I have a Rheem electric forced air heating system in my home.

Customer Question

I have a Rheem electric forced air heating system in my home. Today althopugh the thermostat is set at 62,it won't turn off. It just runs and runs and the house is much warmer than it shouldm be - clise to 80. First I shut off the main breaker for the whole hearter. I took off the panels and found 4 separate breakers. I turned on the main one at the Electric panel for the house and turned off the breakers inside the Rheem unit one by one until the motor for the blower turned off. I gave it a rest and every time I turn that breaker on the blower motor starts up even though the thermostat has been turned down to 50.
Submitted: 3 years ago.
Category: HVAC
Expert:  Billy replied 3 years ago.

 

Hello,

 

the sequencer (relay) has gotten stuck in the closed position.

 

This is not a repairable item and must be replaced.

 

Part -

 

Rheem Ruud Weatherking Factory OEM Protech Parts 42-23116-08 ...

Billy, HVAC Technician
Category: HVAC
Satisfied Customers: 19712
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Billy and 6 other HVAC Specialists are ready to help you
Customer: replied 3 years ago.
Billy, Where can I get a sequencer (relay) for my Rheem electric forced air house heater?
Expert:  Billy replied 3 years ago.

They are very common...but I would need the model number to be specific.

 

Either number from air handler or the part itself.

 

If you can get one or the other I can assist you further.

 

Billy

Customer: replied 3 years ago.

Billy, the model number of the Rheem furnace is

REAB 2040TXX

I couldn't find a part that looked like that one.

 

The only thing similar to that was part number 42-19423-02 fan relay.

Where is the sequencer (relay) located?

Expert:  Billy replied 3 years ago.

Could it be RBEA instead?

 

 

Customer: replied 3 years ago.

Billy,

I checked the label again and it reads:

MODEL NO REAB 2040 TXX

SERIAL NO W FO375 1752 (I can't tell if the "O" is the letter or the number "zero")

TOTAL KW 40/30

HTR. AMPS 160/138.7

etc.

and then more specifications on the label.

Paul King

Expert:  Billy replied 3 years ago.

 

yours is configured a bit different.

 

looks like this

 

Attachments are only available to registered users.

Register Here

Attachments are only available to registered users.

Register Here

Attachments are only available to registered users.

Register Here
View Full Image

Attachments are only available to registered users.

Register Here

Customer: replied 3 years ago.

Billy, thank you for finding the specific item and including a photo in your last reply.

When I clicked on "View Full Image" it came up in a separate window on my screen with an internet address at the top that indicated it was a webpage from Amazon.com.

I assume that Amazon.com carries it. What is the part number in case I can get it from a local furnace repair person or supply house? Is it SL160 ? Also where is this item in the furnace? I can't find any relay or part that looks like this or the other one you sent to me yesterday that is still part of this thread. The web address of the picture may have the part number embedded in it. The address is: http://ecx.images-amazon.com/images/1/41CvvJRwj3L._SL160_.jpg The part of the web address that looks like it might be the part number is the "SL160"

Expert:  Billy replied 3 years ago.

 

Here is the Ruud/Rheem parts manual for your unit. Item 52 is the sequencer and it shows location. The fan relay is just for blower in cooling mode. The sequencer is what we need.

 

http://www.mediafire.com/?co57f4m8s448g1y

 

 

Customer: replied 3 years ago.

BILLY,

I downloaded the Ruud/Rheem parts manual and it was a pdf file. Page two was a nice exploded parts view of the entire unit. I recognized just about all the parts and where they were supposed to go. You had written that Item 52 is the sequencer. I can see what it looks like and where it is supposed to be. ITEM 52 is also shown magnified on the far right and the top of the diagram and and looks like a very small block with spade connections for wires. ITEM #51 ON THE DIAGRAM IS THE FAN RELAY which you said is just for blower in cooling mode. Well that is in the right place and a lot of wires coming from it are going over to the left side of the compartment where the sequencer is supposed to be and the best way I can describe what is over there in the left side on the floor of that compartment are two BIG blocks with a LOT of spade electrical couplings for the many wires that are connected to them and also two more big blocks similar to those are on the vertical wall over in the corner where the sequencer is supposed to be. I found a picture that is generally similar to what these blocks look like even though they may be for some other model but they show you what these much bigger blocks look like. At the following link http://surpluscityliquidators.com/view_product/48166/243 there are three pictures that give you a general view of a larger block like the four blocks I have - 2 blocks on the left side floor and 2 blocks on the left side back wall vertically in the corner. Each of the blocks are about 2" wide and 4" long each taking up all the space in the left hand corner.

The exploded diagram shows ONE much smaller block AND I HAVE FOUR MUCH BIGGER BLOCKS. Perhaps the diagram shows one small sequencer and my unit is supposed to have 4 large sequencers ganged together. (?)

If that is the case, then since you originally said, "the sequencer (relay) has gotten stuck in the closed position. This is not a repairable item and must be replaced," then HOW CAN I DETERMINE WHICH ONE OF THESE FOUR BLOCKS NEEDS TO BE REPLACED - OR IS IT ALL OF THEM?

Expert:  Billy replied 3 years ago.

 

That part you found at the supplied link is correct.

 

The issue is this....if the fan relay is what was stuck, then just the blower would be running and not the heat.

 

Since it is heat and blower running it is a sequencer. The REAB can various amounts of heat with a number of different heat coils. We do not know which coil of yours is sticking on.

 

On the sequencer (and especially the one in link) there are 2 terminals that say HTR.

 

This HTR is where the the thermostat sends it power through...then by use of heat and warp switches, the power of the 24 v from thermostat starts making each set of contacts close at different delayed times. Blower always kicks on first which one stage of heat (one coil) kicking on seconds later....then another will kick on...this prevents all coils needing start up at once.

 

You now need to find which one is stuck by removing a blower wire one at a time from the sequencers. Turn off power, remove wire and tape..turn back on. If fan starts again, replace wire and move to next one.

 

 

 

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial