I have a Coleman Evcon DGAT070BDC mobile home furnace The

Resolved Question:

I have a Coleman Evcon DGAT070BDC mobile home furnace

The problem only occurs when it is really cold outside.The heater kicks on and runs fine until desired temp is reached then shuts down no problem. then the second time it kicks on after cool down, the fan runs for about 15 seconds the stops, kicks on then stops, etc until the exchanger cools down. I replaced the fan limit switch but the problem continues. I jumped the thermostat and still has the same problem.Is there any thing else I can replace to fix this problem? Thanks for your input.
Submitted: 1 year ago.
Category: HVAC
Expert:  V12Tech replied 1 year ago.

V12Tech :

Hello I am Keith , allow me 5 mins to pull up data please.

V12Tech :

Hi

Customer:

I already replaced the fan switch.

V12Tech :

This is not a limt, its the delay

V12Tech :

was it this

V12Tech :

let me see if I can get a pic

V12Tech :

The motor could be doing this if its getting hot?

Customer:

The website you sent me has a whole page of parts on it

V12Tech :

lol

V12Tech :

sorry

V12Tech :

yes it sells them

Customer:

So you are saying replace the delay?

V12Tech :

yes

V12Tech :

the temperature delay or time delay

V12Tech :

i think temp

V12Tech :

must check

V12Tech :

Some had fan delay limits with time on temp off

V12Tech :

I will check

Customer:

Temp delay? What does it look like and where is it located?

V12Tech :

It will be round I believe

V12Tech :

still checking

V12Tech :

i second

V12Tech :



3,470 RESULTS












V12Tech :

This controls the fan in heat mode

V12Tech :

Do you have AC

Customer:

No AC just heater?

V12Tech :

You may want to have the heat exchanger inspected if this was replaced and did this again

V12Tech :

There are cases of this, do you have the fan switch for auto or on for your thermostat

V12Tech :

Does your thermostat have a fan on position

Customer:

I have a on off switch on therastat

V12Tech :

Sorry my computer glitched

V12Tech :

Forthe unit, not fan correct?

V12Tech :

I wanted to see if fan on worked

Customer:

yes turns the stat off only

V12Tech :

if you had this option

V12Tech :

ok

V12Tech :

I am a bit worried aboout the exchanger

V12Tech :

Do you have a Co detector in the home?

Customer:

I dont see that part on unit only the limit switch

V12Tech :

its there

Customer:

Co detector does not go off!

V12Tech :

I will see if I casn find a pic

V12Tech :

Oh good you have one! exlnt

V12Tech :

I am looking for a better pic of unit

Customer:

I only see the limit switch in the fan housing

V12Tech :

still checking

V12Tech :

the fan wires go to it

V12Tech :

looking for pic

V12Tech :
This series furnace may have a recall listed to replace the heat exchanger .


Customer:

How would I find that out?

V12Tech :

The two recalls --attempt to beef up the inner walls and the replacement heat exchangers on the DGAA090 now require another part addition .
The point is the heat exchanger design is weak and YORK denies any problems.
Every furnace over 5 years of use in a northern zone should be inspected for heat cracks in the exchanger after every season .

V12Tech :

coleman or york

V12Tech :

I am reading diffent cersions of your furnace exist

V12Tech :

different versions , i type badly

Customer:

Ok I found too more switches in the exchange area.

V12Tech :

checking

V12Tech :

Safety Bulletin and it states models coleman,Coleman Evcon Red T model numbers DGAT070XXXAND DGAT075 NATURAL AND PROPANE have safety recalls .
These were manufactured 1997-1998-1999 .

V12Tech :

Still looking

Customer:

Mine is a Coleman Evcon DGAT070BDC So no recall?

V12Tech :

I am unsure

V12Tech :

It says some weak designs are suspect but not recalled?

V12Tech :

And inspect annually

V12Tech :

if you have a co detector its unlikly cracked

Customer:

So if I replace those 2 switches and it still does the same it will be the exchanger?

V12Tech :

That fan delay should normally fix the issue

V12Tech :

I have not found a good pic yet of unit

Customer:

Why does it only happen the second cycle? If it that delay it should do it on the first cycle too right?

V12Tech :

It is a bi metal and expands and contracts and they will do this

Customer:

oh I see

V12Tech :

its just 2 dissimilar metals with differing expansion rates so twists

Customer:

should I replace both?

V12Tech :

and cycling over time gets them weak, but this is not normal to switch them often did you swap this out before?

V12Tech :

Yes

V12Tech :

The parts are relatively inexpensive and its like a headlight on a 5 r old car

V12Tech :

the rest are right behind it

Customer:

no just replaced the fan limit switch

V12Tech :

I have replaced one light if not flush with cash but better to replace things so the same age

V12Tech :

Yes delay is the control

V12Tech :

on at 110F

V12Tech :

I think

V12Tech :

yes 110

V12Tech :

At least this is an easy fix

V12Tech :

They make time delays that avoid this issue

Customer:

one has a yellow sticker and one is blue

V12Tech :

not as inexpensive

V12Tech :

Humm not sure what that is

V12Tech :

I can see

Customer:

do you want the numbers that are on them?

V12Tech :

yes

V12Tech :

thanks

Customer:

stand by

V12Tech :

ok

Customer:

yellow is 7970-328 blue is 7975-328

V12Tech :

xlnt

V12Tech :

checking

V12Tech :


7710-3281 fan & limit switch.

Full Size Image
8866-3281 Fan Switch

Fan switch. F130-35F. Size 60T82. Replaces 8866-328, 6806A3341 & 6806-3341. It is also the closest replacement for 8865A-328, 8865A-3281, 8635-3281, 8635-328, 8665-3271, 8665-327, 8665-3281, 8665-328, 8871-3281, 8871-328, 8865A3281 &(NNN) NNN-NNNN Your price $13.82.
8866-3281 fan switch.
Full Size Image
7975-3281 Fan Switch

Fan switch. F110-20F. Size T-0-D60T82 or 60T82. Replaces 7660-328, 7660-3281, 7956-335, 7956-3351, 7966-327, 7966-3271, 7700-328, 7700-3281, 4066-328, 4066-3281, 7975-328, 7995-355, 7995-3551, 8665B328, 8665B3281, 8665-332 & 8665-3321. Your price $10.95.
7975-3281 fan switch.
Full Size Image
7995-3281/A Limit Switch

Limit switch shuts down gas valve if overheating occurs. L150-30F. Size 36TX41. Used in many 95,000 BTU furnaces. Replaces 7995-328, 7995-328/A & 7995-3281. Your price $8.20.
7995-3281A
Full Size Image
025-35380-000 Limit Switch

Limit switch shuts down gas valve if overheating occurs. L140-30F. Size 60T11 replaces previous size of 1NT01EL-2783 or 36TX41. Used in many 56,000 BTU furnaces. Replaces 7945-328, 7945-328/A, 7945-3281/A & 7945-3281, 7945-328/A, 025-27727-003, 025-35380-000, 02527727003 & S1-02535380000. Your price $10.01.
7945-3281A limit switch.
Full Size Image
025-35381-000 Limit Switch

Limit switch L145-30F. Size 60T11 which replaces size 1NT01EL-2784 or 36TX41. Used in many 70,000 Replaces S1-02535381000, 7970-3281, 7970-3281/A, 7970-328/A & 7970-328. Your price $10.01.
7970-3281A limit switch.
Full Size Image
7700-3591 Limit Switch (NLA)

Lower limit switch shuts down gas valve if overheating occurs. L165-30F. Size 60T11. Also known as part # XXXXX Replaces 7700-359, 3200-3281 & 6804-3321. No longer available - call for replacement.
7700-3591 limit switch.
Full Size Image
7705-3591 Limit Switch

Limit switch shuts down gas valve if overheating occurs. L145-20F. Size 60T11. Replaces 7705-359.Your price $13.14.
7705-3591 limit switch.
Full Size Image
7624A3591 Upper Limit Switch

Upper limit switch shuts down gas valve if overheating occurs. L180F degrees manual reset. Size 60TV15. Replaces 7624-A359, 7624-359, 7624-3591, 7675-359, 7724-3791, 7706A3591, 7706-3591 and 7675-3591.Your price $14.26.
7624A3591 limit switch.
Full Size Image
7990-3591 Limit Switch

Limit switch shuts down gas valve if overheating occurs. L180-30F. 1NT01EL-2782 or 36TX41. Replaces 7990-359.Your price $7.69.
7990-3591 limit switch
Full Size Image
7660-3591 Limit Switch

Limit switch shuts down gas valve if overheating occurs. L150-20F. Size 60T11. Replaces 7660-359, 7724-359 & 7724-3591. Your price $14.02.
7660-3591 limit switch.
Full Size Image
7680-3591 Upper Limit Switch

Upper limit switch shuts down gas valve if overheating occurs. L155-20F. Size 60T11. Replaces 7680-359.Your price $13.07.
7680-3591 limit switch.
Full Size Image
025-35358-000 Limit Switch

Upper limit switch shuts down gas valve if overheating occurs. 150F. Size 1NT08EL-4052 or 36TX41. Manual reset. Replaces 02535358000. Your price $14.67.
025-35358-000 limit switch.
Full Size Image
7680-3791 Upper Limit Switch

Upper limit switch shuts down gas valve if overheating occurs. L140-20F. Size 60T11. Replaces 7680-379.Your price $11.45.
7680-3791 limit switch.
Full Size Image
8866-3291 Limit Switch

Limit switch shuts down gas valve if overheating occurs. L135F. Manual reset. Size 60T15. Replaces 8866-329, 8866-326 & 8866-3261. Your price $11.71.
8866-3291 limit switch.
Full Size Image
6806-3351 Limit Switch

Limit switch shuts down gas valve if overheating occurs. L150-35F. Size 60T11 or 20601L65-663. Replaces 6806-335, 8880-3271, 8866-3271 & 8880A3271.Your price $15.50.
6806-3351 limit switch.


 

V12Tech :

Im looking its hard to seeee both numers i have i am stil looking

Customer:

So one is a upper and one is a lower switch

V12Tech :

7995-3281A
Full Size Image

V12Tech :

yes

V12Tech :

http://www.mobilehomerepair.com/ColemanGas.html

V12Tech :

this is where I found the pics

V12Tech :

7975-3281 fan switch.
Full Size Image

Customer:

That is the yellow one!

V12Tech :

yes

Customer:

did you find the blue one?

V12Tech :

the other is there too I think

V12Tech :

looking

V12Tech :

weird i dont see that one listed here

V12Tech :

still looking

Customer:

My unit is 57,000 BTU

Customer:

If that one goes bad it will turn off the gas right? Then the unit will not fire up.

V12Tech :

I dont see it but would ereplace it

V12Tech :

is it the correct#

Customer:

let me check

V12Tech :










































































































an and Limit Switches


Full Size Image
025-27792-001 Flame Rollout Switch

Temperature control switch with manual reset, L200F. Size 36TX16. Replaces 02527792001. Your price $9.27 each.
025-27792-001 temperature control switch.
Full Size Image
025-29041-005 Limit Control

Limit control switch. L140-30F. Size 36T01B3. Back plate measures 1-7/8" x 2-3/4" with two 1/4" spade terminals. 3" arm length. Replaces S1-02529041005.Your price $21.13.
02529041005 limit control L140-30F.
Full Size Image
025-31813-000 3" Limit Switch

Limit control switch. L160-30F or L160F-30. Size 36T01B3. Back plate measures 3/4" x 2-3/8" with two 1/4" spade terminals. 3" arm length. Replaces 02531813000. Also known as part # XXXXX and 1NT23L-2647. Sale price $12.76 each.
02531813000 temperature control switch L160-30F.
Full Size Image
025-31814-000 3" Limit Switch

Limit control switch. L150-30F or L150F-30. Size 36T01B3. Back plate measures 3/4" x 2-3/8" with two 1/4" spade terminals. 3" arm length. Replaces 02531814000. Also known as part # XXXXX and 1NT23L-2647. Your price $13.16 each.
02531814000 temperature control switch L150-30F.
Full Size Image
026-32588-017 Burner Limit Switch

Flame roll out switch. Manual reset. L350F. Size 36TX16. Replaces(NNN) NNN-NNNN& 02632588017. Your price $32.87 each.
026-32588-017 burner limit switch.
Full Size Image
2702-3191 Rollout Limit Switch

Flame roll out control senses when the flame 'rolls' out of the combustion chamber, shutting down the overfired burner. Manual reset. L300F. Size 1NT08L-3182 Replaces 2702-319, 026-34723-000, 026-34027-000, 02634723000 & 02634027000. Your price $7.94 each.
2702-3191 rollout limit switch.
Full Size Image
2845-3171 Fan Switch

Fan switch. F105-10F. Size 60T12. Your price $13.69.
2845-3171 fan switch.
2845-3191 Limit Switch

Limit switch with manual reset. L195F. Size 60T. Replaces 2845-319, 8865-326, 8865-3261, 8865A326 & 8865A3261. No longer available.
2845-3191 limit switch.
Full Size Image
2940-3191 Flame Rollout Switch

Flame roll out switch. Manual reset. L300F. Size 60T14. Replaces 2840-3191, 2840-319 & 2940-319. Your price $16.79.
2940-3191 flame rollout switch L300F.
Full Size Image
7710-3281 Fan & Limit Switch

Fan & limit switch. F105-20F. Size 60T82. Replaces 7710-328.Your price $13.29.
7710-3281 fan & limit switch.
Full Size Image
8866-3281 Fan Switch

Fan switch. F130-35F. Size 60T82. Replaces 8866-328, 6806A3341 & 6806-3341. It is also the closest replacement for 8865A-328, 8865A-3281, 8635-3281, 8635-328, 8665-3271, 8665-327, 8665-3281, 8665-328, 8871-3281, 8871-328, 8865A3281 &(NNN) NNN-NNNN Your price $13.82.
8866-3281 fan switch.
Full Size Image
7975-3281 Fan Switch

Fan switch. F110-20F. Size T-0-D60T82 or 60T82. Replaces 7660-328, 7660-3281, 7956-335, 7956-3351, 7966-327, 7966-3271, 7700-328, 7700-3281, 4066-328, 4066-3281, 7975-328, 7995-355, 7995-3551, 8665B328, 8665B3281, 8665-332 & 8665-3321. Your price $10.95.
7975-3281 fan switch.
Full Size Image
7995-3281/A Limit Switch

Limit switch shuts down gas valve if overheating occurs. L150-30F. Size 36TX41. Used in many 95,000 BTU furnaces. Replaces 7995-328, 7995-328/A & 7995-3281. Your price $8.20.
7995-3281A
Full Size Image
025-35380-000 Limit Switch

Limit switch shuts down gas valve if overheating occurs. L140-30F. Size 60T11 replaces previous size of 1NT01EL-2783 or 36TX41. Used in many 56,000 BTU furnaces. Replaces 7945-328, 7945-328/A, 7945-3281/A & 7945-3281, 7945-328/A, 025-27727-003, 025-35380-000, 02527727003 & S1-02535380000. Your price $10.01.
7945-3281A limit switch.
Full Size Image
025-35381-000 Limit Switch

Limit switch L145-30F. Size 60T11 which replaces size 1NT01EL-2784 or 36TX41. Used in many 70,000 Replaces S1-02535381000, 7970-3281, 7970-3281/A, 7970-328/A & 7970-328. Your price $10.01.
7970-3281A limit switch.
Full Size Image
7700-3591 Limit Switch (NLA)

Lower limit switch shuts down gas valve if overheating occurs. L165-30F. Size 60T11. Also known as part # XXXXX Replaces 7700-359, 3200-3281 & 6804-3321. No longer available - call for replacement.
7700-3591 limit switch.
Full Size Image
7705-3591 Limit Switch

Limit switch shuts down gas valve if overheating occurs. L145-20F. Size 60T11. Replaces 7705-359.Your price $13.14.
7705-3591 limit switch.
Full Size Image
7624A3591 Upper Limit Switch

Upper limit switch shuts down gas valve if overheating occurs. L180F degrees manual reset. Size 60TV15. Replaces 7624-A359, 7624-359, 7624-3591, 7675-359, 7724-3791, 7706A3591, 7706-3591 and 7675-3591.Your price $14.26.
7624A3591 limit switch.
Full Size Image
7990-3591 Limit Switch

Limit switch shuts down gas valve if overheating occurs. L180-30F. 1NT01EL-2782 or 36TX41. Replaces 7990-359.Your price $7.69.
7990-3591 limit switch
Full Size Image
7660-3591 Limit Switch

Limit switch shuts down gas valve if overheating occurs. L150-20F. Size 60T11. Replaces 7660-359, 7724-359 & 7724-3591. Your price $14.02.
7660-3591 limit switch.
Full Size Image
7680-3591 Upper Limit Switch

Upper limit switch shuts down gas valve if overheating occurs. L155-20F. Size 60T11. Replaces 7680-359.Your price $13.07.
7680-3591 limit switch.
Full Size Image
025-35358-000 Limit Switch

Upper limit switch shuts down gas valve if overheating occurs. 150F. Size 1NT08EL-4052 or 36TX41. Manual reset. Replaces 02535358000. Your price $14.67.
025-35358-000 limit switch.
Full Size Image
7680-3791 Upper Limit Switch

Upper limit switch shuts down gas valve if overheating occurs. L140-20F. Size 60T11. Replaces 7680-379.Your price $11.45.
7680-3791 limit switch.
Full Size Image
8866-3291 Limit Switch

Limit switch shuts down gas valve if overheating occurs. L135F. Manual reset. Size 60T15. Replaces 8866-329, 8866-326 & 8866-3261. Your price $11.71.
8866-3291 limit switch.
Full Size Image
6806-3351 Limit Switch

Limit switch shuts down gas valve if overheating occurs. L150-35F. Size 60T11 or 20601L65-663. Replaces 6806-335, 8880-3271, 8866-3271 & 8880A3271.Your price $15.50.
6806-3351 limit switch.



Our network of back-up suppliers help keep out-of-stocks to a minimum.
































































Flame Sensors and Ignitors


Full Size Image
025-35354-000 Remote Flame Sensor

Senses whether or not the burner is firing.Your price $18.38.
Quick Tech Tip
025-35354-000 flame sensor.
Full Size Image
2631-3481 Thermocouple 24"

Thermocouple senses pilot light and closes gas valve if none sensed. Used in most all furnaces with a pilot light except those with a sparker. Your price $8.95.

2631-3481 thermocouple.
Full Size Image
7975-3881 Remote Flame Sensor

Senses whether or not the burner is firing. Replaces 7975-388P/A & 7975-388. Was $80.36,Overstock price $49.00.
Quick Tech Tip
7975-388PA flame sensor
Full Size Image
025-41021-000 Hot Surface Ignitor

Glows to light burner. 120V. Fragile. Do not touch with bare hands while installing. Replaces 1474-051, 1474-0521, 1474-052P, 02541021000 & 025-41021-000. Your price $39.00.

1474-052P hot surface ignitor
Full Size Image
7995-3061 Electrode Sparker

Sparker with flame sensor. Your price $80.62.
Quick Tech Tip
7995-3061 electrode.
Full Size Image
7970-377P Electrode Sparker

Electrode emits a spark to ignite pilot light. Your price $60.00.
7970-377P 
sparker.
Full Size Image
025-32625-000 Ignitor

Ignitor glows and lights burner. Fragile. Do not touch with bare hands while installing. Used on DGAD060CD, DGAE080CD & DGAF100CD furnaces. Also known as model number 271N & 271NM. Replaces 025-32626-000, 025-31801-000, 025-30277-700, 025-31802-000 & 025-30385-700. Your price $43.06.
View Conversion Instructions
025-32625-000 ignitor.
Full Size Image
025-30788-700 Flame Sensor

Flame sensor shuts down gas valve if no flame sensed. 5" total length. Bare sensing rod measures 1.75". Used on DGAD060CD, DGAE080CD & DGAF100CD furnaces. Replaces 025-30788-000, 02530788000 & 02530788700. Your price $23.12.
Quick Tech Tip
025-30788-700 flame sensor.
Full Size Image
2667-3051 Electrode Assembly

Electrode assembly often used in residential furnaces.Your price $127.88.
2667-3051 electrode assembly.
Full Size Image
2702-311P Sensor Rod

Sensor rod senses flame. 3" long, bent end is 2.25" long. Replaces 2702-311.Your price $18.45.
Quick Tech Tip
2702-311P sensor rod.
Full Size Image
2940-3041 Electrode Assembly.

Electrode assembly. Measures 6.25" long. Replaces 2940-304, 2940-3051, 2940-305 & 22-100000-614.Your price $119.12
2940-3041 electrode assembly.
Full Size Image
025-27773-700 Flame Sensor

Flame sensor. Total lengh is 4". Sensing rod is 2.5" long. Replaces 02525434700 & 02525434000 02527773000, 025-25434-700 & 025-25434-000. Your price $16.76.
Quick Tech Tip
025-27773-700 Coleman flame sensor.
Full Size Image
785-001 Automatic Pilot Relight Kit.

Pilot light reignitor kit automatic lights pilots that blow out. Operates on either 120 or 24 volt. Instructions show hooking up both power sources, but we'd recommend only hooking up 1 power source. Includes bracket for connecting sparker near pilot light. Removing burner/pilot assembly and drilling screw holes may be required. Also includes 105C appliance wire and ends (not shown) for connecting ignitor to power. This is an after-market part. Although frequently added to all types of appliances with pilot lights such as furnaces, water heaters, space heaters, dryers, stoves etc, most manufacturers do not recommmend using after-market add-ons and will general void any warranty. Replaces 7700AAF526. Your price $75.75.
Installation instructions
Pilot light ignitor sparker reignitor.
Customer:

blue is 7970-328

V12Tech :

ok

V12Tech :

looking

V12Tech :

7975-3281 fan switch.
Full Size Image

V12Tech :

This is all I see

V12Tech :

I would bet one is newer

V12Tech :

obsolete my guess

V12Tech :

likely replaced with this one

V12Tech :

checking

Customer:

I noticed on my yellow switch it has a double wire connector on one side

V12Tech :




























































































































































































































































































































ITEMDESCRIPTIONNO.
REQ.
USED ON
MODEL
MFG
PART#
1

Roof Jack (See Furnace Wiring Dia.)


1All4000 Series
2

Casing Top


1All7945A5721
3

Upper Limit Switch (0-180 deg. Manual Reset)


1All7624A3591
4

Booster Assembly (Includes 5-9)


1All7990-6451
5

Booster Gasket


1All7995A386
6

Impellor (3-13/16 x 1-7/8 x 3/8)


1All8865-3611
7

Mount Plate (Booster Motor)


1All8865A1471
8

Motor Mount (Rubber 4/pkg.)


1All8865B1281
9

Booster Motor - 3000 RPM


1All7995-3169
10

Cover (Control Box)


1All7945A1351
11

Mounting Plate (Ignition Module)


1All7970-120
12

Ignition Module (Triple Try)


1All1474-0061
13

Observation Plate w/Gasket
Gasket (Observation Plate)


1
1
All7706-5251
7706-3251
14

Gas Valve 24V .5 Amp 1/2" x 3/8"


1All7707-3261
15

Note: See Chart for Burner Orifice #


All-
16

Valve Bracket


1All7945B5151
17

Panel (Coil Cavity 19-13/16")


1All7656A5201
18

Customer Envelope


1All1973-072/A
19

Gasket Pkg. (Heat Exchanger)


1All7945-3011
20

Heat Exchanger w/Gaskets
Heat Exchanger w/Gaskets
Heat Exchanger w/Gaskets


1056
070, 075
095
7956-5751
7975-5751
7995-5751
21

Gasket Pkg. (Heat Exchanger)


1All7945-3011
22

Motor 056, 070 & 075
Motor 056, 070 & 075
Motor 095
Motor 095


DGAT, DLAS
DGAM
DGAT, DLAS
DGAM
7966-311P
1468-2209
1468-2129
1468-2209
23

Scroll


7966A530
24

Motor Mount (3/pk)


7670-3551
25

Thermostat (Adj. Ant.)


1All7670-368P
26

Connector Plug


7680-348
27

Motor Clamp


7670-5391
28

Run Capacitor - 095*
(7.5 Mfd. 370V.)


1499-4461
29

Blower Wheel
(10-5/8 dia. x 7-1/8 x 1/2)


1472-2751
30

Filter Retainer


2All7970-3451
31

Filter (19-3/8 x 35-3/4 x 1/4)


1
All
7660-3401
32

Panel (Upper)
Panel (Upper)


1
1
DGAM
DGAT, DLAS
7975-1561
7956-5231
33

Panel (Lower)
Panel (Lower)


1DGAM, DGAT
DLAS
7956-1571
7956-1631
34

Remote Sensor


1All7975-3881
35

Hot Surface Ignitor


1All1474-0521
36

Ignitor Sheild


1All7970-179
37

Mounting Plate (Burner)


1All7945-1631
38

Burner Assy.
(Less Gas Valve-Inc. 12, 13 16)


1All7970-5851/A
39

Transformer (115 - 24V 40VA)
Transformer (115 - 24V 15VA)


1DGAM, DGAT
DLAS
2940A3541
7945-3551
40

Booster Relay


1All7956-3671
41

Fan Switch (C - 110 deg. - 90 deg.)


1All7975-3281
42

Limit Switch
(Open--140 deg. Close--110 deg.)
Limit Switch
(Open--145 deg. Close--115 deg.)
Limit Switch
(Open--150 deg. Close--120 deg.)


1

1

1
056

070, 075

090
7945-3281

7970-3281

7995-3281
43

A/C Relay


1All7975-3771
44

Junction Box Cover


1All7956-1121
V12Tech :

1 is upper limit

V12Tech :

1 is fan delay

V12Tech :









Fan Switch (C - 110 deg. - 90 deg.)


1All7975-3281
V12Tech :









Limit Switch
(Open--145 deg. Close--115 deg.)
Limit Switch
(Open--150 deg. Close--120 deg.)


1

1

1
056

070, 075

090
7945-3281

7970-3281
Customer:

So they just anded a 1 at the end of the number?

V12Tech :

accidentally sent extra one

V12Tech :

7970-328 7975-328 yep

V12Tech :

It looks like you could use a slightly different temp setting

Customer:

I noticed on my yellow switch it has a double wire connector on one side

V12Tech :

theyv are 10 degrees apart

Customer:

I noticed on my yellow switch it has a double wire connector on one side

V12Tech :

Is there wires on both

Customer:

what do I do about the double wire connection on the switch?

Customer:

yes 2 wires on one side

V12Tech :

I would replace as is

V12Tech :

is there a reason why not?

Customer:

but the new switch only has one connection on both sides? the yellow one

V12Tech :

Oh do you mean a Y added on?

V12Tech :

Thhey make commectors to add a y

V12Tech :

is this added on

V12Tech :

slides over terminal

V12Tech :

The switch is like a drawbridge

V12Tech :

it just closes and opens

Customer:

oh it comes off I just thought the switch was made with two connections

V12Tech :

if you need a Y it must been added?

V12Tech :

ok good

V12Tech :

Very observant!

V12Tech :

You are doing really good here!

V12Tech :

Not everyone can do this

Customer:

thank you

V12Tech :

You must have experience?

V12Tech :

Mechanically minded!

Customer:

no just cant afford to have someone do it for me...lol. I try and tackle repais myself

V12Tech :

LOL

V12Tech :

I used to get in trouble for fixing units too cheap lol

V12Tech :

I never won the parts sales but won least call backs

V12Tech :

Contractors want $300 per call min

V12Tech :

they tellus

Customer:

thats funny but honest in my book!

V12Tech :

Yes

V12Tech :

The markup is wild

V12Tech :

R22 freon is $300 for 30 lbs sells $75 lb

V12Tech :

Nice!

Customer:

I know...thats why I am picking your brain...lol

V12Tech :

I cant do it

V12Tech :

Thats ok!

V12Tech :

I really love my job'

Customer:

yea that freon is way out of control

V12Tech :

Yes llike heroin lol

V12Tech :

I imagine??

Customer:

lol

V12Tech :

I donrt know lol

Customer:

this is a good way to make extra money for you techs!

V12Tech :

Yes!

Customer:

Hope they give you a good cut!

V12Tech :

I actually had a pennysaver ad for 349 get me zero work 1 month

V12Tech :

50%

Customer:

Wow! Do you do good on here?

Customer:

what state are you in?

V12Tech :

Well I would if everyone paid, but as its satisfaction guarenteed some are not wanting to pay

V12Tech :

Ca

V12Tech :

Sacramento

Customer:

Im in CA too bay area!

V12Tech :

And some ratepoorly and dont pay ouch!@

V12Tech :

WOW

V12Tech :

Sac has it pretty bad now

Customer:

I will rate you good and pay...:):):)

V12Tech :

Tank you so much!!

Customer:

Thank you sir!

V12Tech :

I would do this for nothing, I used to onother forums long ago

V12Tech :

Thank you

V12Tech :

I like saving peple$$

V12Tech :

It's been nice speaking with you,,or typing

Customer:

You do a good job at it and saved me!

V12Tech :

I wish we could speak

V12Tech :

Thanks!

Customer:

Happy New Years to you and yours!

V12Tech :

Happy New Years to you too!

V12Tech :

You have 30 days to re open

Customer:

Bye

V12Tech :

just talk lol

V12Tech :

bye

V12Tech :

Thank you!

V12Tech, HVAC Technician
Category: HVAC
Satisfied Customers: 260
Experience: A.A.S. MET, E.P.A cert, Certificate of Excellence HVAC/R
V12Tech and 4 other HVAC Specialists are ready to help you
Expert:  V12Tech replied 1 year ago.
Our chat has ended, but you can still continue to ask me questions here until you are satisfied with your answer. Come back to this page to view our conversation and any other new information.

What happens now?

If you haven’t already done so, please rate your answer above. Or, you can reply to me using the box below.
Expert:  V12Tech replied 1 year ago.
Hello Kevin Keith here,
It was nice speaking with you about the furnace Kevin, I wanted to schedule a follow up to insure you are satisfied with the issue.
Thank you,
Keith.


P.S.
You didn't rate my service before you left, was this an oversight? I hope you are satisfied with my service?
Keith.
Expert:  V12Tech replied 1 year ago.
Thank you very much!

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial