I have a Weil McLain CGt-5-PIN boiler with waterless hot water

Resolved Question:

I have a Weil McLain CGt-5-PIN boiler with waterless hot water heater with hot water baseboards. I only get almost luke warm water for showers with an occasional minute of nice warm/hot water. Also water drips out of a verticle tube(about 4 cups a day)
Submitted: 2 years ago.
Category: HVAC
Expert:  Phil replied 2 years ago.

Phil :

All work to be done by licensed professional. WE KEEP GOING UNTIL YOU HAVE THE INFORMATION YOU NEED, I come and go. This is step ONE.

Phil :

Hello

Phil :

Please look at this link, and confirm this is the boiler you have or not. Thanks

Phil :

Tell me if the base board heat works or not.

Phil :

and tell me if you can about how old the boiler is

Phil :

We can go from there until the situation resolves

Phil :

Phil

Customer:

This is the exact boiler. The base board heat works. I just bought the house from an estate sale so information is fleeting, but best I can figure is 4 yrs old

Phil :

Hello again,

Customer:

hello

Phil :

If the vertical tube comes from the boiler it is the pressure relief valve that is leaking, it has a floppy handle hanging from the top of it in most cases

Customer:

yes. this is what is happening.

Phil :

that is the manual release lever... put a bucket under the tube and trip the handle about 20 times, that will bounce the valve seat up and down and re-seat the valve in many cases.. if that fails the valve should be replaced

Customer:

ok. i will go try now

Phil :

Next we need to test the hot water flow rate in order to assess any water scale in the heat exchanger

Phil :

Fill a one gallon jug from the kitchen hot water tap wide open, and again from the cold water tap and tell me how long each took in seconds

Phil :

we can go from there.

Phil :

Phil

Customer:

I check a couple of times and it appears to be 53 seconds for cold water and the same for hot water

Customer:

that was the kitchen sink

Customer:

in the basement sink i got 15 seconds for cold and 48 seconds for hot

Customer:

is anyone ever going to answer back. its been 2 days

Phil :

Hello again. the just answer servers have been down, all day yesterday...and about half of today so far.... hopefully they are fixed now...

Phil :

I will do my best through all this.

Phil :

Did the water quit dripping from the pressure relief valve when you lifted the relief valve handle and then let go of it, so the valve snapped back shut? That will often re-seat the valve and stop the leaking.

Phil :

Thanks for doing the flow rate tests...

Phil :

from those tests it appears the heat exchanger for domestic hot water is OK and not clogged with water scale. (mineral deposits).

Phil :

See page 23 of the manual, tell me if your system has three pumps or just one pump... the diagram on the left shows a pump on the boiler and additional pumps for the radiant heat and another one for the domestic hot water.

Phil :

the diagram on the right shows just one pump, and thats on the boiler. I suspect that is what you have. zone valve #5 controls the flow of boiler water to the domestic hot water heat exchanger... that valve is controlled by a thermostat (not shown in the drawing) the lets the boiler water heat the domestic hot water... that thermostat or its sensor is going bad.

Phil :

Let me know what you find on your end.

Phil :

We can go from there

Phil :

thats the link again in case you need it

Phil :

Phil

Phil, Mechanical Engineer
Category: HVAC
Satisfied Customers: 5589
Experience: Retired HVAC/ Electrical & Boiler contractor. Industrial
Phil and 5 other HVAC Specialists are ready to help you
Expert:  Phil replied 2 years ago.
What Happens Now?

Your chat has ended, but you can still work with your Expert to get an answer to your question if you have not yet received one.

Come back to this page at any time to see additional information from your Expert.  You will also receive an email when your question is updated.  If you want to send a message to your Expert, use the box below.

If you have already received a satisfactory answer to your question, click the Accept button above.  Experts are credited for each accepted answer they provide.
Customer: replied 2 years ago.
I am a newbie to this house stuff so here goes. Their is one thing on my boiler labeled a circulator. Their is three zone valves. Upstairs their is three seperate thermostats
Expert:  Phil replied 2 years ago.
Thanks, XXXXX XXXXX the system piped that way with one pump works is that hot water is pumped around the hot water piping loop, see the diagram on page 23 of the link I posted.

when a room thermostat calls for heat the valve for that radiator or set of radiators opens, and lets hot water into the loop.

and the radiator gets hot... things that will prevent that is air in the radiators, or water pressure below 15 or 20 psig depending on how tall the building is.

all that apparently works.

it is just the domestic hot water heater, heated by the boiler hot water loop that doesn't work properly.. it has a similar valve and thermostat that regulates the hot water feed to the domestic hot water unit... tell me if you can find that.... it is shown on the diagram on page 23 with only one pump on the right.

that valve has wires attached, those go to the thermostat that controls the valve.. that thermostat has a sensing element attached that goes to the domestic hot water tank. it is that sensor that is likely going bad.


Look that over, we can go from there... none of this is effortless by the way, the college course on these skill sets takes 2 years, then to get good at working on these systems takes another 5 or 10 years of practice.

so be patient with yourself, study the manual I sent and page 23 until you figure out which is which on your system

we can go from there'

Phil




Customer: replied 2 years ago.
all i seem to be able to find is something labeled a low limit thermostat on tankless heater
Customer: replied 2 years ago.
all i seem to be able to find is something labeled a low limit thermostat on tankless heater. also a high limit
Expert:  Phil replied 2 years ago.
Good work.

Tell me where the low limit thermostat is set.. and if there is a 'differential' or DIFF setting on it, and where that is set.

Tell me what settings are available the high limit, and where it is set

we can go from there

Phil
Customer: replied 2 years ago.
Low has no diff. set at 190. high set at 210
Expert:  Phil replied 2 years ago.
The 190 to 210F settings, are settings you see on *high temperature safety cut out switches....if that switch is marked low limit then someone has been messing with it. or the covers on the the thermostats have been switched.


the hot water temperature controls are set between 120 and 150F at the highest.

Boiler work takes about 2 years of community college courses as an entry point, and a few years practice in the field as an apprentice.. none of these adjustments can be a fix..they all have to work together and the person adjusting them needs to be able to identify each control device, then adjust accordingly..then use instruments to verify how it all operates.

Tell me what city you are in or nearest and I will see if I can find a Weil McLain dealer in your area

Phil




Customer: replied 2 years ago.
franklin ma
Expert:  Phil replied 2 years ago.
Weil-Mc Lain XXXXX# XXXXX Milford, MA (NNN) NNN-NNNN‎ · weil-mclain.com
"Weil-McLain is a leading designer, manufacturer and marketer of gas- and oil-fired hot water and steam boilers for space heating in residential ..." - weil-mclain.com

you are fortunate, this appears to be the regional dealer.. call them and ask about service, they are about 7 miles away.


Let me kmow how it goes, Phil
Customer: replied 2 years ago.
thanks.

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial