The uint will run in heat Mode only if I load up the diaphram switch.
I simulate negative pressure on the hoses going to Swith pressure upper part XXXXXXX #21 and switch Pressure Lo. part #1011739 # 31 the unit starts right up. ( like a quick re-set ) The unit will run to thermostate setting and will not re-start.   It will also start up by disconnecting Switch Limit XXXXXXX #17 and runnes to TS Temp setting and will not re-start. What is going on.   I replaced the control fan timer and the Limit switch 10008445 still no change Imhad three technicians look at it already I am on a 10 year repair service contract with sears. I still have the heat running right. It is cold in NY, its in my fathers house and he is comming home from the hospital next week. I need to get the heat fixed ASAP. I have been with this problem now for three weeks and in communication with sears about 35 phone calls.
Tell me how to fix it I will do it myself. I am a engineer for gas insatllation for NG

Submitted: 337 days and 17 hours ago.
Category: HVAC
Value: $30
Status: AWAITING CUSTOMER ACTION
+
Read More
Posted by Rick Mather 337 days and 14 hours ago.

Answer

sounds like the induced draft proving switch has a problem, Are the ports clean that the switch hoses are connected to.

337 days and 14 hours ago.

Reply

The Daft Prove switch was cleanred and checked out already. It is a logic problem once the fan tuns on it starts up. And runs.

Posted by Rick Mather 337 days and 14 hours ago.

Answer

Have you checked all connections on the control board

Answer

Was the flame rod checked or replaced

Picture
Expert: Rick Mather
Pos. Feedback: 96.2 %
Accepts: 
Answered: 12/20/2008

HVAC Technician

35 years experience, HVAC

+
Read More

Related HVAC Questions

  • Good morning, I have a Robertshaw millivolt gas valve par...
  • My husband switched our old thermostat with a new Honeywell
  • how do the air condition of a mitsubishi lancer 2004 works
  • why my water heater overflow?
  • I have a Payne PH12NA048-0 Heat pump and want to install a
  • Im trying to replace the compressor in a trane XE-800 the ne...
  • I have a W-R thermostat type no. 1F86-244 and need to know
  • I have a Lennox G-23 series, the fuse needs ocassional repla...



Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.
Question List | Become an Expert | Terms of Service | Security & Privacy | About Us
© 2003-2009 JustAnswer Corp.