How JustAnswer Works:
  • Ask an Expert
    Experts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional Answer
    Via email, text message, or notification as you wait on our site.
    Ask follow up questions if you need to.
  • 100% Satisfaction Guarantee
    Rate the answer you receive.
Ask Phil Your Own Question
Phil
Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 7596
Experience:  Retired HVAC/ Electrical & Boiler contractor. Industrial
23932409
Type Your HVAC Question Here...
Phil is online now
A new question is answered every 9 seconds

return air question

This answer was rated:

I just had a ac installed recently. The unit is a 3.5 ton air handler with a 4 ton condenser. The air handler has 22x24 return opening and my return air grill is 20x24. My contractor agreed that my return is slightly undersized but due to the tight area (no room to expand it between the trusses) he said it was not a problem because the return was drawing air silently and the static pressures were fine. He said it does hurts my efficiency slightly but not enough to actually be concerned about. I've done a Manual D calculation and I have 480 sq ins but I calculate I need 576 if I want 350 fps air velocity and that's not even adjusted for grill free area. My question is....Is he right that I shouldn't worry about it if my return is quiet (which it is) or is there something else I should be worrying about?

Welcome to Just Answer!

The contractor is most likely correct, but it depends on how long the return air duct is, and what size the return air duct is, and if it has any 90 degree turns or bends in it.

Let me know about that, we can go from there. As things stand so far, you are indeed smaller than the ideal but not by enough to make a significant difference... particularly if you are in a humid climate, such as the gulf coast of the US.

by the way the return air grill and return duct velocity is figured in feet per *minute you have an apparently typographical error ... FPS (feet per *second)*s.

I am going to bed in a few minutes, if I miss your tonight, I will pick this question up again first thing in the morning.



Phil


.
Customer: replied 3 years ago.


Oh yeah, def a typo. fps is for bullets not air velocity lol. The return air duct is only about 8 ft long. Could you give me some insight as to why the recommended return size is so large? Is sound the only reason?

Customer: replied 3 years ago.


Sorry didn't read fully, 18" duct with no 90 turns just a long sweep and I live in South East Florida

Hello again, the 18" round duct, 8 feet long is 15% small for return air requirements of 350 CFM per ton of cooling capacity. 350 x 4 = 1400 CFM

Thats 792 feet per minute CLICK HERE FOR THE CALCULATOR

Thats 15% above the recommend maximum velocity, but with no 90 degree bends and only 8 feet long it will be passable in most cases depending on the size of the supply air ducts and the *total external static pressure of the duct system.

If the supply air ducts are all 15 to 20% undersized then the system will be restricted for net air flow..and that would make a significant difference in the systems over all performance.


But if the supply air ducts are not undersized as well, then the 18" return duct, only 8 feet long and with no 90 degree bends will be passable... not ideal at all, but passable. This is a common problem with two story houses where getting large enough spaces to run duct work is a problem.

Do your schedule D calcs on the entire system, with pressure drops figured at the registers per the specs on the particular registers used, and the supply air duct sizes and lengths, and the get the total static pressure drop... compare that to the total external static pressure capabilities of the air handler or furnace used.

If you do not exceed the total external static pressure of the air handler or furnace there will generally be no problem at all... however if you do exceed the total static pressure capabilities of the air handler or furnace by even 10%, you can suffer a loss of air flow in the 20%* range and that will definitely affect performance and leave the system more prone to icing the coil when the house is warm inside and the outside temperature is below 75F... an iced coil stops all air flow.

The issue here is the practical issue of how to fit large enough duct work into the structure given the limited space available as the contractor stated. It would be good if you find a way to run an additional return air duct at least 12 inches in diameter.

If you rate my response *positively I can hold the question open for follow up.


Phil











( It is 350 CFM per ton in Florida, very low air flow per ton, because of the very high humidity there... the humidity (steam essentially) carries tremendous heat with it, allowing for less air flow, so we can run very easily at 350 CFM per ton, as compared to 400 to 500 CFM per ton in dryer climates)
Phil and 3 other HVAC Specialists are ready to help you