I had the thermostat set at 74 degrees and woke up to a temp.

 
A-1 Tech's Avatar
  • Answered by:A-1 Tech
  • Service Manager
  • Positive Feedback: 98.8 %
  • Accepted Answers: 381
Verified Expert
in HVAC

Recent Feedback

Positive
Nice job
Positive
Very helpful and clear in his explanations. A good experience
Positive
Satisfied with answer. Please understand I'm on a budget. That is why I asked...
Positive
very thorough! very knowledgeable. great job!!
Positive
thank you Ron Roye
Positive
Awesome site! Thanks again Ron!
Positive
I very much appreciated the help. Very friendly and patient. I will recommend...
Positive
Very knowledgeable and helpful.
Positive
Ron was awesome. Very knowledgeable. Patient. Helpful. Saved me $500 by not...

Customer Question

I had the thermostat set at 74 degrees and woke up to a temp. of 79 degrees in the house. I went outside to look at the A/C unit and the fan was not spinning and there was a buzzing coming from the unit. Bad motor or condenser?

Submitted: 322 days and 6 hours ago.
Category: HVAC
Value: $30
Status: CLOSED

Accepted Answer

Picture
Expert:  A-1 Tech replied322 days and 6 hours ago.


A-1 Tech :

Hello, my name is XXX XXX I will assist you today

Customer :
A-1 Tech :

Was this a slight buzz sound or more like the compressor was running?

Customer :
Customer :

Hi Ron,

Customer :
Customer :

It was more of a slight buzzing sound. It did not sound like anything was running, but more stuck

A-1 Tech :

Have you checked your breakers?

Customer :

I have not, checked those yet. Should I trip the breaker for the A/C unit

A-1 Tech :

The buzz is the contactor energized, so the t-stat is calling for cooling.

A-1 Tech :

Yes, lets be sure it's not the breaker.

Customer :

Ok, I will do that right now

A-1 Tech :

Sometimes they do not look tripped when they actually are. This will be a double breaker. Turn hard to the off position, then back on. This will be in your main breaker panel for the home.

Customer :

The unit still has a buzzing sound after I tripped the breaker

A-1 Tech :

Would you happen to have a volt meter?

Customer :

Sorry, I do not

A-1 Tech :

okay.

A-1 Tech :

Please take the cover off the unit to get to control panel. We will want to locate the contactor. That is what is buzzing

A-1 Tech :

Full Size Image

Customer :

ok, this will take a few minutes to do

A-1 Tech :

it will look something like this

A-1 Tech :

no problem

Customer :

ok, the cover is off

A-1 Tech :

in the middle of the contactor, these should be pulled in, can you see that they are? they are spring loaded.

A-1 Tech :

Please assume that we have 230 volts to the unit. So be careful where you touch.

Customer :

i do not see a part that looks like the pic above

A-1 Tech :

What is your unit brand?

Customer :

it says goodman manufacturing on the label I see

A-1 Tech :

okay, do you have a model number, I can pull manual?

Customer :

Model CKL-30-1E

A-1 Tech :

great, I will pull that manual, it will take a few minutes.

Customer :

ok

Customer :

Ron,

I just tripped the breaker a couple more times and turned it on again. The fan is spinning this time.

A-1 Tech :

great

A-1 Tech :

no compre4ssor though?

Customer :

The fan is spinning and the unit seems to be running. Not sure what you mean by compressor?

A-1 Tech :

okay

A-1 Tech :

is it blowing warm air out the top of the unit?

A-1 Tech :
A-1 Tech :

also, the insulated line outside should be getting cool-cold

Customer :

air is blowing out the top of the unit, it's not all that warm though

Customer :

the insulated line is cool, but not all that cold

A-1 Tech :

okay, it sounds like the compressor is running, are you getting cool air to the home now?

Customer :

the air running into the house isn't all that cold yet, but it's blowing up through the vents

A-1 Tech :

great.

A-1 Tech :

This could have been a one time tripped breaker, maybe lights flickered or something, or it could be other problem not showing right now.

A-1 Tech :
A-1 Tech :

Keep an eye on it, the outdoor motor could run for a while then over heat and shut off.

Customer :

I am a little concerned with the air blowing into the house not being as cold as it normally is

A-1 Tech :

this would be possibly low on refrigerant

A-1 Tech :
A-1 Tech :

It will take a few minutes however for the system to reach peak performance.

A-1 Tech :
A-1 Tech :

Do you have a thermometer?

A-1 Tech :

Full Size Image

A-1 Tech :

this is inside control compartment. 181 is the contactor

Customer :

I do not see the thermostat in the unit

A-1 Tech :

to the left is the capacitor, please observe is this capacitor swollen and it's overall condition.

A-1 Tech :

no, I was referring to a personal thermometer to check air temperature blowing out the vents

Customer :

I also noticed the coils around the unit are covered in dust and dirt from being next to the woods. Should this be cleaned out too

Customer :

Ah, I will check with a thermometer

A-1 Tech :

yes, you can wash these coils out. please turn the breakers off first and do not get water on fan motor.

A-1 Tech :

a water hose will work fine for this

Customer :

The capacitor is on the outside of the unit correct?

A-1 Tech :

this can be done after we are finished, that is not why the unit tripped during the night.

A-1 Tech :

capacitor is inside the control panel inside the unit

Customer :

No nothing looked swollen on the inside of the unit

A-1 Tech :

Full Size Image

A-1 Tech :

these are capacitors

A-1 Tech :

okay, lets check the temp coming out the vent

Customer :

no it does not look swollen

A-1 Tech :

They can be bad without swelling, but swelling is good indicator.

Customer :

The temp. from the personal thermometer doesn't get below 77 degrees

A-1 Tech :

okay, it sounds like the compressor may not be running. Please see if that insulated line is sweating and cold, the smaller line should be warm that is not insulated.

A-1 Tech :

77 sounds like same temp as the room temp

Customer :

ok, i just went out to the a/c unit and the fan is not longer spinning and the unit sounds like it is off. Air is still blowing through the vents in the house even though the temp. is 80 and I have the a/c set at 74

Customer :

the insulated line is not cool and feels the same as the smaller line

A-1 Tech :

the breaker may have tripped again

Customer :

Crap!

A-1 Tech :

yep

A-1 Tech :

lets try to reset again

Customer :

Now I get nothing. The unit doesn't start up and no air blows through the vents

A-1 Tech :

the breaker tripping outside should not have effeced the air out the vents, that would be a seperate breaker.

Customer :

great! Not sure what happened now

A-1 Tech :

what type heat do you have?

A-1 Tech :

do you still hear a buzz outside?

Customer :

yes, the buzzing is back and the fan does not blow

A-1 Tech :

fan outside or inside?

Customer :

fan outside on the ac unit does not move again

A-1 Tech :

okay, but fan inside is blowing?

Customer :

it was blowing a few minutes ago, but when I turned off the ac to trip the breaker again, the fan inside stopped blowing as well.

A-1 Tech :

okay, you may be turning off the indoor breaker. Do you have electric heat?

Customer :

no I do not have electric heat, I have natural gas heat. In the fuse box I am tripping the double fuse for the AC

A-1 Tech :

okay

Customer :

ok, the fan for inside the house is blowing again, but the ac unit is still not running

A-1 Tech :

Lets turn the breaker off to the outdoor unit. You will need to remove the top grille on the unit to feel the motor and see if it is hot. I expect it to be very hot. Also please feel the compressor to see if it is hot, very hot. I think the motor and compressor may be off on over loads.

A-1 Tech :

If you have a disconnect mounted on the wall by the outdoor unit. Turn it off or pull the plug inside it for safety.

Customer :

Ok, so I just went out to the ac unit and the buzzing was still there and the fan not moving. I nudged the fan with a stick and it started to spin at full speed.

A-1 Tech :

ok, cool

A-1 Tech :

that tells me you probably have a bad capacitor. It could be the motor, but usually is the capacitor.

Customer :

ok, that is something I cannot fix on my own..correct?

A-1 Tech :

The only way to tell for sure would be with a meter that can check capacitors.

Customer :

volt meter?

A-1 Tech :

They are very simple to replace. Finding one today may be a problem

A-1 Tech :

volt meter that can also check capacitors. Some volt meters do not check capacitors.

Customer :

Really, they are simple to replace? Yeah, I doubt today is the day to find anything ac repair related

A-1 Tech :

You may find a dealer that will sell you a capacitor.

A-1 Tech :

you will need a : 5/35/370 volt

Customer :

what would be the cost to have someone do it for me?

A-1 Tech :

this can vary depending on the dealer and his pricing and can vary a lot.

Customer :

ballpark high and low please

A-1 Tech :

the capacitor itself should run about $40.00

A-1 Tech :

They will charge a service call then the price of capacitor installed. $200.00

A-1 Tech :

Most companies use a flat rate price guide.

Customer :

ok, kind of what I was expecting.

A-1 Tech :

You can do it yourself for about $40.00

Customer :

if it is just a capacitor, I might give it a try myself

A-1 Tech :

But, when they come out, they should also check your refrigerant for you.

A-1 Tech :

Where do you live?

Customer :

You also mentioned bad motor earlier, did you mean bad fan motor?

Customer :
Customer :

I live in Minneapolis

A-1 Tech :

yes, bad outdoor motor, but when you said it started with a little help, that makes me think capacitor.

A-1 Tech :

It could be the motor, but usually the capacitor.

A-1 Tech :

Do you have a Grainger near you?

Customer :

what sort of cost would a motor be

Customer :

Yes, there are a couple near by

A-1 Tech :

A motor at Grainger would run about $100.00, dealer cost to install would be about $450-$550

A-1 Tech :

I would go to Grainger and get the new capacitor

Customer :

man I hope it's the capacitor!

Customer :

ok, I will stop at Grainger tomorrow to get one.

A-1 Tech :

It is fairly inexpensive, to try first

A-1 Tech :

Note:

A-1 Tech :

Be sure power is off to unit, then short out the capacitor terminals to each other, then replace wire for wire

A-1 Tech :
A-1 Tech :

The capacitor will be labeled: Herm COM Fan

A-1 Tech :
A-1 Tech :

I will be available for follow up if needed.

Customer :

Thanks so much for your help Ron. How would I follow up with you?

A-1 Tech :

You can also mark what color wire goes to each terminal and take the old capacitor with you

A-1 Tech :

Just come back to this question. I will also mark you for follow up tomorrow.

Customer :

Thanks..One last thing, the fan is still blowing on the unit outside, however, there is no air blowing out the top of the unit

A-1 Tech :

Most service techs will have this on their truck if you want to try to find one who will sell you the part. dealer cost is about $18.00 just to keep them honest.

A-1 Tech :

That is fine, the fan will blow inside untill you turn the thermostat off.

A-1 Tech :

If a dealer will sell you one for $40.00. that is not bad

A-1 Tech :

Do you have further questions for now?

Customer :

I don't think so, I will just keep an eye on the ac unit until I can either purchase a capacitor or have someone come out to fix it. You have been very helpful

A-1 Tech :

Thank you very much. A good rating is appreciated.

Customer :
A-1 Tech :

Have a great 4th

Customer :

You too!

Customer :

Expert TypeService Manager
Category: HVAC
Pos. Feedback: 98.8 %
Accepts: 381
Answered: 7/4/2012

Experience: I have been in the HVAC business for over 35 years.

Ask this Expert a Question >
Customer replied320 days and 23 hours ago.

Ron - Thank you again for all your help yesterday. It was in fact the capacitor. It has been replaced and everything is working properly again!

Picture
Expert:  A-1 Tech replied320 days and 23 hours ago.

Great, I'm happy to see you are cooling again. You were great to work with, without your eyes and hands, we couldn't have located the problem. I am also happy that you let me know.

Thanks,

Ron

Note: No need to reply unless follow up is needed.

 
Tweet

8 HVAC Technicians are Online Right Now

Ask Your Question Now
Hvac Questions Date Submitted
Hello, I have an existing Copeland Compressor for my HVAC system, 5/16/2013
Is it normal for the Home HVAC Evaporator coils to have ice 5/16/2013
I am a service tech with 49 yrs. experience in all genre of 5/15/2013
Good quote for 4 Ton 13 SEER Kelvinator install ? > My 5/15/2013
I recently had a HVAC residential attic system replaced. They 5/15/2013
I installed a honeywell thermostat a few months ago and it 5/14/2013
We have a commercial office that we have remodeled and are 5/14/2013
I have a Totaline P/N 0441 thermostat, but the screen is blank 5/14/2013
how to connect inline duct blowers to my Amana AMVC95 model 5/13/2013
I have a Honeywell manual thermostat wire connections are (yellow, 5/13/2013
RSS
Next 10 >
Ask A HVAC Technician
Type Your HVAC Question Here...
characters left:

Top HVAC Experts

See More HVAC Technicians

JustAnswer in the News

Nbc
Washington Post
New York Times
Cnn
Learn More

How It Works

  • Ask an Expert
  • Get a Professional Answer
  • Ask Followup Questions
  • 100% Satisfaction Guarantee
Learn More
 
 
 

Recent Articles in HVAC

  • Electric Boiler Problems
  • Radiant Heating Problems
  • Questions on Furnace Problems
  • Air Conditioner Questions
  • Questions about Expansion Tank Problems
  • Questions about Thermocouple Problems
  • Questions about Radiator Problems
  • Air Filter Problems
  • Dehumidifier Problems
All HVAC Articles
 
 
 
close
Find Expert answers related to your question.
Sign up using email
We will never post anything without your permission.
Already have an account? Sign in

Ask a HVAC Technician

Get a Professional Answer. 100% Satisfaction Guaranteed.
221 HVAC Technicians are Online Now
Type Your HVAC Question Here...
characters left:
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.