I had a Goodman GMH81155CN furnace/AC unit installed a year

Customer Question

I had a Goodman GMH81155CN furnace/AC unit installed a year ago but did not put the furnace into operation because of a lack of propane supply. I did have it converted to a propane configuration. I now have supply and tried to fire it up today but it is not getting propane through the unit regulator valve. The igniter operates fine, but there is no gas supply to the plenum. What should I check for to see why no fuel is being provided through the unit gas valve/regulator?
Submitted: 10 months ago.
Category: HVAC
Expert:  Airheatman replied 10 months ago.
Hello. My name is XXXXX XXXXX I'll do my best to help. Troubleshooting often requires meters and test equipment. Let's get started and see what we can do.
These units have a little on off switch on the gas valve itself. Lets start by making sure that switch has been turned to ON
Customer: replied 10 months ago.

The switch is on.


 

Expert:  Airheatman replied 10 months ago.
Ok, when furnace fails to ignite, look at the led light on the control board and tell me if it flashes, if so how many blinks between pausing
Customer: replied 10 months ago.

Where is the control board located? Do I need to remove the cover to the squirrel cage section? If so, it will take me approximately 15 minutes to get back to you.


 

Expert:  Airheatman replied 10 months ago.

Most Goodman furnaces will have a little inspection window to look in to see the flashing led.

Let me ask you this, when the igniter lights, do you hear the gas valve click? and do you have a volt meter to check to see if we are getting 24 volts to the gas valve?

Customer: replied 10 months ago.

OK, I know where the window is located and yes I have a multimeter to check the voltage. I will need to know which terminal to check. But for right now I will go up and recycle the unit and watch for the flashing light I will return in about 5-8 minutes with the result.

Expert:  Airheatman replied 10 months ago.
Sounds good .We will go from here.
Customer: replied 10 months ago.

I opened the fan door and held the door switch in and cycled the unit. The red light did not flash, stayed a steady weak red, and no sound from the gas solenoid on the valve, there was a click coming from the control board when the igniter cycled on and off.


 

Expert:  Airheatman replied 10 months ago.
OK, lets get meter set to ac volts 200. Turn thermostat to call for heat. When igniter lights, see if we get 24 volts between C and PM or C and Hi on the valve
Customer: replied 10 months ago.

Ok this will take approximately 15-20 minutes as I will cycle it multiple times to conform what I am reading.

Expert:  Airheatman replied 10 months ago.
No problem just come back and let me know if we are getting voltage to valve. We will go from there.
Customer: replied 10 months ago.

Did you get my reply on the voltage? It was 4.0 PM and went to 24 when igniter lit and on HI it was 14 and went to 24

Expert:  Airheatman replied 10 months ago.
Ok. I just now got the reply. Seems the issue is either in the gas valve or the pressure to the valve. Do you have a gas pressure tester or manometer to verify we are actually supplying at least 11" WC of gas pressure. And did they convert the valve and orifices to LP at installation? Furnace seems to be doing what it should up to the point that valve is not opening.
Customer: replied 10 months ago.

No manometer, and the unit was converted for LP, I guess this then calls for a technician to come and check that? I do not know what one costs, but if it is reasonable, I may purchase one. If the 11" water pressure is confirmed, then I guess the next step is to replace the valve? Your thoughts.

Expert:  Airheatman replied 10 months ago.
That is correct. Furnace is sending 24 v to valve at proper time, but valve is not opening. This will be because pressure is not right or valve is defective.
Customer: replied 10 months ago.

OK, I am ordering a manometer, or rather a pressure gauge that reads in inches. I will check the pressure and go from there. However, I purchased a "appliance" gas supply line to transition and it came with a connection nipple that had a safety valve integrated. The pressure kept closing that valve until I closed the valve to less just over half open. I am thinking that would indicate adequate pressure. I removed that nipple and installed a full flow nipple and still have the issue of no supply to the burner section. What are your thoughts on that?

Expert:  Airheatman replied 10 months ago.
Do you have a regulator in the gas line prior to the actual furnace gas valve? It could be that we actually have too high of gas pressure preventing the diaphragm from opening/
Customer: replied 10 months ago.

I have a high press at the LP tank (about 20 in) and a low press (about 14 in )just as the line comes into the building. then a 1.5 in. line to the appliances and the furnace with a run of about 32 ft to the furnace. Only a kitchen stove as WH is electric.


 

Expert:  Airheatman replied 10 months ago.
I am curious about the pressure at the inlet of the valve.Why such a large line to furnace. Should only be 1/2" gas line.
Customer: replied 10 months ago.

I am sorry. the line is 1/5, I put a . instead of / I have come to the conclusion that the valve may be frozen. I will wait until I get the pressure gauge and if the pressure is not the problem, will order another valve to replace this one. Will you be available in a week or so to help me through that process? Replacing the valve assy seems to be fairly simple, just take the supply manifold off with the valve and put a new valve on and replace the manifold.

Expert:  Airheatman replied 10 months ago.
LOL. I was thinking an inch and a half?.
Yes I will be available and look forward to helping and finding out exactly what the issue is.
After rating the question you have 30 days to follow up and work on the question. If you would rather wait until we are done to leave rating,and if for any reason question gets closed by moderators, just start out withCustomerand it will be sent to my desk.
Airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 4567
Experience: Furnace, A/C and heat pump specialist.
Airheatman and 4 other HVAC Specialists are ready to help you
Customer: replied 9 months ago.

OK, manometer went off the chart. Called LP supplier who sold me the low pressure regulator and said it was set at 11 in. I removed the regulator, cleaned it out (shook some dirt and crap out) and re-installed the regulator. Service pressure at the furnace is now 11 in. as it was supposed to be. (I think the regulator diaphragm was open and allowed 10 PSI to the furnace valve) but no gas is being delivered to the burn chambers to start. Is the next step to purchase a new gas valve ($100 online) or is there anyway to troubleshoot the gas valve? .

Expert:  Airheatman replied 9 months ago.
You should have a fitting on the outlet side of the valve to screw a fitting into and attach the manometer. The apply 24v to valve and see what is coming out that side.We should have between ^' and 10" WC coming out.
Customer: replied 9 months ago.

OK, it looks like there are two caps on the valve (white rogers 2 stage) one is low and I cannot make our the other stamping, (hi I am sure) and I will look for the outlet fitting to see if I can hook the manometer up to the valve. I will get back to you as soon as I can..

Expert:  Airheatman replied 9 months ago.
Ok, the fitting will be a hex or allen screw.Your manometer should have a threaded fitting that will screw in where you remove the cap.
Customer: replied 9 months ago.

OK, voltage is ok, I checked supply at fitting on the inlet side and have 11 in. voltage is still running 4.2 to 24 on one pin and 14.6 to 26.2 on other pin. still no gas to ignition area, everything checks out except the valve will not actuate to allow flow to ignition area.

Expert:  Airheatman replied 9 months ago.
I suspect the valve will have to be replaced. The high pressure may have damaged the diaphragm in the valve.
Customer: replied 9 months ago.

OK, new development, I put my hand on the valve body as it would cycle when the 24v was applied and felt a slight vibration and heard a faint click as if the solenoid was trying to actuate the valve but it was not opening. And, I suspect you are right, the diaphragm in the valve may have been warped by the hi pressure, (10 PSI) from the tank regulator. I will order one now and get back to you if it does not fix the problem.

Expert:  Airheatman replied 9 months ago.
Look forward to hearing back, Hopefully this will get you fixed up
Customer: replied 9 months ago.

OK, just a thought, valve on goodmanparts.net is not a white rogers but a replacement type. What do you think of "replacement parts" that are not the original OEM brand? $100 as opposed to $250+?

Expert:  Airheatman replied 9 months ago.
Excellent choice. No need to pay for oem parts as long as valve is a compatible valve,I recommend saving the money vs oem.
Customer: replied 9 months ago.

OK, thanks, XXXXX XXXXX order it now. Will let you know what happens and maybe ask some more questions.

Expert:  Airheatman replied 9 months ago.
I will be here
Customer: replied 9 months ago.

Good news, I replaced the Honeywell valve and the furnace works like it should. I guess the 10psi hit from the stuck low pressure regulator did the original valve in. I am keeping the valve and will try to find a new diaphragm for it and have it as a backup spare.


 


Thanks for the assistance.


 

Expert:  Airheatman replied 9 months ago.

Thanks for allowing me to help..

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial