Hi,
Which brand of zone valve? Model number also if you have one also which pump controller.
Thank you
Mark.
I have two honeywell zone valves v8043 . The limit control on the boiler is a honey well
L8148E
Do you want the diagram or step by step directions ?
Thank you,
Journeyman Technician
UA Journeyman Pipefitter , HVAC, Refrigeration, DDC controls. 26 years.Commercial & residential
Here is the link to the typical wiring for Honeywell zone valves and aqua stat pump control. Page 5 figure 3 is probably what you want.
Basically each zone valve is wired in parallel to the pump start circuit .
Each T/stat starts its associated zone valve moving, when the valve hits its end switch proving it is open it tells the pump and boiler to start. Look at the diagrams and let me know if there is anything that you need help with.
http://www.forwardthinking.honeywell.com/related_links/water/5000_series/install/95c_10932.pdf
You doing ok with that ?