I have a York Gas Furnace model GY9S1000C20DH11G that has a

 
Kenton Guidry's Avatar
  • Answered by:Kenton Guidry
  • HVAC Technician
  • Positive Feedback: 98.8 %
  • Accepted Answers: 962
Verified Expert
in HVAC

Recent Feedback

Positive
Very helpful, courteous and patient.
Positive
Just got fast start kit installed last weekend and it seems to have cured the...
Positive
Thanks so much for your help. I spent 3 hours online trying to find those...
Positive
Knows his stuff.
Positive
Very helpful. Provided me with an answer to my question where no one in this...
Positive
advice was well appreciated
Positive
Very informative session and very nice person: patient, helpful, courteous.
Positive
Kenton was great. He was incredibly patient with me and not only directed me...
Positive
Good feedback!

Customer Question

I have a York Gas Furnace model GY9S1000C20DH11G that has a Fault Code 3. How do you reset the limit switch?

Thanks

 

Optional Information:
Make : York
Model : GY9S100C20DH11G

Already Tried:
At first I had 11 red flashes, so I unplugged the unit and started looking for the limit switch. I decided to plug it back in and it worked for about 10 minutes, now I have 4 red flashes

Submitted: 528 days and 17 hours ago.
Category: HVAC
Value: $23
Status: CLOSED
Picture
Expert:  Kenton Guidry replied528 days and 17 hours ago.

SLOW GREEN FLASH: Normal operation.

SLOW AMBER FLASH: Normal operation with call for heat.

RAPID RED FLASH: Twinning error, incorrect 24V phasing. Check
twinning wiring.

RAPID AMBER FLASH: Flame sense current is below 1.5 microamps.
Check and clean flame sensor. Check for proper gas flow.

4 AMBER FLASHES: The control board is recieving a “Y” signal from
the thermostat without a “G” signal, indicating improper thermostat wiring.

1 RED FLASH: This indicates that flame was sensed when there was
not a call for heat. With this fault code the control will turn on both the
inducer motor and supply air blower. A gas valve that leaks through or
is slow closing would typically cause this fault.

2 RED FLASHES: This indicates that the normally open pressure
switch contacts are stuck in the closed position. The control confirms
these contacts are open at the beginning of each heat cycle. This would
indicate a faulty pressure switch or miswiring.

3 RED FLASHES: This indicates the normally open pressure switch
contact did not close after the inducer was energized. This could be
caused by a number of problems: faulty inducer, blocked vent pipe, broken
pressure switch hose or faulty pressure switch.

4 RED FLASHES: This indicates that a primary or auxiliary limit switch
has opened its normally closed contacts. With this fault code the control
will operate the supply air blower and inducer. This condition may be
caused by: dirty filter, improperly sized duct system, incorrect blower
speed setting, incorrect firing rate or faulty blower motor.

5 RED FLASHES: This fault is indicated if the normally closed contacts
in the rollout switch opens. The rollout control is manually reset. If it has
opened, check for proper combustion air, proper inducer operation, and
primary heat exchanger failure or burner problem. Be sure to reset the
switch after correcting the failure condition.

6 RED FLASHES: This indicates that after the unit was operating, the
pressure switch opened 4 times during the call for heat. If the main
blower is in a “Delay on” mode it will complete it, and any subsequent
delay off period. The furnace will lock out for one hour and then restart.

7 RED FLASHES: This fault code indicates that the flame could not be
established. This no-light condition occurred 3 times (2 retries) during
the call for heat before locking out. Low gas pressure, faulty gas valve,
faulty hot surface ignitor or burner problem may cause this. The furnace
will lock out for one hour and then restart.

8 RED FLASHES: This fault is indicated if the flame is lost 5 times (4
recycles) during the heating cycle. This could be caused by low gas
pressure or faulty gas valve. The furnace will lock out for one hour and
then restart.

9 RED FLASHES: Indicates reversed line voltage polarity or grounding
problem. Both heating and cooling operations will be affected. Check
polarity at furnace and branch. Check furnace grounding. Check that
flame probe is not shorted to chassis.

10 RED FLASHES: Gas valve energized with no call for heat. Check
gas valve and gas valve wiring.

11 RED FLASHES: This indicates that a primary or auxiliary limit switch
has opened its normally-closed contacts and has remained open for
more than five minutes. This condition is usually caused by a failed
blower motor or blower wheel.

12 RED FLASHES: This code indicates an open igniter circuit, which
could be caused by a disconnected or loose wire or by a cracked or broken
igniter.

STEADY ON RED: Control failure. Replace control board.

60-MINUTE AUTOMATIC RESET FROM LOCKOUT: This control
includes a “watchdog” type circuit that will reset from a lockout condition
after 60 minutes. Operational faults 6,7,8 will be reset. This provides
protection to an unoccupied structure if a temporary condition exists
causing a furnace malfunction. An example would be a low incoming
gas supply pressure preventing unit operation. When the gas pressure
is restored, at some point the “watchdog” would restart the unit and provide
heat for the house.

NOTE: If a flame is detected the control flashes the LED for 1/8 of a
second and then enters a flame stabilization period.

Customer replied528 days and 17 hours ago.

I know what 4 red flashes means, what I need to know is how to correct it. How do you close the limit switch?

 

Thanks

Picture
Expert:  Kenton Guidry replied528 days and 17 hours ago.

Your going to have to look for a switch that looks like this. The only way you can reset these switches are if they have a small red button on top. The #4 error also makes a reference to a high limit. If that high limit is open and will not reset by itself you'll have to replace. it.graphic

Picture
Expert:  Kenton Guidry replied528 days and 17 hours ago.

One more thing is to find out why the unit tripped. Is the air filter really dirty? or perhaps you have some supply air registers closed?

Customer replied528 days and 17 hours ago.

I cant seem to find anything like that. Can you look at these pictures and see if you see it? Thanks

 

 

graphicgraphic

Customer replied528 days and 17 hours ago.

The air filter was dirty and has now been replaced. Air supply registers closed? How do I check that?

Thanks again

Accepted Answer

Picture
Expert:  Kenton Guidry replied528 days and 16 hours ago.

That air filter may have done it. These pictures are very helpful.

I see a limit switch on the black induced draft fan that is attached to the pvc. Looks like a brown and orange wire.

The main limit is in the upper right hand corner of the picture with what looks like a white and brown wire.

Then I see another limit on the upper right hand corner of the picture sitting on top of the metal enclosure that the burners are in.

The high limit cannot be manually reset but the other two can.

Look on the bottom of that burner enclosure too (the exact opposite side of the limit i see in the upper right).

Expert TypeHVAC Technician
Category: HVAC
Pos. Feedback: 98.8 %
Accepts: 962
Answered: 1/7/2012

Experience: 12 years install/service experience.

Ask this Expert a Question >
Customer replied528 days and 16 hours ago.

There was no button on the black induced draft fan, however there was on on top of the metal enclosure and one on bottom as well. Pushed both buttons, then turned it back on. It worked for a few minutes but now I am back to 11 red flashes. Is there anything else I can try or should I call in an expert?

Picture
Expert:  Kenton Guidry replied528 days and 12 hours ago.

Do you have a meter? We can measure voltage and determine what switch is causing this.

 
Tweet

4 HVAC Technicians are Online Right Now

Ask Your Question Now
Hvac Questions Date Submitted
I have a Carrier HVAC system. Tech2000 SS. Last night it quit 6/12/2013
My son just moved in today to a house in Georgia where it is 6/11/2013
I've struggled with McQuay Enfinity Water Source Heat Pumps 6/2/2013
Bryant HVAC units, one for downstairs doesn't blow cold air, 5/31/2013
Turn on A/C without memory card? 5/28/2013
My white rogers thermostat type # XXXXX is flashing HVAC 5/20/2013
I have a Trane HVAC 5/19/2013
Hello, I have an existing Copeland Compressor for my HVAC system, 5/16/2013
I am a service tech with 49 yrs. experience in all genre of 5/15/2013
We have a Carrier 376BAW060115 model furnace. We have not used 5/12/2013
RSS
Next 10 >
Ask A HVAC Technician
Type Your HVAC Question Here...
characters left:

Top HVAC Experts

See More HVAC Technicians

In The News

Nbc
Washington Post
New York Times
Cnn
Learn More

How It Works

  • Ask an Expert
  • Get a Professional Answer
  • Ask Followup Questions
  • 100% Satisfaction Guarantee
Learn More
 
 
 

Recent Articles in HVAC

  • Electric Boiler Problems
  • Radiant Heating Problems
  • Questions on Furnace Problems
  • Air Conditioner Questions
  • Questions about Expansion Tank Problems
  • Questions about Thermocouple Problems
  • Questions about Radiator Problems
  • Air Filter Problems
  • Dehumidifier Problems
All HVAC Articles
 
 
 

Ask a HVAC Technician

Get a Professional Answer. 100% Satisfaction Guaranteed.
142 HVAC Technicians are Online Now
Type Your HVAC Question Here...
characters left:
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.
Truste
Contact Us | Terms of Service | Privacy & Security | About Us | Our Network
© 2003-2013 JustAnswer LLC
  • Pearl.com
  • JustAnswer UK
  • JustAnswer Germany
  • JustAnswer Spanish
  • JustAnswer Japan