My goodman heating unit trips the breaker outside at the panel.

Resolved Question:

My goodman heating unit trips the breaker outside at the panel. I have had the breakker replaced. it is a 60 amp breaker. it does not trip the one one the unit. this model is ARUF036-00A-1. The ser. is XXXXXXXXXX What can cause this. it only trips it after the heating temp. has been on for a few cycle. I had the amps checked at the unit and it was 18.5. the unit is rated at 18.8. this has been and on going problem.
Submitted: 2 years ago.
Category: HVAC
Expert:  Airheatman replied 2 years ago.

airheatman :

I will try to assist you

airheatman :

Is your breaker tripping that feeds the indoor unit or the outdoor unit?

airheatman :

The ARUF is the indoor unit.Do you have a heat pump or straight electric heat? Is the breaker that is tripping suppling power to the indoor unit, the outdoor unit or both?

Customer:

It supplies the indoor unit. It is a straight electric heat.

airheatman :

Ok

airheatman :

How many KW of heat do you have

airheatman :

There should be a label on the front of the ARIF air handler that states how many heat strips are installed

Customer:

I dont recall the kw amount, but each set of elements are reated at 18.8 amps and the max operating amp is 20/20. can you determine the kw with the model? The unit also has a part no. on it. #14310-04

airheatman :

When the unit comes from the factory, it does not have any heat strips.The installer installs either 5KW,10KW or 15KW heat kit.The original label from factory showing amp draw does not include heat strips.

Customer:

There are three

airheatman :

The model number you listed shows no heat (thus the 36-00).

airheatman :

If you have three elements, you have 15 KW heat

airheatman :

This is why breaker is tripping

Customer:

yes you are correct

airheatman :

Technically a 5 kw strip can draw as much as 22 amps

airheatman :

So 3 five kw strips will draw as much as 66 amps plus whatever the blower drwas

Customer:

There is a 60 amp breaker in the inside unit, but it does not trip.

airheatman :

Can you tell me where the third strip gets its power ? Normally if you have 15 KW you will have both a 60 amp breaker feeding 2 stips as well as a 30 amp breaker feeding the third element,Do you not have the second breaker at the air handler?

Customer:

If the unit is drawing too many amps. shouldnt the inside break trip also? because it feeds from the supply box.

airheatman :

Do you not have 2 breakers on the air handler

Customer:

Yes, there is a 30 amp, and a 60 amp

Expert:  Airheatman replied 2 years ago.

Do you have two different power sources feeding the two breakers or just the one that is coming from the 60 amp in main panel?

Expert:  Airheatman replied 2 years ago.
If both the 60 amp breaker and the 30 amp breaker are fed from one 60 in the main panel, the one in main panel will trip when that third element which is fed by the 30 amp breaker comes on
Customer: replied 2 years ago.
Relist: Incomplete answer.
the chat ended before i could receive an answer
Expert:  Airheatman replied 2 years ago.
Sorry our chat locked. If your furnace is being fed by one 60 amp breaker,When the third element comes on, it is drawing more than 60 amps.In the unit, everything is protected because only 2 elements are on the 60, But when the other element comes on, it is drawing on the same breaker in main panel.You will need a seperate 30 amp breaker in main panel supplying voltage to the 30 amp in air handler or a larger wire and breaker to feed both the 30 and 60.
Expert:  Airheatman replied 2 years ago.
Does this make sense to you? You have a 60 amp circuit from your main breaker panel feeding a 60 amp breaker in the air handler,This is fine and will not cause any problems.However, when you connect the third heat strip ,on the additional 30 amp breaker with the 60 amp circuit, you are overloading the circuit and therefore tripping the breaker. To prevent the circuit from overloading, you will need to add a seperate 30 amp circuit to the air handler to feed the 30 amp breaker and third element. Or you would need to replace the 60 amp breaker to a 90 amp breaker and replace the 60 amp wire with 90 amp wire.
Expert:  Airheatman replied 2 years ago.
Are you still with me? Let me know if you have a seperate 30 amp breaker in the main panel that supplies power to the 30 amp breaker in the air handler.If not, you can turn the 30 amp breaker off and just use 10 kw heat until you can have wiring corrected.
Customer: replied 2 years ago.

sorry I had to leave you. I am at home now. My unit has both a 60 and 30 amp breaker in the air handler as well as a 60 and 30 amp breaker in the main panel. The 60 amp out side is the one that trips.

 

Expert:  Airheatman replied 2 years ago.

Ok, so you do already have two seperate breakers feeding the air handler.That is good. Next lets look at the 60 amp that is tripping.What size wire do they have ran between the main panel and air handler?It should be at least #6 copper .We can go from there

Customer: replied 2 years ago.
it is awg #6, and awg # XXXXX at the 30 amp
Expert:  Airheatman replied 2 years ago.
Are there any connections or junction boxes between the breaker and air handler that might have a loose wire connection?
Customer: replied 2 years ago.

None.

 

Expert:  Airheatman replied 2 years ago.

Do you have an amp meter to verify that all elements work? I would say you could have an element in the air handler that could be shorting to trip the breaker.I do not believe that two elements are drawing enough amps to trip it.But I am like you, I would think the breaker on front of air handler would trip. It really sounds like your breaker itself is getting hot.Have you looked at the buss bars where the breaker plugs into the main panel to verify the breaker bus bar is making a good connection?

Customer: replied 2 years ago.
YES, I JUST REPLACED THE 60 AMP. IT IS A FPE TYPE. IT IS SNAPPED INTO THE BUS TIGHT. I DO SEE SOME OVERHEATED ENDS ON TWO OF THE ELEMENT WIRES THAT IS CONNECTED TO THE SEQUENCER. I PUT MY METER ON THEM THEY ARE DRAWING AND AVG OF 17 AMPS. ON THE TWO STRIPS. THE THIRD IS NOT ON.
Expert:  Airheatman replied 2 years ago.

This definitely sounds like a loose connection overheating rather than over amps.I just cannot tell you why the one in the air handler doesn't trip.The only thing I can think is that the big breakers in the Goodman unit are not true rated breakers, but rather disconnects

Customer: replied 2 years ago.

I WILL REPLACE THE CONNECTORS ON THE WIRES AND CONTACT YOU AGAIN IF IT CONTINUES. BUT THANKS, XXXXX XXXXX ACCEPTED YOU HELP

 

 

Expert:  Airheatman replied 2 years ago.
Thanks for letting me work with you.Feel free to follow up and I would like to know what you find
Airheatman, HVAC Technician
Category: HVAC
Satisfied Customers: 4838
Experience: Furnace, A/C and heat pump specialist.
Airheatman and 4 other HVAC Specialists are ready to help you

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial
 
 
 
Chat Now With A HVAC Technician
Airheatman
Airheatman
Heating & Air Conditioning Contractor
2950 Satisfied Customers
Furnace, A/C and heat pump specialist.