Here are the goodman products evap--ARVF182416BA S/N

Customer Question

Here are the goodman products
evap--ARVF182416BA S/N (###) ###-####
cond-- GSC130181AE S/N(###) ###-####
Low side pressure 80 psi actual line temp 80F
High side pressure 180 psi actual line temp 91F
compressor drawing 4.0-4.2 amps
good airflow going over evap coil---- only 1 to 2 degree delta
ambient air in room about 75F with 55% RH
compressor not going off because set point of 68F not satisfied
Submitted: 2 months ago.
Category: HVAC
Expert:  Airheatman replied 2 months ago.

Sounds like possibly bad compressor valves. The suction pressure is high for a 75 degree return and head is low.

Suction line is warm and amp draw is slightly low. All indication on bad compressor valves