How JustAnswer Works:
  • Ask an Expert
    Experts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional Answer
    Via email, text message, or notification as you wait on our site.
    Ask follow up questions if you need to.
  • 100% Satisfaction Guarantee
    Rate the answer you receive.
Ask Rick Your Own Question
Rick, HVAC Supervisor
Category: HVAC
Satisfied Customers: 19080
Experience:  40+ yrs. experience as a licensed oil & gas technician.
Type Your HVAC Question Here...
Rick is online now
A new question is answered every 9 seconds

I have installed a heat exchanger to heat my pool, how do I wire it?

This answer was rated:

I have installed a heat exchanger to heat my pool off my boiler. All the plumbing is done. a new circulator has been installed dedicated to the pool. I need some help wiring an aquastat, flow valve, switching relay and the circulator together to the boiler. My boiler is a Burnham MPO-IQ 112,000 btu's. I have an electrician coming Monday to wire it. Unfortunately I need the pool warm for this weekend. Any help would be appreciated.

Welcome to Just Answer, I'll do my best to help with your situation.

First I need some info; what is the brand and model of your relay? how many zones do you currently have on your heating system? how are they (the zones) controlled? zone valves or a circulator for each zone?

Customer: replied 3 years ago.
The relay is a taco sr501...4 zones on heating system...3 for heat, 1 for indirect hwh....they are controlled by zone valves off of 1 circulator
This may take a bit to figure out how to do this with only 1 relay (if it can be done). Do you ever plan to need the pool heat at the same time as the space heating in the house?
Customer: replied 3 years ago.
No...pool in the summer, heat in the winter...I live in the northeast

I assume you have the install instructions for the relay in case you need it. All the following numbered/letter terminals mentioned are on your relay (unless stated otherwise). First you run a 120 volt feed to N (neutral) & H (hot) on the relay. If the jumper is installed to 3 leave it in place. Then connect the hot side feed of the circ to 4 N/O and the circ neutral to the neutral feed. Next the control side, you wire the flow switch and the aquastat in series to T & T. Then connect 2 leads from 6 N/O & 5 to T & T on the boiler control.

Wiring it this way will make the heating system circ run when the pool heater calls. Since the zone valves should be closed no heat should circulate through the house. This is not ideal but will work. The best way to do this is with another relay which would control the heating circ instead of having the boiler control the heating circ. But you only have one relay for now. If you don't want the heating circ to run you can disconnect it until you get another relay.

Rick and other HVAC Specialists are ready to help you