My heat pump will not come on. Outside unit nor the attic unit.

Resolved Question:

My heat pump will not come on. Outside unit nor the attic unit. I crossed the G wire and the R wire together and the attic fan doesnt come on either.
Submitted: 1 year ago.
Category: HVAC
Expert:  Billy replied 1 year ago.
Hello,

was it running recently?

Billy

Customer: replied 1 year ago.

It was running about 1 month ago. We turned it off and it wont come back on

Expert:  Billy replied 1 year ago.
Thank you,

First thing is that this is a sign of no power to the thermostat.

before proceeding -

do you have a volt meter
do you have access to the air handler in attic

Billy

Customer: replied 1 year ago.

Yes I have both

Expert:  Billy replied 1 year ago.
Excellent.

If you follow the thermostat wires into the air handler....they will attach like they do at stat...R,G,Y etc....

we need to set meter for ac volts...and see if R to C (R to cabinet metal works also) has 24v.

Then we can pick a direction.

Customer: replied 1 year ago.

I am unclear. Are you saying to test the R wire to the C wire or are you saying to test the R wire to the metal housing of the air handler to measure for 24 v? Also just so you know the thermostat on the wall does not use C wire. I was told this is only for power to the thermostat and mine runes off battery power only.

Expert:  Billy replied 1 year ago.
C is a common terminal inside the air handler. It is like a neutral to 120v.

The metal cabinet or C terminal fill the same role for the test we want to do.

So in short...find the R terminal inside the air handler...and a C terminal OR just the cabinet.

Customer: replied 1 year ago.

continuity is all I get. No voltage

Expert:  Billy replied 1 year ago.
Ok,

do we have main power to the unit? Is power cut off by a door safety switch when door removed?

If you have make/model of air handler I can assist further

Customer: replied 1 year ago.

power is to the unit and it is a Goodman Manufaturing Corp Model no. a24-10

Expert:  Billy replied 1 year ago.
Thank you.

Are you familiar with what the transformer is? and doo you see a yellow blade fuse on a circuit bord?

Customer: replied 1 year ago.

I do know where the transformer is. Also I do not see a blade fuse anywhere.

Expert:  Billy replied 1 year ago.
We need to see if the transformer has an output of 24v.

Then we caan see if transformer is bad....which is generally caused by a short in wiring outside.

Customer: replied 1 year ago.

Ok. How can we do that

Expert:  Billy replied 1 year ago.
On one side of transformer you have 209/230v supply.

The other side is the low voltage output of 24v which gets sent to the thermostat.

Now we want to check the 2 low voltage wires to see if 24v is actully coming out of the transformer.

Customer: replied 1 year ago.

So just touch the volt meter to both sides of the transformer correct? And I should have a 24v reading?

Expert:  Billy replied 1 year ago.
that is correct..make sure you are on the 24v side
Customer: replied 1 year ago.

Ok I checked the 24v side and there is no voltage coming out.

Expert:  Billy replied 1 year ago.
Ok,

now there is one last check...do you have 220v supply to the transformer?

Customer: replied 1 year ago.

yes I had also checked the other side while i was up there and I did get a reading for 220

Expert:  Billy replied 1 year ago.
Ok, then you have a bad 208/230v to 24v transformer.

Something either went wrong with the transformer or there is a short that took out the transformer.

Once the transformer is replaced and wiring all checked for damaage you should be back to normal.

Billy

Customer: replied 1 year ago.

OK. I was thinking thats what you were going to say lol.. I will replace it tomorrow once the supply house opens. Thank You for your help on this issue.

Expert:  Billy replied 1 year ago.
You are very welcome. I am available for 30 days after answer is rated so feel to return for follow up

Billy

Billy, HVAC Technician
Category: HVAC
Satisfied Customers: 19792
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Billy and other HVAC Specialists are ready to help you
Customer: replied 1 year ago.
Greetings Billy, I am still having issues with the A/C. I replaced the transformer. The fan did come on. After the fan in the air handler came on and I ran it for about 10 min. I turned the A/C to cool. I went outside and noticed the outside fan was not turning. After about 10 min in cool mode I noticed the air handler fan stopped working. I went back in the attic and checked the transformer again and it had the 220 volts coming in but it was not measuring any voltage on the 24 volt side. I also smelled burning smell from the transformer. It was very hot to touch. So apparently I blew the new transformer. Is there something I can check to see why it is blowing?
Expert:  Billy replied 1 year ago.
Have you inspected all the thermostat wire from the indoor unit to the outdoor unit?

Any scrapes, nicks or pressed against metal?

Also we want to put a cheap blade fuse in the wire from transformer (24v) this will save transformers and instead blow the fuse.

we can make one like this with a blade fuse

This can be the outdoor contactor or the reversing valve also.

You can also buy a tranformer that has a built in trip breaker switch...this one only needs to be reset instead of replaced.

Attachments are only available to registered users.

Register Here

Attachments are only available to registered users.

Register Here

Attachments are only available to registered users.

Register Here
View Full Image

Attachments are only available to registered users.

Register Here


Customer: replied 1 year ago.
I did not notice any nicks in the wire however I will go back and do a thorough check on all wires. Would there be anything else I can check on tonight since the parts store is closed? If I wanted to make the blade fuse, what particular fuse rating should I use? Tomorrow I will check on the transformer with built in breaker when the store opens.
Expert:  Billy replied 1 year ago.
A 3 amp or 5 amp fuse works well

Attachments are only available to registered users.

Register Here

Attachments are only available to registered users.

Register Here

Attachments are only available to registered users.

Register Here
View Full Image

Attachments are only available to registered users.

Register Here
Customer: replied 1 year ago.
ok Great! I will inspect all wires now. And tomorrow I will either place an inline blade fuse or the transformer with built in switch. If I do not see any nicks in the wire is there anything else I can check on tonight?
Expert:  Billy replied 1 year ago.
Do you know how the contactor pulls down when energized?

Attachments are only available to registered users.

Register Here

Attachments are only available to registered users.

Register Here

Attachments are only available to registered users.

Register Here
View Full Image

Attachments are only available to registered users.

Register Here
Customer: replied 1 year ago.
No I do not know this part
Expert:  Billy replied 1 year ago.
The contactor is where the wires end up at from the thermostat....it is in the outdoor unit and is responsible for closing and turning on the 220v compressor and motor...but it is the 24v from the Y terminal that closes this switch.

If the wires all look good then we have to look at the contactor.

Customer: replied 1 year ago.
OK I will go outside and check this out.
Expert:  Billy replied 1 year ago.
Please be aware that if the disconnect is on at the outdoor unit there is 220v present

Customer: replied 1 year ago.
I looked outside and the wires look good in the condenser unit. I also pressed down on the contactor with the power on and the fan motor did start. Can I assume there is a short in the Y? or perhaps another possible issue?
Expert:  Billy replied 1 year ago.
The contactor could have a bad coil (the part that cause magnetism)

This is a rudimentery test....but you can turn on indoor blower (if transformer good ) and push the contactor in and wedge it closed. This provides cooling BUT it will not shut off.

did you say it does not blow in heat and this is a heat pump?

Customer: replied 1 year ago.
Well I cannot turn on the blower till tomorrow since I have blown the transformer and need to replace it. I have not tested the heat. If the contactor is bad, is it a possibility that is what caused the transformer in the air handler to blow?
Expert:  Billy replied 1 year ago.
That is correct.

we have only 2 possibilities IF the wiring is all good and no bare spots...that would be the contactor or reverse valve.

The reverse valve vale only works in cooling....so if you ran heat ok...but it blows in cooling, this would lead me to the reverse valve. This would be found following the O wire from thermostat to outdoor unit.

Customer: replied 1 year ago.
OK. I will inspect all the wire tonight, replace the blown transformer tomorrow with either installing a transformer with a breaker or installing an inline 3 or 5 amp inline fuse. Once all that is in place I will try the heat first, then I will try cool. If the transformer blows in cool I will check the reverse valve.
Expert:  Billy replied 1 year ago.
And remeber I am available for that 30 day time so feel free to return as needed.

Billy

Customer: replied 1 year ago.
ok thank you for all you have done!

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial