I have Lennox Diplomat Furnace, Model 80MGF2-45A-1. The Furnace

Resolved Question:

I have Lennox Diplomat Furnace, Model 80MGF2-45A-1. The Furnace will run, just no heat. Light on board blinked 3 times rapid, then I replaced thermostat and light blinks normally, but still no heat from unit. No flame from burners. I followed instruction manual for relighting burners, no success,... need assistance.
Submitted: 3 years ago.
Category: HVAC
Expert:  ComfortZone replied 3 years ago.

ComfortZone :

Does this furnace have a standing pilot that you must manually light?

Customer : No
Customer : Auto-light not manual
ComfortZone :

Does the ignitor glow bright orange?

Customer : I'm confused. Do you not have the service manual for this unit. The ignitor isnot
Customer : The ignitor is not visible
Expert:  ComfortZone replied 3 years ago.
I do not so I will opt out.
Customer: replied 3 years ago.
OK, great. Since that is the case, I take it that this matter was forward to another service expert?
Customer: replied 3 years ago.
Relist: Answer quality.
...need another "expert" to reply to original questions....ASAP
Expert:  Billy replied 3 years ago.

 

 

Hello,

 

This is a pressure switch issue.

 

First here is what I assume is your model. Please verify

 

http://www.cozyparts.com/Lennox-Parts/forum/Lennox_service_manual/Furnaces/80MGF_08_01_2004.pdf

 

 

Customer: replied 3 years ago.
Thanks for the fast response. I looked at the repair manual that you attached and this appears to be the exact furnace that I have. I just have 3 burners though.
Expert:  Billy replied 3 years ago.

 

Thank you,

 

Are you familiar with the pressure switch that must prove air flow?

 

 

Customer: replied 3 years ago.
I am familiar with the location of the pressure swith location on the furnace. As a matter of fact, I check the hose leading from this switch to the fan,...no blockage detected.
Expert:  Billy replied 3 years ago.

 

Do you mind a hands on test?

 

 

Customer: replied 3 years ago.
Certainly. How shall I perform this test?
Expert:  Billy replied 3 years ago.

 

Turn furnace off

Locate and remove the 2 wires connected to pressure switch and hold apart.

Turn power back on with thermostat turned to heat and up.

AFTER the exhaust fan starts, touch the 2 wires together so they make metal to metal contact. Some find a paper clip with the ends stuck into the bottom of the wire connectors helpful. If you do this do not let metal touch the cabinet. It is only 24v but could blow a fuse.

 

I need to know if the unit progresses after the pressure switch wires are touched together.

 

 

 

Customer: replied 3 years ago.
I follow the steps and placed the 2 wires together for >60 secs, no response, burner did not ignite.
Expert:  Billy replied 3 years ago.

 

Thanks for your help....

 

Now there are a couple different circuit boards used in this unit. How many diagnostic lights are on your board?

 

 

Customer: replied 3 years ago.
1 diagnostic light, RED, labeled "LED1"
Expert:  Billy replied 3 years ago.

 

Ok,

 

and are you positive the code is 3? When the furnace was shut down and then restarted...did the diagnostic start solid or flashing....and then lock out with 3?

 

 

Customer: replied 3 years ago.

As I recall, the LED blinked 3 times rapidly, then I replaced the thermostat and now the LED blinks normally but slow. The light on the other furnace blinks normally, but fast. It runs normally, also.

Customer: replied 3 years ago.
When the furnace was shut down and restarted, the diagnotics LED started in flashing mode; no solid LED noted. I can recheck.
Customer: replied 3 years ago.
Just verified. Turned the furnace off for 60 sec, then back on. There is a steady, slow LED with no interruptions. The two wire for the pressure switch remain disconnected, ....did not reconnect.
Expert:  Billy replied 3 years ago.

 

Thanks...was the upper exhaust fan running during this time?

 

 

Customer: replied 3 years ago.
The upper exhaust fan (blower) was not running. The blower deeper inside the cabinet seems to work. The upper blower does not respond at all.
Expert:  Billy replied 3 years ago.

 

Take doors off furnace. Tape safety door switch down at top of bottom door. Locate where the thermostat wires attach to the circuit board. You should see R, Y, W, G, C.

 

Tell me if you have identified them and we will do another quick test. We are close to an answer now...

 

 

Customer: replied 3 years ago.

I noticed that this unit does not have a safety door switch. I looked for this on today and never located this door switch. Does every unit absolutely have a safety door switch? I may have overlooked it.

 

I see the R, Y, W, G, C on the circuit.

 

Before testing, should I reconnect the wires leading to the pressure switch?

Customer: replied 3 years ago.
There is a single door for the top and bottom, not two doors
Expert:  Billy replied 3 years ago.

 

 

page 7 figure 1 shows where a normally placed door switch would be.

http://www.cozyparts.com/Lennox-Parts/forum/Lennox_service_manual/Furnaces/80MGF_08_01_2004.pdf

 

Now..yes put wires back on pressure switch.

 

Turn power on....so at this point we have the circuit board exposed...power is on.

 

Now use a short wire, jumper etc...and jump R to W. One end of wire on R while other touching W...and hold in place....tell me if exhaust fan starts...and if it does if the unit tries to run..

 

 

 

Customer: replied 3 years ago.

Definitely no door switch present.

 

I jumped R and W with paperclip. The blower that lies encased behind the circuit board powers on, and the LED light flashes a steady, fast, "normal", RED. The blower at the top, above the pressure switch, does not come on at all. It has not ran during any of these procedures.

 

Note: In the past, it seemed that the when I turned on furnace from the thermostat, the blower behind the circuit board would come on but the LED would blink slow and steady, not fast. I may be incorrect.

Expert:  Billy replied 3 years ago.

 

Ok here is the issue at hand.

 

The reason you got the initial code 3 is because the exhaust fan did not start. Since it did not start the air switch could not be closed.

 

Now we are down to 2 choices....

 

1) the exhaust motor gets power but doesnt run

2) the exhaust fan does not get power which means circuit board is bad.

 

Now the exhaust motor could have power but not run due to obstruction in exhaust housing.

 

Try the R to W again...and this time spin the black fan wheel on the rear of the exhaust motor. This is a cooling fan for the exhaust motor. See if when you spin it if it tries to start ...is seized...if it hums... any sign of life. After this we would need a volt meter to see which is not working.

 

 

Customer: replied 3 years ago.

Just so that I am on the same page, you are referring to the exhaust motor that is displayed on page 19, figure 21, correct?

Expert:  Billy replied 3 years ago.

Good question...it could also be page 7 figure 2....It appears the unit could have either.

 

 

Expert:  Billy replied 3 years ago.

 

I am very sorry but I have to go offline. I will respond first thing tomorrow morning.

 

I hate to go offline this close to an answer for you, but I am out of time.

 

Billy

Expert:  Billy replied 3 years ago.

 

Any update?

 

 

Customer: replied 3 years ago.

No heat. I think that the next step was to test something with a Multi-Meter, which I have. I am not at home presently. How long are you available today? I plan to return home in the next 3 hrs.

Expert:  Billy replied 3 years ago.

Send a response to this thread...I will be notified on my phone and I will respond as soon as I can.

 

 

Customer: replied 3 years ago.
I am online and at home. I just await your reply to this message.
Expert:  Billy replied 3 years ago.

 

Very sorry, had an emergency service call.

 

Which motor did you have ...the one with the cooling fan on back of motor or not?

 

 

Customer: replied 3 years ago.

I have one with the fan on the back of the motor. The fan moved freely when I jumped R and W.

Expert:  Billy replied 3 years ago.

 

So with R and W jumped...the fan did not run.....but spin by hand freely?

 

 

Customer: replied 3 years ago.

Yes, that is correct. No resistance from fan with R and W jumped.

Expert:  Billy replied 3 years ago.

 

There is a plug to the motor..it starts as wires from the circuit board and then there is a plastic connector....do you know what I refer to?

 

 

Customer: replied 3 years ago.

Yes, I am familiar with this connector. There is numbering on the connector for each connection.

Expert:  Billy replied 3 years ago.

 

Ok....we are at the point we need something to see if power is at that plug. A meter, a light tester, anything that can tell me if power is present...

 

 

Customer: replied 3 years ago.
OK. I have a Multi-Meter. I need to review the how exactly it works. The is a red and black wire, and a dial in front.
Expert:  Billy replied 3 years ago.

set dial to ac volts ~

and set for range less than 600.

 

Test meter by sticking leads into a outlet you know works...look for 115 - 125 volts.

 

This will tell us if meter is set and working

Customer: replied 3 years ago.
OK. I tested the meter and it works.
Expert:  Billy replied 3 years ago.

 

Great....now unplug the motor and start the furnace....see if the plug that comes from the circuit board energizes with power or not.

 

 

Customer: replied 3 years ago.
OK. Leading from the circuit board is the female connector. There is a large black cable and a white one which interconnect with the opposing black cables on the male end. I plugged the meter "rods" into the holes on the female end of the connector and the meter indicates that there is power.
Expert:  Billy replied 3 years ago.

 

Thank you....was it over 115 volts?

 

 

Customer: replied 3 years ago.
I have the ACV dial set at 300 (max). The dial goes mid-way when I insert the rods into the female connectors.
Expert:  Billy replied 3 years ago.

 

Ok, that is sufficient.

 

You have a bad exhaust fan motor. It may spin by hand but apparently has bad windings.

 

Looks like you will need to replace the inducer/exhaust motor.

 

 

Customer: replied 3 years ago.

OK. So I will need to simply replace the entire part seen on page 7, Figure 2 (Combustion Air Blower), correct? or will I need to open the item and remove the motor and replace that?

Expert:  Billy replied 3 years ago.

 

Nope the whole assembly. Which is really not a bad job. I believe you unhook the wiring and vent pipe...then 3 - 4 screws. Pretty quick job.

 

Thanks for all your help.

 

Billy

Billy, HVAC Technician
Category: HVAC
Satisfied Customers: 19769
Experience: Endorsed for unlimited heating, cooling, oil burners, boilers, refrigeration, hydronics
Billy and 3 other HVAC Specialists are ready to help you
Customer: replied 3 years ago.
Thanks for all of your assistance.

JustAnswer in the News:

 
 
 
Ask-a-doc Web sites: If you've got a quick question, you can try to get an answer from sites that say they have various specialists on hand to give quick answers... Justanswer.com.
JustAnswer.com...has seen a spike since October in legal questions from readers about layoffs, unemployment and severance.
Web sites like justanswer.com/legal
...leave nothing to chance.
Traffic on JustAnswer rose 14 percent...and had nearly 400,000 page views in 30 days...inquiries related to stress, high blood pressure, drinking and heart pain jumped 33 percent.
Tory Johnson, GMA Workplace Contributor, discusses work-from-home jobs, such as JustAnswer in which verified Experts answer people’s questions.
I will tell you that...the things you have to go through to be an Expert are quite rigorous.
 
 
 

What Customers are Saying:

 
 
 
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
< Last | Next >
  • You did one super job of explaining to me everything there is to know about this fridge. I'm looking forward to asking you questions in the future. Jimmy Bagley, IA
  • Wonderful service, prompt, efficient, and accurate. Couldn't have asked for more. I cannot thank you enough for your help. Mary C. Freshfield, Liverpool, UK
  • This expert is wonderful. They truly know what they are talking about, and they actually care about you. They really helped put my nerves at ease. Thank you so much!!!! Alex Los Angeles, CA
  • Thank you for all your help. It is nice to know that this service is here for people like myself, who need answers fast and are not sure who to consult. GP Hesperia, CA
  • I couldn't be more satisfied! This is the site I will always come to when I need a second opinion. Justin Kernersville, NC
  • Just let me say that this encounter has been entirely professional and most helpful. I liked that I could ask additional questions and get answered in a very short turn around. Esther Woodstock, NY
  • Thank you so much for taking your time and knowledge to support my concerns. Not only did you answer my questions, you even took it a step further with replying with more pertinent information I needed to know. Robin Elkton, Maryland
 
 
 

Meet The Experts:

 
 
 
  • gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
< Last | Next >
  • http://ww2.justanswer.com/uploads/SE/ServiceTechRus/2012-6-7_2119_056.64x64.JPG gotoman for ac's Avatar

    gotoman for ac

    HVAC Technician

    Satisfied Customers:

    4657
    51 years of experience install design and repair of all makes and models of AC
  • http://ww2.justanswer.com/uploads/AL/alumalite/2012-5-10_234018_shutterstock506249951forJA500.64x64.jpg Phil's Avatar

    Phil

    Mechanical Engineer

    Satisfied Customers:

    3888
    Retired HVAC/ Electrical & Boiler contractor. Industrial
  • http://ww2.justanswer.com/uploads/skibum0101/2008-12-16_015819_just_answer.jpg Rick Mather's Avatar

    Rick Mather

    HVAC Technician

    Satisfied Customers:

    3132
    35 years experience, HVAC
  • http://ww2.justanswer.com/uploads/RY/Rygis20/2011-5-7_3143_DSC5324.64x64.JPG Matthew's Avatar

    Matthew

    HVAC Technician

    Satisfied Customers:

    1994
    14 years experience in the HVAC field of service, installation, Manual J & D calculations
  • http://ww2.justanswer.com/uploads/KE/kentguidry/2011-9-26_214316_0059.64x64.jpg Kenton Guidry's Avatar

    Kenton Guidry

    HVAC Technician

    Satisfied Customers:

    962
    12 years install/service experience.
  • http://ww2.justanswer.com/uploads/solarman1947/2009-12-13_223915_phpkKBcXq_c2PM.jpg Rick Ridley's Avatar

    Rick Ridley

    UK Heating Engineer

    Satisfied Customers:

    871
    Retired But have had 30 years on the tools, Ex CORGI
  • http://ww2.justanswer.com/uploads/Ironheadfan/2009-12-18_222416_pump_005.jpg Tom's Avatar

    Tom

    HVAC Technician

    Satisfied Customers:

    770
    16+yrs HVAC/R service. Residential Commerical Industrial