hello. i am trying to install a venstar T5800. from a honeywell.

Resolved Question:

hello. i am trying to install a venstar T5800. from a honeywell. what do i do with the old Rc wire?
Submitted: 10 months ago.
Category: HVAC
Expert:  A-1 Tech replied 10 months ago.

A-1 Tech :

Hello, my name is XXXXX XXXXX I will assist you today

Customer:

hi ron

A-1 Tech :

Your old thermostar has an Rc and Rh or Rc and R ?

Customer:

Rcband R

Customer:

Oops Rc and R

Customer:

What was hooked up was W,Y,G,Rc, R and C

A-1 Tech :

Okay, you should have a wire that fed the R or the Rc with a jumper across. Is that correct?

Customer:

uh no jumper. two separate wires. The Red from AC went to Rc, The red from heat went to R

A-1 Tech :

That indicates you have a 2 transformer system which is rare. Most a/c units don't have a transformer

A-1 Tech :

You may not be able to have a 2 transformer system with this t stat, but you can convert it to a 1 transformer system.

A-1 Tech :

Let me look at your new stat wiring diagram. just a minute please.

Customer:

hmm. i had a c wire run because i was using a battery operated tstat prior.

Customer:

it worked with the old honeywell. there is no power to the venstar now

Customer:

are you saying Rc is a 24Volt input?

A-1 Tech :

yes

A-1 Tech :

Rc is 24 volt input for cooling

Customer:

so should i hook that up to the c on the venstar?

A-1 Tech :

The C is the 24 volt common or neutral and will be needed for the stat to funtion

A-1 Tech :

I would put the wire going to Rc on the R terminal and tape off the wire that was going to the R terminal on the old stat.

A-1 Tech :

If you accidently shorted the Rc wire or the R wire, you may have blown a fuse at the furnace circuit board

A-1 Tech :

can you jumper the Rc to the G and see if the blower comes on?

Customer:

i dont think so. let me quickly hook up the old one. ill get back to you in 5

A-1 Tech :

okay

Customer:

ok. back. both ac and heat come on now

Customer:

so the old one works

A-1 Tech :

great

A-1 Tech :

you have the R and Rc connected?

Customer:

yes

A-1 Tech :

Does your heat work also?

Customer:

seems to be

A-1 Tech :

I see you said it did, sorry.

A-1 Tech :

Can you access the heat ? And what type heat do you have?

Customer:

thats ok. i had a nest tstat. wouldnt work until i hooked up a c. when i did it worked fine for a while until the baseplate blew out.

Customer:

never get a nest.

Customer:

i have gas hot water heat

A-1 Tech :

We can try to convert this to a 1 transformer system if you would like.

Customer:

i dont think anything is working now. ill get back to you in a few

A-1 Tech :

The only problem I have with this is we don't know the size of your transformers.

A-1 Tech :

okay

Customer:

the heat works. the blower motor for the ac does not turn on now. prolly blew the fuse in it

A-1 Tech :

does the a/c and the heat use the same blower?

Customer:

no.

Customer:

gas hot water heat, rheem electric ac

Customer:

two separate systems

A-1 Tech :

I understand. So the thermostat controls the fan on the a/c only?

Customer:

the tstat call for cooling but nothing happens

Customer:

the tstat controls the blower which then passes on the call for cooling to the compressor

Customer:

but the fan doesnt come on at all now. the blower unit is dead

A-1 Tech :

Does the a/c unit run?

Customer:

my understanding is the fan should come on if i switch it on at the tstat even if i dont want cooling, correct?

A-1 Tech :

that is correct

Customer:

the compressor never turns on.

A-1 Tech :

the fan and compressor are on the same transformer

Customer:

i think the call to the compressor is relayed through the blower unit. yes i beleive they are

Customer:

so im basically stuck until i get the blower unit up again

Customer:

correct>?

A-1 Tech :

Typ, the Rc is the hot and on a call for cooling, it energizes the Y and the G terminal with the Y being cooling and G being the fan

Customer:

i shouldve just watched football :-)

A-1 Tech :

Sorry for your troubles.

A-1 Tech :

Where do you live?

Customer:

ny

A-1 Tech :

is it warm there now?

Customer:

its not a big deal. i will have my HVAC guy fix the fuse. my setup with my old honeywell tstat was easy. venstar should give you better instructions,

Customer:

its about 72 out

A-1 Tech :

Here is what I would do

Customer:

ok

Customer:

jumper the rc to the c?

A-1 Tech :

You have a 2 transformer system and trying to make it work on a 1 transformer t-stat.

A-1 Tech :

Rc to C would be a direct short

A-1 Tech :

R and Rc are both hot wires.

A-1 Tech :

C is a common/neutral

A-1 Tech :

I would have the a/c guy change you over to a 1 transformer system

Customer:

hm ok where does my c go to now?

A-1 Tech :

We could do that now, but I don't know if the transformers are large enough

A-1 Tech :

the C still goes to the C terminal

Customer:

its not going to help now since i blew that fuse, correct?

Customer:

and why was it ok with my old tstat?

A-1 Tech :

well, if the transformer for the heat were large enough, it would. But we don't know

A-1 Tech :

Because the old stat had a place for 2 hot wires. One to rhe R and the other to the Rc

Customer:

i dont want to mess with my heating unot. its a new traingle tube with microprocessors etc. i was told not to mess with the transformer on that one,.

Customer:

understood. so when i switched from heat to cool it just used the RC wire rather thab the r, correct?

A-1 Tech :

It can still be changed over to single transformer.

A-1 Tech :

yes, that is correct

A-1 Tech :

R is hot wire for heat and Rc is hot wire for cool

Customer:

gotcha so how would i do that?

A-1 Tech :

keep the transformer for the heat

Customer:

the R wire?

A-1 Tech :

BUT, instead of the hot going through the thermostat, it would go through a set of relay contacts.

A-1 Tech :

correct, the R

A-1 Tech :

then, use the wire going to the Rc terminal and put it on the R terminal on the stat.

A-1 Tech :

would be normal operation for cooling. But when it calls for heat, it would energize the relay which in turn closes the contacts bringing the boiler on

A-1 Tech :

right now, it turns the boiler on without the relay

A-1 Tech :

we need the relay to seperate the 2 transformers.

A-1 Tech :

give me a little bit and I will draw this out for you if you would like

Customer:

sounds complicated. ok. great

A-1 Tech :

your HVAC tech should know how to do it

A-1 Tech :

I will show your boiler as energizing a gas valve as I don't know what all controlls you have on it.

Customer:

yes he should. just pisses me off that venstar doesnt clarify this. as i said its a fairly standard installation around here,

A-1 Tech :

I agree,

A-1 Tech :

They could have put a Rh for heat and Rc for cool

Customer:

exactly. thats what the Nest Tstat had. but thats a crap product,

A-1 Tech :

give me a bit and I will draw up your existing and the way it will need to be done.

Customer:

awesome. thnKA

Customer:

THANKS

A-1 Tech :

will be a rough sketch

A-1 Tech :

I will attach it here as a picture

Customer:

k

A-1 Tech :

okay, going to scan these, then I will post.

Customer:

ok

A-1 Tech :

Full Size Image

A-1 Tech :

Full Size Image

A-1 Tech :

This may not be exact, your cooling transformer may be in the cooling unit and not the blower. Just the location of wiring would change.

Customer:

thanks. looks simple enough. ill rate you so you get paid. thanks again. if you would like to know how it turns out send me your email adress. imXXX@XXXXXX.XXX

A-1 Tech :

we can't give out our email, but you can come back to this question and let me know. I would appreciate that.

Customer:

ok. how would i do that?

A-1 Tech :

your email shows as just x to me

A-1 Tech :

I will put you down for a follow up in a couple days. you will get an email

Customer:

how about this? tmatwellatgmaildotcom

Customer:

ok great thanks again for your help

A-1 Tech :

Thank you and good luck. This will work for you

A-1 Tech, Service Manager
Category: HVAC
Satisfied Customers: 492
Experience: I have been in the HVAC business for over 39 years.
A-1 Tech and 3 other HVAC Specialists are ready to help you
Expert:  A-1 Tech replied 10 months ago.
Thank you for the positive rating. If I can assist you further please let me know.

Ron

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial