if you are getting oil from this line,shoul fill bottle fast. pull out nozzle assy. & replace nozzle with same size. make sure electrodes are set correctly
1 half inch up from center of nozzle
1 eighth inch out in front of nozzle
1 eigtht inch gap between electrodes
after nozzle assy. is re-installed, you can drag screwdriver across transformer terminals while it is running to check transformer. should arc halfway across, use a good screwdriver and be careful! 10,000 volts! this should get it going
HVAC Technician
17 yrs experience installs,service & maintenance hvac