Hi,I have a Payne furnace. I was receiving the Code 33

Customer Question

Hi, I have a Payne furnace. I was receiving the Code 33 "limit switch" error code and I had a HVAC guy troubleshoot. He added a second return vent directly adjacent to the furnace into the house. However, this still triggers the same code. A Payne technician was called and he suggested that my tech take readings on both supply and return. He did the readings and told me that the readings were in normal parameters. When I remove the filters off of both returns, I do not get a code however, I see the furnace cycle without throwing any code. The LED is solid during this cycling. It seems that it doesn't reach the target temperature and shuts the fan down and then cycles and then restarts and continues heating. This occurs every five/ten minutes until the target temperature is achieved and then it shuts down completely until the next interval. I do notice that when the target temperature is reached, my thermostat's relay does click. At that point, the furnace does go through it's normal shutdown sequence. I had a different HVAC technician come to troubleshoot further and he wasn't of any help. He removed the filters and fired it up and since there was no code, he blamed the filters, charged me $50 and left. Some help he was. This is frustrating... Can you please help? Thank you, James  Model Number is XXXXX
Submitted: 2 years ago.
Category: HVAC
Expert:  mranswer replied 2 years ago.
This is some sort of air flow issue from what you describe here. Has this been going on since this was installed? Is the blower wheel clean? Is there an a/c coil present in this system and if so has it been inspected to make sure it is clean too?
Customer: replied 2 years ago.
I don't know. It's been ongoing since I bought the house almost three years ago. How do I check the blower wheel and the A/C coil. The A/C side is Bryant brand and sits below the Payne furnance. Did you see my attached image of the model number?
Expert:  mranswer replied 2 years ago.
Only a visual inspection of these parts will tell, so if you are so able then go ahead. Any dirt on the blower wheel drastically cuts its ability to move the air and a dirty evaporator coil acts just like a dirty filter.
Customer: replied 2 years ago.
That is not what I asked? I asked, how do I access the blower and ac
Coil?
Expert:  mranswer replied 2 years ago.
The blower is in the furnace- it is not hidden, just take off the access panel. Use a flashlight and mirror to see the wheel. To see any dirt on the coil means you must look at it from the point where the air ENTERS the coil as dirt will only be on the INLET side just like a filter. I do not know the exact physical set-up of what you have, but I am sure that you can figure out how to look at it- panels may need to be removed, etc. but the coil is not in a secret location either. Air flows into the furnace only 1 way, so there should be no confusion here as to which way the air flows thru the coil.
Customer: replied 2 years ago.
Okay. I'll check and report back. Do the side panels come off for this model?
Expert:  mranswer replied 2 years ago.
No, only the front comes off on this.
Customer: replied 2 years ago.
Hi,

I've attached two more images... I can barely get to the blower. I used a mirror and can't really see good enough to notice any dirt.

I don't know where the coil is. Here's my only access in these two images.

Thanks,
James

graphicgraphic
Customer: replied 2 years ago.
Relist: Incomplete answer.
Would like to know more information on accessing the parts described in my ticket.
Expert:  Billy replied 2 years ago.

 

Hello,

 

do you see the box that the furnace sits on?

 

That is the ac coil.

 

Could you attach picture of that please.

 

Billy

Customer: replied 2 years ago.
Hi Billy,

Here's an image of the whole stack. The Bryant is at the bottom.
graphicgraphic
Expert:  Billy replied 2 years ago.

 

Thank you,

 

the last picture of the big silver box with BRYANT on it.

 

The right side panel comes off by removing 5/16s screws. This will let us see the ac coil surface.

 

Also, this circuit had many issues with turning off the blower and causing the issue you describe. It is a HK42FZ circuit board. It was known for turning th blower off for no reason resulting in the 33 code.

 

I do not know if this is your issue...but this was a issue with this circuit board.

 

Remove the panel and take pic of inside and I can tell right away if it is a factor.

 

Billy

Customer: replied 2 years ago.
Hi Billy,

I got the cover off of the Bryant. Here's the photos. It doesn't look dusty/dirty. What's next?

Thanks,
Jamesgraphicgraphicgraphicgraphic
Expert:  Billy replied 2 years ago.

That is what I thought.

 

Can you tell me if any tech has taken a "temperature rise"

 

 

Customer: replied 2 years ago.
Not sure what you mean?
Expert:  Billy replied 2 years ago.

Your unit is rated for a temp rise of 30-60 defgrees. It means it is designed to suck in air and heat it 30-60 degrees.

 

You deduce this by measuring temp of air at return register...and air at first supply register, and then figure the difference.

 

70 return air and 100 register is 30....

 

I would like to know your temp rise.

Customer: replied 2 years ago.
Can I use a regular temperature gauge? That is all I have with me? This is from Radio Shack that has a probe to monitor the outside temperature? If I can use this, how long should I run the HVAC at each location to get the reading?
Expert:  Billy replied 2 years ago.

 

I would like the temps after a 5 minute run time.

 

I thank you for the extra help.

 

Billy

Customer: replied 2 years ago.
Hi Billy,

At return 73 degrees.
At register 95 degrees.

NOTE: The HVAC only stays on for about 3-4 minutes and cycles so not able to read for five minutes.

Also, the limit switch was the replaced two years ago when I first had the tech come out. I thought there was a second sensor that he had replaced as well. The main board you speak of was NOT replaced.



Thanks,
James
Expert:  Billy replied 2 years ago.

You are at the very bottom of the temp rise range. It is my opinion it is not due to blockages , dirty blower, coils or duct work...

 

If any of those were the case your temp rise would be 60 degrees or higher.

 

It is my bet that you have one of the affected boards that turn the blower off randomly while burner is on resulting in overheat at that given time.

 

I realize this is new development..but I personally changed around 300 of these boards.

 

Billy

Customer: replied 2 years ago.
Now this... I have a home warranty and would like to have the board replaced under this warranty. The last guy that came out under my home warranty was "full of it..." if you get my meaning...

How much does the board cost? And are you able to send someone out to change it? Or is this something I can do on my own?

Thanks,
James
Expert:  Billy replied 2 years ago.

The replacement board is a wire for wire changeout.

 

I see you are savvy with pics so the best thing is to take pics and jot notes, but you will find it to be a straight changeout.

 

Plus, in the event you need help, just return here.

 

Billy

Customer: replied 2 years ago.
Okay, where should I get this board from? HK42FZ
Expert:  Billy replied 2 years ago.

They are available quite a few places..

 

Here is an example - http://shortyshvac.com/index.php?main_page=product_info&products_id=39

 

you will see HK42FZ004 all the way to HK42FZ016 because they kept reworking the board .

 

Billy

Customer: replied 2 years ago.
Hi Billy,

I'm not clear. So since there are so many different versions, which version/model do I need to pick up? Can you be precise? I don't want to order the wrong product and be SOL. I've already invested over $1000.00 and got no where. I have no problems accepting your answer. I just need to be certain.

Here's my circuit board.

Thanks again,
James
graphic

Thanks,
James
Expert:  Billy replied 2 years ago.

I am sure. Plus at the top edge of your board is the HK42FZ009 which was 2 reworks agao.

 

If you look at the link I supplied you will see the 009 is covered, and then you can verify the 009 at the top of the circuit board you have,

 

Billy

Customer: replied 2 years ago.
Hi Billy,

I will go ahead and get the one from your link. I really hope this answers my issues with my HVAC. I've been really frustrated not having a solution for almost three years.

Thanks!
James
Expert:  Billy replied 2 years ago.

You are welcome...here is my deduction:

 

33 is overheat code.

The temp rise which is normally operating desig temp is 30-60.

You running temp is 30- which means you are certainly not overheating.

This eliminates dirty blowers, gas pressure, duct, dirty ac etc..

If any of those were a factor the temp rise would be 60+.

 

This leaves us with 2 options....

 

1- a weak limit switch. It trips at lower temps than it is supposed to.

2 A bad circuit board. Turns blower off at random.

 

I apologize I did not mention a weak limit. The problem with this unit is I changed so many boards I aometimes neglect the other potential answers.

 

It may be cost effective to replace the limit first as a move toward a solution.

 

 

Billy, HVAC Technician
Category: HVAC
Satisfied Customers: 19633
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Billy and 3 other HVAC Specialists are ready to help you
Customer: replied 2 years ago.
Hi Billy,

This site needs updating. It's been popping errors and becomes inaccessible. I tried to press the accept button earlier and it froze the page.

I did replace the limit switch as the first step 2.4 years ago.

Thanks,
James
Expert:  Billy replied 2 years ago.

 

Sorry for site issues James, I was locked out from replying.

 

I thank you and will be available for no charge follow up on this question whenever you need.

 

Billy

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial