Ask Phil Your Own Question

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6072
Experience:  Retired HVAC/ Electrical & Boiler contractor. Industrial
23932409
Type Your HVAC Question Here...
Phil is online now
A new question is answered every 9 seconds

I have a Teledyne Laars boiler model number PW0400CN12KBASN,

Customer Question

I have a Teledyne Laars boiler model number PW0400CN12KBASN, a
two stage unit. The gas valve is a Robertson Grayson 7000DER2HC, it
has a Honeywell S8600F electronic control and a Honeywell two stage
temperature controller L6008G1009 (Laars part number RE0093200).

The problem is the boiler fires O.K. and the flames come up, but after
operating a little while the temperature increases the the point where
the high limit cuts the unit off. Then after it cools down the unit will
work again and go through the same cycle. If I turn the temp controller
down during this time the boiler will NOT cut off (even whenever it is turned all the way down to the stop).

I was thinking of replacing the temp controller and the immersion well
(I figured I would not be able to get the old bulb out).
Submitted: 1 year ago.
Category: HVAC
Expert:  Phil replied 1 year ago.
Welcome to Just Answer!

The temperature controller is most likely bad... to test that remove one of the two wires attached to it while the boiler is firing...if the burner goes off... the controller is bad. Thats a test intended for experienced technicians. Be careful not to let the wire touch anything when you lift it off of the terminal during the test.

If you are not experienced, let me know I will show you another way to do it..its a bit more time consuming and complex.

You should have no problem getting its sensor bulb removed from the well...look for a clip at the top of the well you have to remove .. the bulb should slide right out..

I will hold this question open for follow up with no time limit as long as you rate my responses *positively.

Thanks!

Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 6072
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Phil and 6 other HVAC Specialists are ready to help you
Customer: replied 1 year ago.

Thanks for responding.
The controller has two "R" terminals with nothing connected.


The "B" terminal has a wire on each terminal. I believe this makes up the


24 volt circuit to start and fire the boiler. The "W" terminal has a wire


on each terminal - I believe one is stage one and the other is stage two.


I did lift what I believed was stage one wire and the boiler turned off.


Please explain why this would indicate changing the temp controller?


Also whenever I had stage two going, I turned the controller all the way down and it would NOT TURN off.


These parts cost approx. $277.00, I would like to get this right. Is there any other part that would cause this problem?


I pulled the brown wire off the gas valve and the unit shut down - which is what it is supposed to do.


What is the other way to verify this is the part that needs replacing?

Expert:  Phil replied 1 year ago.

Hello again! Thanks for the excellent rating.

The control operates by breaking the circuit the two wires that go to the switch ... verify the switch by looking at the wiring diagram on the temperature control.... by removing one of the wires you are simulating the switch opening. So we know that it is the control failing to open the switch when it should.

You should try that a dozen times or so... it takes a while to format ones thinking patterns in these regards.... then it becomes obvious.

_________________


.if it is failing to break the circuit that energizes the gas valve when the temperature of the boiler water is above the thermostats set point.... then either the contacts are fused closed...or the sensing element is not sensing the water temperature.

If the sensing element is 3/8 or 1/2" diameter copper bulb, it is full of refrigerant. When the refrigerant warms up it puts pressure on a diaphragm inside the controller and that is mechanically linked to the switch that the wires are connected do.

If the sensing element is electronic it is called a 'thermistor'.. and is 1/4" in diameter, chrome plated as a rule and has an insulated set of wires going to it.... *not a thin copper tube.

Let me know which you have, . We can go from there.

Phil

Customer: replied 1 year ago.

I have the 3/8" diameter copper bulb. According to the schematic one "W" terminal on the controller goes to the first stage and the other


"W" terminal goes to the second stage. It looks as though the two "R"


terminals make and break the 24V control voltage.


 


Please tell me if you think there is any other part in this system that could give this symptom before I purchase the controller, etc. tomorrow. This would be an expensive mistake and very disappointing.


 


The only other components to choose from, in my opinion, would be the


gas valve and maybe the electronic controller. It seems as though the


temp controller is the component that actually removes the 24V to turn


the boiler off ---- IS THIS CORRECT?


 

Expert:  Phil replied 1 year ago.
You are correct... the chances that we are mistaken here are zero. Be very sure you wire the new one exactly as this one is.... make a large, overly clear and unmistakable diagram of the wiring... a photo would be good too.

Note: the 'terminals' such as R do not make or break... it is the switch connected between R and W that make and break... you can test that by killing power to the boiler, removing the wire to R and to W then operating the switch by adjusting the dial to its extremes... if the switch does not open and close, the controller is bad.

either its contacts are burnt closed or more likely the sensing element has lost its charge. Stay in touch as needed, I will hold the question open.


Phil
Customer: replied 1 year ago.

Phil,


Thanks for your help. I will be installing the temp controller tomorrow,


so I may have a couple more questions.


 



 


 

Expert:  Phil replied 1 year ago.
Good plan. Follow up as needed.

Phil
Expert:  Phil replied 1 year ago.
Hello again,

When you put the new sensing bulb into the thermo-well use some heat conductive paste made for the purpose, they will carry it at the place you buy the temperature control...its made of grease and aluminum powder. about 95% aluminum... lacking that the control will tend to lag quite a bit.

Phil
Customer: replied 1 year ago.

Hi Phil,


Thanks for the follow-up suggestion about using the heat conductive


paste. I figured I needed this whenever I removed the old one. I was


hoping there would be enough residue from the old bulb! I did not


realize I needed this.


 


I installed the temp controller on Monday and everything has been


fine. I will keep you posted.


 


Thanks for being so conscientious - your help is appreciated.


 


GG

Expert:  Phil replied 1 year ago.
Hello again... thanks for letting me know it all worked out well on your end... By working with us you saved yourself $300 to $500 in shop service charges, or a lot more if they had made a mistake in diagnosis.

and you learned something... that actually creates more dendron arm connections in the brain and makes you exponentially smarter over time.

Phil

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial
 
 
 

Related HVAC Questions

Chat Now With A HVAC Technician
Phil
Phil
Consultant to Engrs, Govt & Contractors
4567 Satisfied Customers
Retired HVAC/ Electrical & Boiler contractor. Industrial