My inside coil is freezing up. I had a local service tech, check it out and he said " 65/193 temperature split 18 degrees 78 degree return. Unit charge is right on withcharging chart."

After he left, the inside coil froze up in a few hours?

Submitted: 159 days and 1 hours ago.
Category: HVAC
Value: $15
Status: AWAITING CUSTOMER ACTION

Answer

Hello,

The the unit can freeze given any of the following..

dirty filter
dirty evaporator coil
low blower/restriction
low on refrigerant
Bad thermal expansion valve

The reading we need to know is the superheat (or subcooling if txv)

I would look for numbers higher than what was written.

If the outdoor temp is equal to or higher than your indoor temp I est more around 70-75 on the suction pressure....which you are reading 65. Once you get to 60 and below you begin to freeze.

I think he needs another look at it...or another tech needs to look at it.

Depending on the superheat...sounds like it is low.

Billy

Picture
Expert: Billy
Pos. Feedback: 99.7 %
Accepts: 
Answered: 6/15/2009

HVAC Mechanic

State Licensed Mechanical Contractor, Heating, Cooling, Oil Burners, Heat Pumps, Boilers, Geothermal

Related HVAC Questions

  • How do I get water pressure on 24ijunior?
  • I have a Fulflo 4FO oil filter setup. I replaced the filter
  • i'm getting a LO (lock out) and a BFT (boiler flow temp) mes...
  • I just installed a Maytag M1010 Series furnace. The circuit
  • We have a classic upstairs floor plan of 3 small bedrooms +
  • Hi. My AquaStar waterheater is not producing very hot water....
  • my unit won't start I have replace every electical part that
  • Help - our GF 3800 keeps turning off. We get e17 and we've



Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.
Question List | Become an Expert | Terms of Service | Security & Privacy | About Us
© 2003-2009 JustAnswer Corp.