Question

I have a Bryant CAV395024070 furnace thats taking a code 31. When I run a component test, the inducer motor comes on, sometimes for only a second, sometimes for the proper amount of time, sometimes not at all. The remainder of the components all go through the test no matter what the inducer motor does. When I turn the thermostat on, sometimes the furnace runs, other times only the blower motor comes on and will run until I either turn the thermostat off or lower the set temperature so that the thermostat is satisfied. If I get the furnace to run and it satisfies the thermostat and shuts down, it may come back on as normal the next time the thermostat calls for heat. Other times the inducer motor will start then stop before the igniter glows and you can hear a noise coming from the control board. When this happens I reset the manual reset limit switch (flame rollout switch) and the noise goes away and the furnace will then run as normal. Is the problem with a relay on the ctl. board?

Submitted: 314 days and 10 hours ago.
Category: HVAC
Value: $9
Status: CLOSED
+
Read More
Posted by coolman1973 314 days and 8 hours ago.

Answer

hi. what does the sticker on the furnace say code 31 is

314 days and 7 hours ago.

Reply

For code 31 it is....Pressure, Draft Safeguard, or Auxiliary limit (when used) switch did not close or reopened. If open longer than 5 minutes, inducer shuts off for 15 minutes before retry. Check for: ***Proper vent sizing and condensate pitch ***Vent restriction or high winds ***Defective inducer motor or start capacitor ***Defective pressure switch or connections. If it opens after trial for ignition period, blower will come on for 90 second recycle delay. ***Inadequate combustion air supply ***Low inducer voltage ***Disconnected or obstructed pressure tubing The pressure switch has been replaced, I have checked the venting and condensate pitch. It is a new filter and has adequate combustion air supply.           

Posted by coolman1973 314 days and 7 hours ago.

Answer

ok shut the power off and on to reset the board, then restart the furnace and tell me step by step what happens thanks

314 days and 7 hours ago.

Reply

The led went solid, The inducer motor started and ran for about 15-20 seconds then shut down. Now I have a code 31 and the control board is making a sound intermittently. Now the blower came on.

Edited by XXXXXXXXXX on 12/30/2008 at 12:25 AM

Posted by coolman1973 314 days and 7 hours ago.

Answer

ok try this for me, take the hose of the inducer motor that goes to the pressure switch, blow and suck on the hose put it back on and restart the furnace.

314 days and 7 hours ago.

Reply

<p>Same result.</p>

Posted by coolman1973 314 days and 7 hours ago.

Answer

sounds like u have a bad relay in ur control board, if u can find a ac/heat parts house that sells rheem units u should be able to get one for maybe 100 bucks or so. and if its less than 5 yrs old ur parts are still under warranty

314 days and 7 hours ago.

Reply

That is the conclusion that I came to, but I don't know anything about heating and cooking other than what I have learned trying to resolve this issue. I have a technician coming out later this week but if I know it is the control board I can change that out myself and probably save at least $100 or more. I found the control board online for $280. Do you think it should be available cheaper?

Posted by coolman1973 314 days and 7 hours ago.

Answer

what yr is the furnace,

314 days and 7 hours ago.

Reply

November 1995

Accepted Answer

ya that 90% furnace board is a little more money , u could prob get it cheaper if u were a contractor but 280 is better than 600 for someone to come out and do it

Picture
Expert: coolman1973
Pos. Feedback: 95.9 %
Accepts: 334
Answered: 12/30/2008

Hvac tech and Mechanic

15 yrs field exp/5yrs supervisingexp/ Nate and Epa cert.

+
Read More

Related HVAC Questions

  • replaced 2 radiators -Glow worm space saver mk 2 no water ge...
  • Are the batteries full time in the thermostate or are they
  • I have a musty smell when I turn on my Prestige II air condi...
  • dear i want to apply for mechanical engineer designer
  • ideal fanned flue c80ff from wickes no hot water
  • how do you wire the thermostate to the zone valve (2 zone
  • Ignition Failure, check ground. Intertherm 90+ furnace.
  • Ocasionally my forced air will not cone on when I turn the



Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.
Question List | Become an Expert | Terms of Service | Security & Privacy | About Us
© 2003-2009 JustAnswer Corp.