Have 2 x Tempstar DC90 furnaces installed Dec 1996. One does

Customer Question

Have 2 x Tempstar DC90 furnaces installed Dec 1996. One does upstairs, one does downstairs. Replaced older honeywell thermostats with new honeywell thermostats. Each furnaces is controlled by its own T-stat. Renovation required new pull of wires (insufficent # XXXXX on old install for new T-stats) which also required Honeywell Wiring Module (THP9045). Problem is this, inducer blower will not shut-off on one of the furnaces - runs continuously while other furnace operates normally. If a simple thermostat is installed in lieu (cobbled in beside the furnace), then inducer blower works OK. Go figure! Any insightd? Bad T-stat? bad wiring Module? bad furnace control board? bad furnace sensor?
Submitted: 1 year ago.
Category: HVAC
Expert:  wwhac1985 replied 1 year ago.

wwhac1985 :

Do you have a volt ohm meter

wwhac1985 :

Is your furnace flashing any fault codes

Customer :

Checking

Customer :

No multimeter.

Customer :

no codes

wwhac1985 :

have you disconnected jsut the W wire on the furnace control board and left all others in place

Customer :

Checked with Multi-meter previously and T-stat voltages (including call) were fine

wwhac1985 :

sorry Just

wwhac1985 :

Have you reset the power to the furnace

Customer :

dissconnect W? on wiring terminal board or furnace control board?

wwhac1985 :

Yes

Customer :

not sure on disconeecting power (just via switch)

wwhac1985 :

yes or breaker

Customer :

then power was reset multiple times

wwhac1985 :

Does the furnace start up normal and heat

Customer :

Normal start and heat (fresh air blower cycles normally) but inducer motor keeps running

wwhac1985 :

Have you removed the control board to see if there is any burn marks on it

Customer :

no burns

wwhac1985 :

If you have all thermostat wires disconnected from furnace and the Inducer motor is still running then it is a faulty control board there is a relay in the board that when it gets a connection from r-w it energizes a relay on the control board that closes a circuit passing 120 volts to the inducer motor.

wwhac1985 :

If there is no wires on the low voltage terminals and you check across r-w there should be 24 volts

Customer :

used simple T-stat and looks to run A-OK; use new T-stat and is NG

wwhac1985 :

How do you currently have the new thermostat and contol module wired up

Customer :

AS per honeywell instructions

Customer :

both furnaces done identically, 1 OK 1 is not

wwhac1985 :

Have you checked the continuity between r-w with a multimeter

wwhac1985 :

coming from thermostat

Customer :

T-stat voltages OK

wwhac1985 :

Do you have a furnace only or is there a a/c unit also

Customer :

No a/c, just furnace

wwhac1985 :

How many wires did the existing thermostat have

Customer :

2

wwhac1985 :

what kind of thermostat do you currently have on the wall

Customer :

new wire pull has 4

wwhac1985 :

what are you using the wire module thp9045 for

Customer :

T-Stat is a Honeywell OEM for Lutron (wireless) Previous T-Stat was an older Honeywell programmable version

Customer :

New T-stat requires 2 pair of wires - module allows shared common.

wwhac1985 :

Is your current thermostat wireless

wwhac1985 :

Do you have the model number of the thermostat

Customer :

New T-stat wireless settings control, but all T-stats are hardwired on wall

Customer :

T-Stat is LR-HWLV-HVAC

wwhac1985 :

Does the thermostat still have the r-rc jumper still installed

Customer :

just checked, no jumper

wwhac1985 :

The thermostat comes with a factory installed jumper check your other thermostat to see if it still has the jumper installed

wwhac1985 :

Install factory jumper between r-rc after turning off power then go into installer setup and check install option 900

Customer :

no jumper on other furnace T-stat

wwhac1985 :

it is a brass flat piece of metal between them have you checked option 900 in the installer setup

Customer :

sorry, rechecked and found small jumper on both T-stats from R to Rc

wwhac1985 :

ok I was looking at the wiring diagrams and application use for the module it is used for a fan and compressor to be run off 1 wire if you only have 2 wires what terminals do you have them hooked up to

wwhac1985 :

is the thermostat recognizing the module

Customer :

goes to R, W, K, and C (with jumpered R-Rc)

wwhac1985 :

so you have 4 wires at the thermostat and they go to the module then only 2 wires that go to the furnace and module

Customer :

yes

wwhac1985 :

Have you tried switching the two modules around to see if you still have the same problem as i recall you dont have a multimeter

wwhac1985 :

also when you disconnect the r and w wires to the furnace the furnace should just stay off no inducer motor running

Customer :

not yet. Can also swap t-stat heads on the bases. Can we pick this up later please? Time zone here has me up too late

wwhac1985 :

yes that is fine

Customer :

thanks

Expert:  V12Tech replied 1 year ago.
Have you checked the continuity between r-w with a multimeter
wwhac1985 : coming from thermostat
Customer : T-stat voltages OK
......................................................

used simple T-stat and looks to run A-OK; use new T-stat and is NG
.............................................................
You said induced draft runs, so it is a gas furnace.K is for a compressor!

Customer : No a/c, just furnace

You have no compressor or AC!!!!


Customer : New T-stat requires 2 pair of wires - module allows shared common.


No you dont need this for heat only with a gas furnace!
The sared common you describe is to run the green fan circuit with the compressor, just as a thermostat will in auto position, the yellow is jumped internally to green in auto!
This will simply run the compressor and fan together rather than using green and yellow!


.................................................................

The THP9045 Wiring Module is designed to be used with applicable thermostats in 1 Heat/1
Cool retrofit applications where only 4 wires are available. The K terminal on the thermostat
can be used to operate both the fan and compressor on a single wire, and the module is
designed to receive the signal from the K terminal, split that signal and reroute it to operate
the compressor, and/or fan for normal operation. See the THP9045 manual for further details
Technical Assistance | 24 hours a day, 7 days a week | www.lutron.com
U.S.A. / Canada: 1.800.523.9466 | Mexico: +1.888.235.2910
Other Countries: +1.610.282.3800
........................................
You do not need that K terminal or the kit!
Customer : No a/c, just furnace
..............................................................



Programming by a Lutron Factory Trained Installer
For full functionality, the HVAC Controller must be programmed to a Repeater and PC software
must be used by a Lutron factory-trained installer. For questions on how to become a qualified
installer, please contact your local Lutron representative.
To add the thermostat to a Lutron system:
Use the Lutron PC software to start activation
mode. When a Lutron system is in activation mode,
an unaddressed thermostat will show “Device Is
Unaddressed” at the top of the screen.

...........................................

Heat Only System (Series 20)
Rc [R+Rc joined by jumper]
R Series 20 valve terminal “R” [1]
W Series 20 valve terminal “B”
Y Series 20 valve terminal “W”
C 24 V common [3]
S1/S2 Optional remote sensor

THE "K" terminal is not used in Heat only.
in fact the whole thing is not required!

Customer : New T-stat requires 2 pair of wires - module allows shared common.

........................................
Heat Only System With Fan
Rc Power [1]
R [R+Rc joined by jumper]
W Heat relay
G Fan relay
C 24 V common [3]
S1/S2 Optional remote sensor

................................................
Heat Only System
Rc Power [1]
R [R+Rc joined by jumper]
W Heat relay
C 24 V common [3]
S1/S2 Optional remote sensor
.........................................
http://resi.lutron.com/LinkClick.aspx?fileticket=iIRX1F8NMpk%3D&tabid=585&mid=1452

Advanced Functions Getting Started
2. Press and hold
blank center key
until the display
changes.
1. Press SYSTEM.
Press s/t to
select function
Function Setting
Press s/t to
change setting
SUN
SYSTEM
HEAT
M33008
M33009
DONE
0280 0
DONE CANCEL
AM
6:01
HEAT SUN
M32755
3. Change settings as
required
4. Press DONE to exit &
save changes.


perating Manual
P/N 041-339 Rev. A 14 69-2656EFS—01
Advanced Functions
Backlight Settings
Function 0280 Press s/t to change the backlight settings:
Options: 0 Backlight ON for approx. 8 seconds after keypress
1 Backlight always on low intensity, with full brightness after keypress
Temperature format (°F/°C)
Function 0320 Press s/t to set the temperature display format:
Options: 0 Fahrenheit
1 Celsius
Furnace Filter Change Reminder
Function 0500 Press s/t to change the furnace filter change reminder:
Options: 0 Disabled
1 10 R.T. Day
2 30 R.T. Day
3 60 R.T. Day
4 90 R.T. Day
5 120 R.T. Day
6 180 R.T. Day
7 270 R.T. Day
8 365 R.T. Day
9 30 C Days
10 60 C Days
11 90 C Days
12 120 C Days
13 180 C Days
14 365 C Days

Advanced Functions
Humidifier Pad Replacement Reminder
Function 0510 Press s/t to set the humidifier pad replacement reminder:
Options: 0 Disabled
1 90 C Days, 30 R.T. Days
2 180 C Days, 60 R.T. Days
3 365 C Days, 90R.T. Days
UV Lamp Replacement Reminder
Function 0520 Press s/t to set the UV lamp replacement reminder:
Options: 0 Disabled
1 365 Days
2 730 Days (2 years)
Clock format
Function 0640 Press s/t to choose a clock format:
Options: 12 12-hour time (i.e., “3:30 pm”)
24 24-hour time (i.e., “15:30”)
Screen lock
Function 0670 Press s/t to choose a screen lock setting (see page 10):
Options: 0 Screen is unlocked (fully functional)
1 All functions locked except temperature controls and CANCEL key
2 Screen is fully locked



APPLICATION
The THP9045 Wiring Module is designed to be used with
applicable thermostats in 1 Heat/1 Cool retrofit applications
where only 4 wires are available. The K terminal on the
thermostat can be used to operate both the fan and
compressor on a single wire, and the module is designed to
receive the signal from the K terminal, split that signal and reroute it to operate the compressor, and/or fan for normal
operation.
Use with the following thermostats:
— THX9321R
— T2060F3080

ACUSTOMER-fl289470- : No a/c, just furnace

THIS IS NOT EVEN REQUIRED NO AC!
Not yelling, just wanted to not blend in.

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar