I am having a problem with a rheem classic 90 plus 3 amp

Customer Question

I am having a problem with a rheem classic 90 plus 3 amp panel fuse blowing whenever I call for cool. I changed out the contactor thinking it may be bad. No visible damage to wires. from the furnace to the compressor. What should I look at next?
Submitted: 4 months ago.
Category: HVAC
Expert:  Airheatman replied 4 months ago.

Do you have several fuses s we can try a few things until we find the short?

Customer: replied 4 months ago.
I had several. But ran out and everything is closed. Best place to buy 3 amp fuses?
Customer: replied 4 months ago.
It only blows when it calls for cool. Heat works just fine so I am sure it has something to do with the compressor.
Expert:  Airheatman replied 4 months ago.

You can get some at a Walmart or auto parts for testing.Can be 5 amp or so if they don't have 3 amps.

Lets start by disconnecting the complete ac circuit at furnace. Remove R wire and The Y wire from board. If there is no Y terminal on board. disconnect the yellow wire where it connects from thermostat in the furnace.

ith those wires disconnected, turn power on to furnace and push door button in. If fuse pops that means we have a problem with board.If not we will move on.

Customer: replied 4 months ago.
I disconnected the wires already to test this. It runs without the wires to the compressor
Expert:  Airheatman replied 4 months ago.

Excellent.Next lets go to outdoor unit. Find where the control wires first enter the unit and remove wire nuts and disconnect the Y and C .This will take the outdoor unit out of the circuit. Turn on power and call for ac. If fuse blows we know we have a short in wire or something between unit and furnace.If not we will go into the condensing unit.

Customer: replied 4 months ago.
C is red wire? I only have yellow or red. So leave both wires connected at the board, disconnect both wires at wire nuts. If it pops the short is in the wire, if not its in the compressor? Sounds too simple. I have to get more fuses. Going to run to Walmart. 20 mins or so round trip. are you on for a while?
Expert:  Airheatman replied 4 months ago.

Go ahead and reconnect everything at indoor unit. Just disconnect the yellow and red at outdoor. I will wait for you. Go ahead and give me model on outdoor unit so I can pull a manual and be looking at the internal circuit of outdoor unit in case fuse does not blow with the yellow and red disconnected.

Customer: replied 4 months ago.
Model no. RAMB-060JAZ Rheem unit. Heading to Walmart be right back
Expert:  Airheatman replied 4 months ago.

Will have manual on desk.Standing by

Expert:  Airheatman replied 4 months ago.

I have to leave for the night but will check in tomorrow morning.

OK looks like there are only 3 or 4 components between where wires enter unit and the contactor.

1.Low pressure switch

2.High Pressure switch

3.Hot gas sensor

4.Time delay.

Manuals shows some are optional so tell me which you actually have.Follow that yellow wire all the way to contactor.

Also while following the yellow wire, look for any place that the yellow wire could have gotten against a hot gas copper line and melted the sheathing allowing wire inside to touch the copper pipe.