My Bryant (Carrier) Plus 90 furnace, model 398AAW036080D shuts

Resolved Question:

My Bryant (Carrier) Plus 90 furnace, model 398AAW036080D shuts off after running for a bit. I can reset and it will come back on, but always shuts back off, so I assume it is sensing a problem during safety checks. I checked rubber hoses going to pressure switch for clogging, nothing there really but blew them out anyway since I had that problem before on another furnace after creating alot of dust in my basement where it was located. Same scenario this time with dust and basement, but this furncace draws air from outside for draft inducer (I did visual check and didn't see anything stuck in pipe, but I didnt snake it out or anything), where as the other furncace got air from the basement. Also, water is leaking from under draft inducer motor once blower kicks in to send hot air through ducts, I can't tell where it is coming from but I think the condensate pan is behind the motor. So, perhaps the water is touching something that causes the furnace to shut down? To investigate further I took the bottom door off and pressed in the safety switch with the power on, when I did this I saw an "arcing light" come from the electircal control box, not sure what it was but is was but the source of the arc came from a small plastic box with clear top located in a larger metal box containing a control board and other items. The furncace ran fine after the arc and then shut down after running for about five or ten minutes like every other time with this problem.
Submitted: 3 years ago.
Category: HVAC
Expert:  Billy replied 3 years ago.

 

So once the furnace shuts off...it will not restart on its own?

 

 

Customer: replied 3 years ago.

It will if I turn it off at the unit and at the thermostat, which I assume resets it, wait about ten minutes and turn them both back on. Otherwise, the thermstat will read "Heat on" but nothing will be happening.

Expert:  Billy replied 3 years ago.
Does your spark cable come from a small 2"x3" box or a 3"x5" box labeled lockout timer?
Customer: replied 3 years ago.

I am at work and can't look, but if you can provide a link to a diagram or picture, I might be able to tell. Sorry, I meant to take a picture with phone for referance. The only boxes I can recall are made of sheet metal: a small one about 2x3 to the right of the inducer motor that has the pressure switch attached to it and says it has hot wires and to not service without turning power off and the other is behind the lower panel and is about 3x5 and has the control panel and some relays or something in it. I haven't investigated into the inside of either box yet. I was hoping the lower box would have a troubleshooting mechanism in it. My old york Diamond 90 (in another house) furnace had a blinking red light for such purposes. BTW, I dont know what a spark cable looks like either.

Expert:  Billy replied 3 years ago.

<a href=Carrier Lockout Relay Timer P/N HH72CH003 - Click Image to Close" title=" Carrier Lockout Relay Timer P/N HH72CH003 - Click Image to Close " width="400" height="717"/>

 

the cable runs from the pilot and is orange.

I will leave this open for you for when you are at the unit

Customer: replied 3 years ago.
Ok, thanks, I'll be in front of unit around 6PM EST.
Expert:  Billy replied 3 years ago.

I should be on then...talk to you later.

 

Billy

 

 

Customer: replied 3 years ago.
Orange wire going from burner box to a 2x3 black box labeled spark ignitor (doesn't look like picture). Blue and green wire going from that box to where gas is turned on or off.
Customer: replied 3 years ago.
Btw, turned it on and it ran normal long enough to bring temp up from 62 to 66 then shut off. Thermostat was set at 74.
Expert:  Billy replied 3 years ago.

 

Thank you.

 

do you mind a hands on test?

 

Remove thermostat..take wire from R and wire from W (usually red and white....and twist together...time how long furnace runs before shutting down.

 

 

Customer: replied 3 years ago.
Ok, twisted and running now. Timing in progress, is there a point where I would stop if it doesn't?
Expert:  Billy replied 3 years ago.

 

Tell me when it has run longer than normal...or if it doesnt turn off. I am looking to see if it runs without shutting down as it did before.

 

Once it either stops..OR..you know it has already ran longer than before let me know.

 

 

Customer: replied 3 years ago.
Flame went out at 12 minutes, fan is still running.
Customer: replied 3 years ago.
Flame went out at 12 minutes, fan went off two minutes later.
Expert:  Billy replied 3 years ago.

 

Thank you...and the wires are still twisted together?

 

And it ran longer than before?

 

 

Customer: replied 3 years ago.
About the same run time, if longer it was not much, and yes wires still twisted. FYI, the first couple of times the original problem happened, I could reset it and it might operate normally for hours before shutting off again. Now it's only minutes.
Expert:  Billy replied 3 years ago.

 

Ok...we are getting there..

 

When flame shuts off...does the exhaust fan shut off just before, same time or after?

 

 

Customer: replied 3 years ago.
Two minutes after on the test we ran, not sure any other time because I'm always away from the unit.
Expert:  Billy replied 3 years ago.

 

And finally.....the main blower that sends air through the ducts.....it shuts off when?

 

 

Customer: replied 3 years ago.
Sorry, but I'm not totally sure if what stayed on two minutes longer was exhaust fan or blower or both. I thought it was blower first, but since you said exhaust fan I went with that without explaining. I can test again if it's critical to distinguish between them.
Expert:  Billy replied 3 years ago.

 

sorry...but it is important.

 

format as such:

 

exhaust starts

pilot lights

burners fire up

flames turn off 10 minutes later

exhaust turns off 2 minutes later

main blower turns off 1 minute later

Customer: replied 3 years ago.
Forgot to turn unit off to reset from before, so will take some time to start test.
Customer: replied 3 years ago.
Second test ... Draft inducer came on with pilot, but flame never kicked in before shutting down. Resetting for another test.
Customer: replied 3 years ago.
Third test ... Power on, exhaust starts, pilot lights, flame and blower kick on, all happened within 1.5 minutes. Ran for 5 minutes, then flame went out but blower and exhaust both stayed on for another 2 or 3 minutes. Same as first test it seems, except didn't run as long.
Expert:  Billy replied 3 years ago.

 

Thank you.

 

This is sounding like the 3 wire pilot is going bad. The pilot has a warp switch in the side of it. It lights, then it heats up the side warp switch...after a while it warps and connects and sends power to the gas valve for main gas.

 

I am also suspecting a "domino" theory that the small circuit board behind the pressure switch is affected.

 

From your last response...you said flame goes out...but what about pilot?

 

 

 

 

Customer: replied 3 years ago.
Pilot and flame out at same time. I'm on my phone for all of this and battery is dying. If you could outline my next steps, you've earned your money. I'll accept your answer, do what you tell me, and then follow up with the results if the website will let me. Thanks!
Expert:  Billy replied 3 years ago.

The pilot will need to be replaced first.

 

This is what is holding the unit pilot mode. Change pilot and let me know.

 

 

Customer: replied 3 years ago.
Will do, thanks!
Expert:  Billy replied 3 years ago.

 

Keep me posted as you progress.

 

Billy

Customer: replied 3 years ago.
Where do I "Accept" your answer?
Expert:  Billy replied 3 years ago.

I have not attached it yet.

 

I want to make sure what I tell you is worth paying for.

 

Once we get to a point that I feel I have helped, then I will send link.

 

Thank you for asking.

 

Billy

Customer: replied 3 years ago.
Ok, it may be a few days before I have time time to get part and install it. I'll follow up then. Thanks aagin!
Expert:  Billy replied 3 years ago.
will keep question open as long as necessary.
Customer: replied 3 years ago.
Just replaced pilot, everything ran like normal so I lowered thermostat until it no longer called for heat, flame went out and blower and exhaust fan stayed on for about two more minutes. I raised thermostat to about ten degrees higher, but furnace never did anything. So, back to the drawing board. Supply house said I was starting at right place with pilot, so now where do I go?
Expert:  Billy replied 3 years ago.

 

Did you say the inducer motor runs after the flame and pilot go out...or at the same time

Customer: replied 3 years ago.
I think it stays on after flame and cuts off with blower, but I am not sure. Is there an easy check?
Expert:  Billy replied 3 years ago.

 

Now that I am confident the pilot warp switch is sending power, I now need to acess the inducer relay board (behind the pressure switch). The key now is if the pilot and flame go with the draft motor or if the draft motor continues to run after the pilot/flame goes out. Sorry but to find out means babysitting the unit and seeing what happens at shut down.

 

 

Customer: replied 3 years ago.
Ok, resetting now, so have to wait unless you know a quick/immediate reset. Btw, if I turn power on at unit before enough time has elapsed, I hear a click at the relay board you mention. If enough time has passed, unit starts normally.
Customer: replied 3 years ago.
Draft motor definitely stopped at same time as when flame and pilot went out. Blower continued for two more minutes.
Expert:  Billy replied 3 years ago.

 

Small circuit board behind pressure switch controls the inducer motor....is there a chance the motor faults and in a split second the flame goes with it?

 

Any faulting of the inducer will be because of that small board. Look at the back of board for hot spot.

 

 

Customer: replied 3 years ago.

Ok, thanks. I might not be able to check until tomorrow.

 

I looked at it last night, but of course I only looked at the front. If I don't see anything on the back, is there a next step?

 

Not sure about faulting, but motor seems to work ok while running (it puts out a strong exhaust) and I felt it after it shut off and it wasn't overly warm or anything.

Expert:  Billy replied 3 years ago.

 

This was one of the designs that were tried and stopped real soon after. The small circuit board had a very high failure rate. It can cut the inducer at will...and also not start up unit.

 

Quite often there is a brown spot on the back of the board. I want you to check first instead of building a new furnace part by part....

Customer: replied 3 years ago.
No brown spot, looks perfect, all solder joint intact best I can tell.
Expert:  Billy replied 3 years ago.

 

Thank you.

 

At this point we need to see if the main board is dropping signal to the inducer board or if inducer board is dropping signal back to main. Do you have a volt meter?

 

 

Customer: replied 3 years ago.
No but if it's the only way I can borrow one.
Expert:  Billy replied 3 years ago.

Ok,

 

To save time I am going to format a troubleshoot...terminal to terminal and send. Will pull the schematic and give you a course of action with what to do depending on results.

 

 

Customer: replied 3 years ago.
Awesome, thanks. I'll tackle it this evening or over the weekend. BTW, I realize this has gone on now for a week and I appreciate your patience ... also, we don't need heat at the moment, temps have been moderate so it's afforded me the time to tinker. Now, if work didn't get in the way, I'm sure things would have went faster.
Expert:  Billy replied 3 years ago.

 

Coming from the pressure switch are 3 wires...yellow, orange and brown.

 

Orange is our 24V to the pressure switch from the board. (small one behind pressure switch) We want to put one meter lead to orange and one to ground. We need 24v on the orange all the time after start up. To start 24v connects to yellow....once the pressure switch closes it connects orange to brown.

 

Once brown gets 24v from the orange at pressure switch it enables pilot.

 

It does this by connecting through the edge connectors. Pull edge connectors and use a flat piece of sand paper and clean contacts.

 

If you can clip meter lead to any ground on cabinet and then to the orange wire on pressure switch.

 

If it faults and there is no 24 v on orange = replace circuit board in blower section or check edge connector.

 

If 24 v remains on orange replace small circuit board behind pressure switch.

 

Customer: replied 3 years ago.
Tested four times, each time the volt meter read around 26.8 after the flame went out and blower and fan shut down. So, will replace small circuit board behind pressure switch according to steps above and let you know the outcome.
Expert:  Billy replied 3 years ago.

 

I will continue to leave open for you.

 

 

Customer: replied 3 years ago.
Success! Evidently, that inducer board was upgraded in 1989, so pretty long run for the substandard old one. Had to add a red wire from limit switch to board, but otherwise easy install. Thanks for all your help.
Expert:  Billy replied 3 years ago.

 

I am very glad it came to an end for you!

 

Bet you know more about your furnace than you ever thought you would...Smile

 

Thanks for all your patience with me. I do this between my regular job and home and realize I am not always quick with replies...you showed great character....thank you!

 

Billy

Billy, HVAC Technician
Category: HVAC
Satisfied Customers: 19948
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Billy and 2 other HVAC Specialists are ready to help you
Customer: replied 3 years ago.
You were great, thanks!

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial