I have a nordyne(intertherm) central heat and air unit model

 
gotoman for ac's Avatar
  • Answered by:gotoman for ac
  • HVAC Technician
  • Positive Feedback: 97.9 %
  • Accepted Answers: 4248
Verified Expert
in HVAC

Recent Feedback

Positive
He was right. Coil was dirty
Positive
Fast service and some what good info, confirms that I should go ahead and get...
Positive
Russ was very helpful tracking down the problem so I didn't have to pay a...
Positive
The "gotoman" made a lot of sense, was patient and very helpful!
Positive
I just replaced the fan motor relay and so far it seems to have fixed the...
Positive
walked us through everything that needed to be done that was within our comfort...
Positive
very informative and knowledgable
Positive
First time using and am very pleased. Will try again in future.
Positive
The Gotoman for ac was very patient and informative. Helped us and stayed with...

Customer Question

I have a nordyne(intertherm) central heat and air unit model number E2EH-015HA. My inside unit only works when the fan is on and not in auto. The outside compressor runs constantly. I have to shut on and off the breakers to have ac. I have no heating control. I have replaced the sequencers and thermostat. The unit apparently tried to freeze up last fall; so I shut it down. The outside unit was running when I came home and the inside unit was not. I also replaced the relay on the unit. I am still stuck in a rut. No AC or heat. I am open to suggestions.

 

Optional Information:
Make : nordyne(intertherm)
Model : E2EH-015HA

Already Tried:
Replaced the relay, thermostat (twice, just in case), sequencer.

Submitted: 752 days and 3 hours ago.
Category: HVAC
Value: $30
Status: CLOSED
Picture
Expert:  gotoman for ac replied 752 days and 3 hours ago.

Did you replace compressor contactor. Russ

Customer replied 752 days and 3 hours ago.

No. I didn't think about that. I just concentrated on the inside since it wasn't working.

Picture
Expert:  gotoman for ac replied 752 days and 3 hours ago.

Turn power off to inside unt and if the outside keeps runn ing contactor contacts are welded. Russ

Customer replied 751 days and 4 hours ago.

Okay. I am going to have to replace the contactor. I lightly broke it free. There were a few burnt areas on it. I still have the problem of the inside unit. The only way that I can get it to run is in fan and not auto. I am open to suggestions.

Picture
Expert:  gotoman for ac replied 751 days and 4 hours ago.

When you turn to cool does outside unit come on without fan. Rfuss

Customer replied 751 days and 3 hours ago.

Yes. The outside unit runs without the fan when the switch at the inside unit is in auto.

Picture
Expert:  gotoman for ac replied 751 days and 3 hours ago.

Do you have terminal board on Furnace with W Y R G C. Is the Y to thermostat connected to Y at terminal board. What is model number of thermostat. Russ

Customer replied 751 days and 3 hours ago.

The terminal board behind the thermostat has W Y R G. There is an O/B terminal. Not a C terminal. I have a blue wire that wrapped up with electrical tape with the other wires, but it has never been used since I have owned the house. The thermostat is a Honeywell RTH221B.

Picture
Expert:  gotoman for ac replied 751 days and 3 hours ago.

Just pulled manual on thermostat. Do you have R to Rc jumpered. On back is the heat switch to HE. Russ

Customer replied 751 days and 3 hours ago.

No. I do not have a R to Rc jumpered on this thermostat. There is only a R terminal the heat switch is on HE. The heat doesn't come on either.

Picture
Expert:  gotoman for ac replied 751 days and 2 hours ago.

On the manual I have with thermastat rth221b it shows an RH and RC. They must be jumpered for correct operation. Russ

Customer replied 750 days and 5 hours ago.

I'll look to see what I am over looking in the instructions. Sorry about the delayed answers. I work graveyard shift.

Picture
Expert:  gotoman for ac replied 750 days and 5 hours ago.

No problem I m here for another three hours. Russ

Customer replied 750 days and 5 hours ago.

I tried a different thermostat I purchased prior to the Honeywell. It is a Filtrete 3M-22. I have gotten the samr results. The fan does not come on in auto, only in manual at the iside unit itself and the heat does not work at all.

Picture
Expert:  gotoman for ac replied 750 days and 4 hours ago.

Do you have a wirnig diagram for furnace. Russgotoman for ac40624.970244213

Customer replied 750 days and 4 hours ago.

Yes. I have it saved on my computer. I was just looking at it.

Picture
Expert:  gotoman for ac replied 750 days and 4 hours ago.

Grey common white heat correct, Russ

Customer replied 750 days and 4 hours ago.

Yes.

Picture
Expert:  gotoman for ac replied 750 days and 4 hours ago.

At the furnace if you jumper R to W does heat come on. Russ

Customer replied 750 days and 4 hours ago.

Looking at the diagram and the actual wiring, R goes to the transformer and W goes straight to sequencer. I jumped a wire between the wires but nothing happened.

Picture
Expert:  gotoman for ac replied 750 days and 3 hours ago.

Then the sequencer must be wired wiring or there is an open in the circuit. I know it is a small space. But check across sequencer for 24 volts. Russ

Customer replied 750 days and 3 hours ago.

Okay. It may take me a little bit. I've got to get my meter to check it out. I'll try to give you a reply back this evening.

Picture
Expert:  gotoman for ac replied 750 days and 3 hours ago.

No problem I will be here till 9:00 ct. Russ

Customer replied 750 days and 2 hours ago.

Okay, I checked the circiuts at the sequencer. I found out that I had some of the wires wrong. They are in the correct places now. I do have heat now. The blower comes on with the heat too. I still have a problem with blower not coming on with the AC. I am open to any more suggestions that you may have. I firmly believe that I am close to a resoluton.

Picture
Expert:  gotoman for ac replied 749 days and 17 hours ago.

Good man you are close. JUmper between the two R terminals and set to HE. If you replaced rely check to make sure the G wire is wired to correct terninak at unit, Russ

 
Tweet

5 HVAC Technicians are Online Right Now

Ask Your Question Now
Hvac Questions Date Submitted
I have a GH19P4/5-125 Lennox furnace. My HVAC man removed 3/27/2013
Hi there, I have had a few problems with my furnace, but the 3/27/2013
Whats the rule of thumb for cost estimating a new construction 3/27/2013
Please comment on this: None of the contractors have mentioned 3/26/2013
Our school has a Weil-McLain Ultra Gas Series 3 with an outdoor 3/26/2013
I have a ge Az61ho9dabw1 heat pump and I'm trying to interphase 3/25/2013
Do you have a contract that would fairly and abundantly represent 3/25/2013
I have a Carrier electric HVAC model fk4cnb006 with variable-speed 3/23/2013
My GDH809004BXAB gas furnace stopped working 3/23/2013
RA-RP 3/23/2013
RSS
Next 10 >
Ask A HVAC Technician
Type Your HVAC Question Here...
characters left:

Top HVAC Experts

See More HVAC Technicians

In The News

Nbc
Washington Post
New York Times
Cnn
Learn More

How It Works

  • Ask an Expert
  • Get a Professional Answer
  • Ask Followup Questions
  • 100% Satisfaction Guarantee
Learn More
 
 
 

Recent Articles in HVAC

  • Electric Boiler Problems
  • Radiant Heating Problems
  • Questions on Furnace Problems
  • Air Conditioner Questions
  • Questions about Expansion Tank Problems
  • Questions about Thermocouple Problems
  • Questions about Radiator Problems
  • Air Filter Problems
  • Dehumidifier Problems
All HVAC Articles
 
 
 
close
Find Expert answers related to your question.
Sign up using email
We will never post anything without your permission.
Already have an account? Sign in

Ask a HVAC Technician

Get a Professional Answer. 100% Satisfaction Guaranteed.
153 HVAC Technicians are Online Now
Type Your HVAC Question Here...
characters left:
Disclaimer: Information in questions, answers, and other posts on this site ("Posts") comes from individual users, not JustAnswer; JustAnswer is not responsible for Posts. Posts are for general information, are not intended to substitute for informed professional advice (medical, legal, veterinary, financial, etc.), or to establish a professional-client relationship. The site and services are provided "as is" with no warranty or representations by JustAnswer regarding the qualifications of Experts. To see what credentials have been verified by a third-party service, please click on the "Verified" symbol in some Experts' profiles. JustAnswer is not intended or designed for EMERGENCY questions which should be directed immediately by telephone or in-person to qualified professionals.
Truste
Contact Us | Terms of Service | Privacy & Security | About Us
© 2003-2013 JustAnswer LLC