What are the normal levels of combustion carrier model

Customer Question

what are the normal levels of combustion for a carrier model 58MCB080 gas furnace? e.i. co co2 excess air and flue temperature
Submitted: 1 year ago.
Category: HVAC
Expert:  airheatman replied 1 year ago.

Where will you be testing? At termination or at furnace with flue disconnected?

Expert:  airheatman replied 1 year ago.

Since the 58MCB is a high efficiency condensing furnace, the flue temp should be approx. same as return air temp and never exceed 125 degrees. This is why the PVC is allowable as vent material.

The carbon monoxide level should be below 100ppm with flue open and never above 400 with vent blocked for testing.

These levels are with sensor inside the pvc pipe