I have a 8 year old 5 Ton Lennox HS26-060 Condenser unit that

Customer Question

I have a 8 year old 5 Ton Lennox HS26-060 Condenser unit that won't start. I found it off with the house circuit breakers tripped. I reset the breakers which caused the unit to make a humming noise for a few seconds and then go silent. Can't get a repair guy here for a week.

Any suggestions on how to narrow down the problem and potentially repair?
Submitted: 10 months ago.
Category: HVAC
Expert:  Phil replied 10 months ago.
.Welcome to Just Answer!

Thanks for that detailed description. That tells me that the compressor 'run capacitor' has failed, or that the compressor has failed due to burnt wire or a more severe problem with the compressor..
The run capacitors cost about $75 each and are easily replaced. Tell me how handy and safe you are working on high voltages appliances and with wiring diagrams. I might be able to coach you on further tests.


. I will stay with you until the situation resolves. I hold questions open after positive ratings to allow for unlimited follow up.

Phil
Customer: replied 10 months ago.

Phil:

I'm pretty good with electrical stuff and have a good volt/ohm/ clamp-on amp meter.

 

Edit: While I was waiting for your first reply, I flipped on the breaker again and there is no sound at all.

 

Breaker returned to off and I pulled the side panel off the unit. Nothing looks out of place, all wires good, etc.

Expert:  Phil replied 10 months ago.

Hello again,

The compressor has 3 wires attached to it, One goes to the R terminal, one to the C terminal and one to the S terminal.

Check the amperage on the wire going to the S terminal during an attempted start for just ONE second..then shut it off.

If the run capacitor has failed open, there will be no amperage on that wire. If there is amperage on that wire... turn the power off to the compressor, and verify that completely using a double checked voltage meter... then disconnect all 3 wires from the compressor, and use an ohm meter to test between each terminal and the compressor body...any read indicates a burnt out compressor.

 

If the compressor is not grounded, check for ohm readings between each combination of the C, S and R the read between S and R should add up to the total between C and R and C and S. All of those reads under 10 ohms

 

typically 3 ohms, 5 ohms and 8 ohms.

 



Look for burnt wire terminals while you are there, and look for an oily or swollen or bulged capacitor.

Caution: the run capacitors are known to explode on occasion.

We can go from there.

Phil

Customer: replied 10 months ago.

There is no AC amperage on the S terminal wire. Also there is no sound like the humming noise I heard yesterday. The capacitor looks pristine and there is no evidence of burned terminals or melted wire insulation.

Expert:  Phil replied 10 months ago.
Hello again,

Did you check amperage on the C and R wires..

if no amperage there, then either the contractor is not closing, and there is no power to the compressor ...... or there is power to the C and R terminals but the compressors internal thermal over load is open due over heating when it attempted to start last time.

It will cool off in an hour or so and you can try again.

Meantime if your multi meter has a 'capacitance' feature on it, you can check the run capacitors capacitance between its center common terminal and the terminal that has a wire going to S on the compressor. (if its just a two terminal capacitor check between them)

Do that with the power off, and the wires disconnected.

Phil
Customer: replied 10 months ago.

Phil, I just realized that with the cool morning here, the system wasn't asking for cooling when I performed the previous tests. Sorry. So, here is the revised results.


 


When switched on, the S wire amperage rises to .08 -.16 amps (not much).


 


The C and R wires are +100 amps (I didn't leave it on long enough to let the meter settle. Seems like nearly a direct short to me.


 


When powered up, there is a humming sound which I take to be a motor trying, but unable to run.


 


The capacitor does not have a "center" terminal as you described, but there is no continuity between any of the 3 terminals. Is this a failed open capacitor?


 


 

Customer: replied 10 months ago.

Phil, I went ahead and pulled the capacitor out and discovered that it is leaking a little bit - looks like oil.

Expert:  Phil replied 10 months ago.

Hello again,

Ignore your ohm readings on the capacitor... an electronic ohm meter will not give a valid read there. Your amp reading on the S wire is below one amp, consider that a zero read.

It looks like the capacitor is bad, or the start winding in the compressor is defective.

Do the OHM tests I described earlier.

"
If the run capacitor has failed open, there will be no amperage on that wire. If there is amperage on that wire... turn the power off to the compressor, and verify that completely using a double checked voltage meter... then disconnect all 3 wires from the compressor, and use an ohm meter to test between each terminal and the compressor body...any read indicates a burnt out compressor.

 

If the compressor is not grounded, check for ohm readings between each combination of the C, S and R the read between S and R should add up to the total between C and R and C and S. All of those reads under 10 ohms

 

typically 3 ohms, 5 ohms and 8 ohms."

 

If the compressor ohms checks our as shown above, then the capacitor is bad.

replace the capacitor. take it to Grainger Industrial Supply or Johnstone Supply and have it matched up for voltage and micro farad rating.

 

The 100 amps on Run and Common are Locked rotor amps, thats normal when a compressor won't start... if it was a direct short it would blow the breaker within 1/2 to 1 second.

 

It takes 2 or 3 seconds to trip the breaker if it is just Locked rotor amps.

 

Let me know how all that goes.

 

I am currently on broadband from Antigua Guatemala where I am for a few weeks, and will check in frequently to see how you are doing...

 

As long as you rate my service to you positively, I will hold the question open with no time limits.

 

Thanks!

 

Phil

 

 

 

Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 5227
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Phil and 2 other HVAC Specialists are ready to help you
Customer: replied 10 months ago.

Phil, The compressor checked out good, so I'm off to buy a capacitor. I located one for about $30 from a wholesaler. Your service has been great and I will rate you accordingly. Money well spent.

Customer: replied 10 months ago.

System up and running!


Thanks again.

Expert:  Phil replied 10 months ago.
Good work! and thanks the excellent rating. I am currently traveling in Central America, right now at the base of Travahan? volcano in Antiqua on a restaurants wifi connection.

Phil

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial