i have a carrier air conditioner installed in august 2004. i can hear the power source getting to
the unit, but it is not engaging the motor.
Submitted: 134 days and 1 hours ago.
Category: HVAC
Value: $18
Status: AWAITING CUSTOMER ACTION
+
Read More
Posted by
Kenton Guidry
134 days and 1 hours ago.
Info Request
Does the indoor fan work?
What do you hear, and where do you hear it?
134 days and 1 hours ago.
Reply
yes the indoor fan is working
i have the panel off the outside unit and i can a humming or buzzing
noise near what i think is a silonoid looking part. a silver sphere shape that has three electrical connections on top
Accepted Answer
The silver sphere you are referring to is a capacitor. It should not have any noise coming from it.
Here is a link to what a capacitor looks like so that we can confirm that is what you are looking at.
http://www.mobilehomerepair.com/media/img/coleman/1498-5351.jpg
Usually if you hear a hum it is from the contactor. Here is a link to a contactor photo.
http://img.china.alibaba.com/img/offer/10/17/38/17/1/101738171
Can you tell me if the contactor is making the noise?
Can you also tell me if your breaker is tripped?
Expert:
Kenton Guidry
Pos. Feedback:
98.8 %
Accepts:
Answered:
7/12/2009
HVAC Technician
EPA issued refrigeration license, College certificate, and 7 years in field.
134 days and 1 hours ago.
Reply
i'm fairly sure the noise was from the capacitor, i will double check that.
i know that the inside breaker is not tripped, i cant tell about the one on the outside i've never seen a breaker like it before.
Posted by
Kenton Guidry
134 days and 1 hours ago.
Answer
The outside may be a disconnect.
Here is a photo of a disconnect.
http://www.deanbennett.com/fuse-disconnect-box.gif
Here is another.
http://www.myhvacparts.com/Fused%20disconnect%20box%20closed.jpg
We need to find out if you have fuses inside the disconnect, or if there is a breaker in the disconnect.
Also, turn the thermostat to off. If the sound stops then the contactor is the culprit.
Please let me know if the sound stops and if you have either fuses, or a breaker outside at the disconnect.
134 days and 1 hours ago.
Reply
the sound stopped after i turned the thermostat to off.
i think the outside must be fuses, there is no breaker switch there.
Posted by
Kenton Guidry
134 days and 1 hours ago.
Answer
Do you see fuses that look like the photo below? Your fuses will be larger than the photo example but will confirm that there are fuses.
http://help.hudsoncarpentry.co.uk/Images/Electrics/howTo/changeFuse/fusesFig1.jpg
The noise must be the contactor.
134 days and 1 hours ago.
Reply
i dont see the actual fuses, just the box with a about 2/12 in square black front the has a small metal pull ring hanging in front
Posted by
Kenton Guidry
134 days and 1 hours ago.
Answer
This must be a non fused disconnect.
Can you turn your breaker to the condenser off, and then on.
Then have someone turn on the air conditioner while you stand outside to watch and hear it.
Let me know if it tries to start.
134 days and 1 hours ago.
Reply
the noise is at the contactor and at times the motor will buzz like it wants to start but doesn't
Posted by
Kenton Guidry
134 days and 1 hours ago.
Info Request
Go ahead and leave the power off.
Does the fan located at the condenser ever come on?
134 days ago.
Reply
a/c power is off. the fan on the outside unit(is that the condenser?)
has not ever come on with or without power. the inside fan unit is still on now
Posted by
Kenton Guidry
134 days ago.
Answer
That condenser fan (outside) should come on with your compressor.
You will have to get a technician out.
Your dual capacitor could have gone out, which in turn caused your fan motor and compressor to malfunction.
Do you see any bulges, oil spots, or dirt over oil near the capacitor?
134 days ago.
Reply
no the capacitor area is completely clear and clean
Posted by
Kenton Guidry
134 days ago.
Answer
Your motor may be out, or the capacitor could be bad.
Your compressor is trying to start but cannot. Either the capacitor is bad, or the compressor has gone out.
Your contactor should not buzz that loud either. It is also possible that it is pitted and needs to be replaced as well.
The best case scenario is that your dual capacitor is out and a new one will fix your problem.
Worst case your fan motor is out, and your compressor is pulling too many amps.
134 days ago.
Reply
thanks for your help!
Posted by
Kenton Guidry
134 days ago.
Info Request
You are very welcome.
+
Read More
Related HVAC Questions
I have a 10 year old heat pump 2 ton tech said compressor fa...
Our water heater keeps shutting off on its own. If we turn
I have a Dunkirk blue furnace that is energy efficient. It
I have a burnt relay in the junction box on the side of my
Replaced fan motor on outside unit. original motor once rep...
I need help shutting off the EH mode on my Carrier thermosta...
I have a T8011R thermostat, we just had a power interruption
I'm looking for a smart valve SV9540M2229 its for my gas hea...