+
Read More

Related HVAC Questions

  • Hot Water tank was replace with the apparatus that goes on
  • electronic ignition will heat up thiers its not telling the
  • no ignition with my cannon caress gas fire
  • I called my company two days ago for an oil delivery and the...
  • My Imperial 80 is doing a couple of different things. Someti...
  • my pilot light goes on and wont kick on the boiler. then the
  • I have an Amana AC/Heating wall unit, PTH153A50AA. It's serv...
  • I have a T8602D Chronotherm IV Deluxe Programmable Thermosta...



Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.
Question List | Become an Expert | Terms of Service | Security & Privacy | About Us
© 2003-2009 JustAnswer Corp.