My Trane XL 80 ignites but won't stay lit. After the flame goes out the indicator lamp flashes 3 times indicating a pressure switch failure according to the diags listed on the control....where is the pressure switch ? Can I replace it myself ? and where can I locate it right away ?

Submitted: 311 days and 3 hours ago.
Category: HVAC
Value: $9
Status: CLOSED
+
Read More
Posted by coolman1973 311 days and 2 hours ago.

Answer

ok when the furnace starts the small inducer comes on first on that motor there is a little tube that goes from the motor to the pressure switch, take the tube off the inducer motor and blow into it and suck. put it back, then were the flue pipe meets the inducer pull the flue pipe off and restart the furnace see if it stays lit

311 days and 2 hours ago.

Reply

I'm not following where the tube is...All I see are wires...

Posted by coolman1973 311 days and 2 hours ago.

Answer

there is a rubber tube hooke on that motor somewhere it may me orange

311 days and 2 hours ago.

Reply

I found the tube, and it has a Y....going to I believe 2 switches...I sucked and blew on the tube....same 3 light flash when I restarted the heater

Posted by coolman1973 311 days and 2 hours ago.

Answer

did u pull the flue pipe off

Posted by coolman1973 311 days and 2 hours ago.

Answer

also hit the switches with ur finger and restart the furnace

311 days and 2 hours ago.

Reply

Still the same issue...the flue is disconnected....I sucked and blew on the vacuum tube....I tapped on the switches...it reverts back to 3 flashes

There is a P01 High and a P02 low

Posted by coolman1973 311 days and 2 hours ago.

Answer

the small inducer motor runs right

311 days and 2 hours ago.

Reply

you're speaking about the small motor that is mounted to the same manifold I pulled the tube out of ....yes it does run and is outputting the exhaust into my heating closet as I have removed the flue vent from it

Posted by coolman1973 311 days and 2 hours ago.

Answer

u have a low fire and high fire press tube ok were the tube Y pull them apart and suck on each single tube going to each pressure switch try that, i know this seems repetitive but this is the best way. let me know

311 days and 2 hours ago.

Reply

I went through the process again...now the heater is running....the flue is still disconnected and it is blowing heat into the house...should I put the flue back on

Posted by coolman1973 311 days and 2 hours ago.

Answer

yes see if the furnace cuts out when u put it back on

311 days and 2 hours ago.

Reply

It did not cut offf when I put it back on and the controller is calling for heat

311 days and 2 hours ago.

Reply

are the P switches just touchy or do you think they were stuck

Posted by coolman1973 311 days and 1 hours ago.

Answer

they can stick but i would check to make sure ur flue pipe is clear andchimmney if it is then ur press switch may be going bad or like we said just stuck.

311 days and 1 hours ago.

Reply

should I replace the switches regardless?

Posted by coolman1973 311 days and 1 hours ago.

Answer

y not

311 days and 1 hours ago.

Reply

were the switches just stuck....I also noticed about 5 minutes after the heater was running the motor really kicked it up a notch and is blowing with more force now

Posted by coolman1973 311 days and 1 hours ago.

Answer

the high fire swich was prob the one sticking

311 days and 1 hours ago.

Reply

Thanks for your help....hopefully I can find the switches tomorrow or do you have an online source

Accepted Answer

no dont really know sorry

Picture
Expert: coolman1973
Pos. Feedback: 95.9 %
Accepts: 334
Answered: 1/1/2009

Hvac tech and Mechanic

15 yrs field exp/5yrs supervisingexp/ Nate and Epa cert.

+
Read More

Related HVAC Questions

  • I have a trane XE80 unit. The heating has gone out. I had a
  • Hi. I have a Honeywell thermostat and it is set to cool at
  • I am unable to turn on my furnace and air conditioner and th...
  • If I keep having a problem with my inside coil freezing up
  • Outdoor unit RPRL024JEZ Indoor Unit RHPLHM2421JA, 2 elect
  • I have an Evolution system with 5 zones. I am in Houston Tx...
  • HERE IS MY QUESTION: I AM WORKING ON A COLEMAN MOBLIE HOME
  • I have the the following unit: Model AR18-1 Part 15212-15 ...



Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.
Question List | Become an Expert | Terms of Service | Security & Privacy | About Us
© 2003-2009 JustAnswer Corp.