How JustAnswer Works:

  • Ask an Expert
    Experts are full of valuable knowledge and are ready to help with any question. Credentials confirmed by a Fortune 500 verification firm.
  • Get a Professional Answer
    Via email, text message, or notification as you wait on our site.
    Ask follow up questions if you need to.
  • 100% Satisfaction Guarantee
    Rate the answer you receive.

Ask Billy Your Own Question

Billy
Billy, HVAC Technician
Category: HVAC
Satisfied Customers: 19669
Experience:  Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Type Your HVAC Question Here...
Billy is online now
A new question is answered every 9 seconds

I am replacing a 3 wire ge condenser fan motor with a A O

Customer Question

I am replacing a 3 wire ge condenser fan motor with a A O Smith replacement motor. The A O Smith motor came with a new capacitor. The ge had a brown wire that went to the old capacitor. A black wire that went to the terminal box. And a yellow wire that went to a larger capacitor (I think) for the compressor. There was also a jumper black wire that went from the old capacitor to the larger capacitor for the compressor.

The new motor has 5 wires. Green wire-ground that I screwed to the grounding plate/screw. A white wire, a black wire, and two brown wires. One of the brown wires has a white stripe. The two brown wires go to the new capacitor on either terminal. I think the old black jumper wire goes to the same terminal on the new capacitor that the solid brown wire is on. I am not sure. I didn't connect the black jumper wire to the new capacitor.

I think the new motor black wire goes where the old motor black wire went. The new motor white wire goes where the old motor yellow wire goes. But not sure on this either.

Help!
Submitted: 2 years ago.
Category: HVAC
Expert:  Billy replied 2 years ago.

Hello,

 

Are you familiar with the contactor?

 

 

Customer: replied 2 years ago.
Not really. I assume it is the black box with the different wires going to it. It is open and flat on the housing wall.
Expert:  Billy replied 2 years ago.

 

The contactor has the high voltage wires coming in on one end and then when closed sends it out the other side.

 

On the new motor we want black to one side and white beside it on other side...then 2 browns to new capacitor...and no other wires to the fan capacitor...

 

2 wires to the contactor and 2 wires to capacitor.

Customer: replied 2 years ago.
Ok. This old Carrier unit was built in 1983. Looks like there is a large (dual?) capacitor mounted to the wall with black wires on the left, yellow wires on the middle terminal and a large white wire on the right. The old motor wires and the compressor wires are plugged into this. However, the old motor had a brown wire to another smaller two terminal capacitor. Then the black jumper wire went from the small capacitor to the black terminal on the larger (dual?) capacitor. I got the new capacitor with the two brown wires from the new motor. I am not going to use the black jumper wire on the new capacitor. The old motor black wire went to what I think you are calling the contactor. Still not sure what this is. Do I put the new motor white wire where the old motor yellow wire was on the larger capacitor that the compressor is connected to?
Expert:  Billy replied 2 years ago.

No.

 

The old motor black does (did) go to the contactor. You will ee this part has 2 feeds in and 2 feeds out.

 

So black to where it was, white on the pole beside it. Then the 2 browns to the NEW capacitor with no jumper. Leave all the rest of the wires where they were as far as compressor and other capacitors.

Billy, HVAC Technician
Category: HVAC
Satisfied Customers: 19669
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Billy and 6 other HVAC Specialists are ready to help you
Customer: replied 2 years ago.

Great. found the contactor. Sound easy from here on out. Ok. It's getting late and I am out of daylight. Plus the white and black wires on the new motor do not have the clips on them for the poles. Too late to run to Lowes. They are already closed. So, can we finish this transaction tomorrow when I have the unit up and running? I may need to ask you more questions.

 

This repair started with a sheared fan blade. The old original motor is still kicking. But, I couldn't get the orignial fan hub off of the shaft. It was rusted on. So, thus the new motor. New capacitor and 5 bladed fan for more efficiency. Thought this would be a 2 hour job at most. But, not sure on all the wires. Thanks for your help.

Expert:  Billy replied 2 years ago.
respond when ready
Customer: replied 2 years ago.

Good morning,

 

The contactor has a bunch of poles on it. The black wire from the old motor is plugged into the "L" side of the contactor which I assume is the left side. There are other black and blue wires on the "R" side of the contactor. Ok, almost there.Do I plug the white motor wire intot the R or L side. I would think the wire would go opposite the black which is in the L side. Thus, the white goes into the R side. But not sure. There are literally, 13 different posts there on the contactor. R or L for the white wire?

Expert:  Billy replied 2 years ago.

You are correct..opposite of black.

 

white r and black l

 

 

Customer: replied 2 years ago.
Ok fan works. rotation is in the correct directions. However, the fan turns on once I turn the breaker on (after putting the outside breaker in the power box outside and going to the garage to turn on the breaker switch in the breaker box). When I turn on the fan from the thermostat controls in the house, the compressor turns on, but the fan turns off. Same for the reverse. Compressor goes off and the fan turns on. ?????? Can I swith the wires or is there something else going on?
Expert:  Billy replied 2 years ago.

sounds like the white and black are on the wrong end of the contactor.

 

 

Customer: replied 2 years ago.

The black wire is in the same place it was when the old motor was in. I just switched the black and white wires. Had the same result. The fan is still going on but off when the compressor kicks on. Back on when the compressor is turned off.

 

I am going to try and send you a photo of the contactor. The motor black wire will be on the bottom (L). The motor white wire will be on the top (R). The white is wire nutted to a yellow wire I stole off of the old motor. It had a clip on it. Shouldn't make a difference. But I thought I would tell you if you notice the white wire is actually yellow. I headed outside to take a photo now. Back in a few. . .

Expert:  Billy replied 2 years ago.

The picture would be great....

 

 

Customer: replied 2 years ago.
graphicgraphic
Expert:  Billy replied 2 years ago.

Ok I see the issue. This is a one pole contactor instead 2 pole contactor. This makes one line always hot.

 

 

Do you see where the main 2 power wires come into the ac unit? and only one goes to the contactor?

 

 

Customer: replied 2 years ago.

yes.

Expert:  Billy replied 2 years ago.

 

That is where the white goes.

 

This is an older style using a one pole switch instead of 2....this means one hot comes in direct without going to the contactor (switch).

 

Leave black where it is and attach white to the other main coming in.

 

 

Customer: replied 2 years ago.
the other main wire is attached to a yellow wire headed to the old dual capacitor that is connected with condensor. So, bundle my motor white wire with the yellow and black wires with a wire nut? MAkes since that the condensor wire (yellow) and my motor wire (white) would get power at the same time.
Expert:  Billy replied 2 years ago.

Correct. Wire nut white to the bundle.

 

Now you have 2 hots coming in....the black goes to the contactor and the other feeds the compressor, capacitor and motor direct from bundle.

let me know if this does it.

 

 

Customer: replied 2 years ago.

Eureka! Works like it should. Cold air is coming out the vents.

 

Thanks for all your help. All my paper instructions referred to a two post system. Thus the confusion. Thanks for hanging with me on this one. Definately worth the money.

 

Blessings

 

Like the lab puppy in the profile pic.

 

Check mine out at pioneerenglishshepherds.com

 

Expert:  Billy replied 2 years ago.

I am very glad you had the patience to see this out. I was not picturing a 0ne pole contactor. Sorry for dragging it out.

 

Well done!

 

Billy

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial