Our air conditioner as well as heater will not come on. I have

 
Tim H's Avatar
  • Answered by:Tim H
  • HVAC professional
  • Positive Feedback: 97.6 %
  • Accepted Answers: 2328
Verified Expert
in HVAC

Recent Feedback

Positive
Great communication and very detailed! Great service, thank you.
Positive
thanks
Positive
Very patient and helpful, I'm very grateful!
Positive
thanks tim . i will try it.
Positive
Yes, the problem was indeed the run capacitor.
Positive
Great help
Positive
Quick response, very helpful
Positive
thanks ...i would have not thought that it was a honeywell part...
Positive
Thank you. Very nice.

Customer Question

Our Air Conditioner as well as heater will not come on. I have checked the disconnect outside, the breakers and still nothing. I had someone helping me earlier but he opted out. Can anyone else help?

 

Optional Information:
Brand: Lennox
Type of HVAC: Air Conditioner

Submitted: 353 days and 3 hours ago.
Category: HVAC
Value: $30
Status: CLOSED
Picture
Expert:  Tim H replied 353 days and 3 hours ago.

Thanks for giving me the opportunity to help! I'm sorry to hear you are having issues. Can you tell me this? What happens when you put your thermostat in the fan "on" position? Does the inside blower come on? This will help us first determine if we have 24 volt control power and also whether or not the thermostat is working. If the blower does come on, but not the outside unit, next check to see if the contactor is pulled in on the outside unit. You will need to remove a cover on the side of the unit right about where all the wiring comes in.Tim H41023.8058122685

Customer replied 353 days and 3 hours ago.

No the fan does not come on. I took the thermostat off and tried jumping the green and red wires (as per the instructions from the last tech) and nothing then as well.

Picture
Expert:  Tim H replied 353 days and 3 hours ago.

Next you need to check in the air handler or Furnace (working without any model numbers here) for a small 3 amp fuse that may be blown. It will look similar to this and be in by or on the main control board.Tim H41023.8152162037

Customer replied 353 days and 2 hours ago.

Lennox model #g4ouh-36a-070-07

Here is a link to a pic of the unit in the attic. Where would the fuse be? Is it in the cover to the right?

Picture
Expert:  Tim H replied 353 days and 2 hours ago.

No, it is in the bottom door of the furnace on the circuit board. Or if furnace lays on it's side, the next door over.Tim H41023.8389773495

Accepted Answer

Picture
Expert:  Tim H replied 353 days and 2 hours ago.

If this is blown, try replacing it (you can pick some up at any automotive store) and see if it starts. If not, or if it blows again, then we need to check for other issues.

Expert TypeHVAC professional
Category: HVAC
Pos. Feedback: 97.6 %
Accepts: 2328
Answered: 4/24/2012

Experience: More than 20 years experience.

Ask this Expert a Question >
Customer replied 353 days and 1 hours ago.

Ok, I visually inspected the fuse, as well as tested the fuse for continuity with my voltmeter, it tested good.

Customer replied 353 days and 1 hours ago.

Accidentally accepted, what do I do?

Picture
Expert:  Tim H replied 353 days and 1 hours ago.

It's no problem. We will continue to work on it. Do you have access to a voltmeter? If so, put the setting on volts AC and open the door where you found the fuse. Push in the blower door switch located near the top of the door. Test across R to C (or common) terminals on the board. We're looking for 24 volts here. If 24 volts, next set the thermostat to cooling and check across C (or common) to the Y terminal. Again we should see 24 volts. Let me know what you find.

Customer replied 353 days and 1 hours ago.

ok the lowest a/c volts setting on my ohm meter is 200 (not sure if this matters) but when I pushed in the door switch and went across the r to c terminals I only got 1 volt. I didn't bother to do the second test since we didn't get 24 volts.

Picture
Expert:  Tim H replied 353 days ago.

Locate two terminals on the board that are marked XFMR-H and XFMR-N. Push the blower door switch in, and check across these. We're looking for 24 volts. If no voltage, check across Line-H and Line-N. Across these two we should have 120 volts. Let me know what you find on all these readings. Make SURE that the voltmeter is set to volts AC, not DC.

Customer replied 353 days ago.

Ok, I'm going to upload a few pics of the circuit board. I couldn't find the transformer terminals, however I did find the line h and n (hot and neutral?) and there is 120 volts there. sorry it takes me so long, it is in the back of my attic, and I have to crawl to it, and then it's on its side.

http://imgur.com/a/In9bO

Picture
Expert:  Tim H replied 353 days ago.

You can use any of the whites on the board as a neutral. The XFMR-H should be right below the Line-H terminal. If you test across any of the neutrals to XFMR-H and get no voltage, the transformer is bad and will need replacement. This is unusual for the transformer to go out without blowing the 3 amp fuse first, but guess it can happen.

Customer replied 353 days ago.

Could it be called something other than xmfr-h? also, where is the transformer located?

Picture
Expert:  Tim H replied 353 days ago.

There were 2 different boards used on that furnace. It could just be called XFMR. You will most likely see a black lead on it. The transformer is down near the circuit board.Tim H41023.9347541667

Customer replied 352 days and 23 hours ago.

I found the transformer, and the leads/terminals xmfr-h,n. I tested several times and kept getting 120 volts, instead of 24 or 0???

Picture
Expert:  Tim H replied 352 days and 22 hours ago.

I apologize, I misspoke. You SHOULD have 120 volts across XFMR-H to XFMR-N. The 24 volts should be across C (common) to R on the board and I think you said previously you had no voltage there. So if the 3 amp fuse is OK, then with no voltage across C-R, the transformer would be burned out. Sorry, it's been a long day!

Customer replied 352 days and 6 hours ago.

Is there a chance it could be the board? I took the transformer off, and took it to johnstone supply this morning.( I didn't see your answer until now) Anyhow, it didn't really make sense abou there being 120 volts, so I asked if they could test it for me, and it tested good. There is no action from either of the green led's on the board. They don't light up at all.

Picture
Expert:  Tim H replied 352 days and 6 hours ago.

Yes, it's possible. Why wouldn't it make sense that there would be 120 volts at the board. A transformer has a primary (higher voltage) and a secondary side (lower voltage). Since you tested across XFMR-H and XFMR-N and got 120 volts, but nothing at C-R, it would make sense that the transformer could be bad. But if they're saying that it's good, you either have a bad connection somewhere, the 3 amp fuse is blown, or the board could be bad. Check across the Secondary side of the transformer with the transformer in place on the unit and see if you get 24 volts. If you do, and the fuse is good, replace the board.Tim H41024.6887499653

Customer replied 352 days and 5 hours ago.

I'm sorry for the misunderstanding. What I meant was when you told me that I should have 24 volts at (what appeared to me to be) the incoming power to the transformer. Please don't misunderstand me, you are way more qualified than me and I really appreciate your advice. I just questioned that one thing, and I saw from your reply now why because it WAS supposed to be 120 volts.

I am taking my daughter to school in an hour, after that I will go back to the attic and start working on it. I'll stay in touch and let you know what I figure out. Thank you again.

Picture
Expert:  Tim H replied 352 days and 5 hours ago.

Yes, I apologize for that, that was my mistake. Across XFMR-H to XFMR-N you should have 120 volts as this is the primary side of the transformer. Typically you'd measure the secondary side across C terminal to R terminal. However, you could also go directly to your transformer secondary side and measure the same 24 volts. And I'd say if you do that and come up with 24 volts, and you're positive the fuse is not blown, then the board is most likely bad. Especially with no LED's lit up.

Another thing you could do is turn the power off and try to tip the board and look at the back. Usually when a board is bad, there will be a burned area or some discoloration or signs of overheating.
Tim H41024.7199219097

Customer replied 352 days and 1 hours ago.

Alright!!! Took the circuit board off, there was a tiny burnt spot on the back. Took it off and went and picked up a new one from johnstone supply and I'm back in business!!! Thank you very much for your help.

Accepted Answer

Picture
Expert:  Tim H replied 352 days and 1 hours ago.

Great!!! Glad we got through this one....

Expert TypeHVAC professional
Category: HVAC
Pos. Feedback: 97.6 %
Accepts: 2328
Answered: 4/25/2012

Experience: More than 20 years experience.

Ask this Expert a Question >
 
Tweet

3 HVAC Technicians are Online Right Now

Ask Your Question Now
Hvac Questions Date Submitted
I have a GH19P4/5-125 Lennox furnace. My HVAC man removed 3/27/2013
Hi there, I have had a few problems with my furnace, but the 3/27/2013
Whats the rule of thumb for cost estimating a new construction 3/27/2013
Please comment on this: None of the contractors have mentioned 3/26/2013
Our school has a Weil-McLain Ultra Gas Series 3 with an outdoor 3/26/2013
I have a ge Az61ho9dabw1 heat pump and I'm trying to interphase 3/25/2013
Do you have a contract that would fairly and abundantly represent 3/25/2013
I have a Carrier electric HVAC model fk4cnb006 with variable-speed 3/23/2013
My GDH809004BXAB gas furnace stopped working 3/23/2013
RA-RP 3/23/2013
RSS
Next 10 >
Ask A HVAC Technician
Type Your HVAC Question Here...
characters left:

Top HVAC Experts

See More HVAC Technicians

In The News

Nbc
Washington Post
New York Times
Cnn
Learn More

How It Works

  • Ask an Expert
  • Get a Professional Answer
  • Ask Followup Questions
  • 100% Satisfaction Guarantee
Learn More
 
 
 

Recent Articles in HVAC

  • Electric Boiler Problems
  • Radiant Heating Problems
  • Questions on Furnace Problems
  • Air Conditioner Questions
  • Questions about Expansion Tank Problems
  • Questions about Thermocouple Problems
  • Questions about Radiator Problems
  • Air Filter Problems
  • Dehumidifier Problems
All HVAC Articles
 
 
 
close
Find Expert answers related to your question.
Sign up using email
We will never post anything without your permission.
Already have an account? Sign in

Ask a HVAC Technician

Get a Professional Answer. 100% Satisfaction Guaranteed.
189 HVAC Technicians are Online Now
Type Your HVAC Question Here...
characters left:
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.
Truste
Contact Us | Terms of Service | Privacy & Security | About Us
© 2003-2013 JustAnswer LLC